[TRNSYS-users] Error in simulation
    David BRADLEY via TRNSYS-users 
    trnsys-users at lists.onebuilding.org
       
    Wed Jul 12 07:30:56 PDT 2017
    
    
  
Ismail,
  You'd have to look at the list file to know for certain what the 
problem is but my guess is that the system isn't converging a lot of the 
time. I imagine that the zone RH goes above 70% so the fan turns on, at 
which point the zone RH drops below 70% so the fan turns back on, which 
makes the zone RH go back above 70%. You need to make sure that you're 
using a controller that has hysteresis (a deadband) and that you are 
using a short timestep (one minute perhaps).
kind regards,
  David
On 07/12/2017 04:27, Ismail OUHALLOU via TRNSYS-users wrote:
> Dear Tnsys users,
>
> I want to simulate an AHU building integrated using type 112b. Control 
> signal of type 112b is: The fan (type 112b) is to be ON if the 
> relative humidity of a zone is greater than 70%.
> When I run simulation, it gets blocked at a given time as shawn in 
> figure below:
>
> 
> Where does the problem come from ?
>
> Thanks in advance
> Ismail
>
>
> -- 
> /************************************************/
> /Ismail OUHALLOU/
> Green building & Sustainability consultant
>
> *Morocco*
> P:+212**620**548**116
> F:+212**522**326**440
> i.ouhallou at trusted-energy.com <mailto:i.ouhallou at trusted-energy.com>
> issmail.ouhallou at gmail.com <mailto:issmail.ouhallou at gmail.com>
>
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170712/2570da7b/attachment-0003.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Capture.PNG
Type: image/png
Size: 93598 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170712/2570da7b/attachment-0003.png>
    
    
More information about the TRNSYS-users
mailing list