[TRNSYS-users] Problem with heat pump Type 505 cooling and heating performance data

David BRADLEY via TRNSYS-users trnsys-users at lists.onebuilding.org
Mon Jul 3 13:31:54 PDT 2017


Usually the catalogs report total flow and do not separate out by return 
or outside air because the return and outside air streams mix before 
going through the heat pump.

It doesn't matter if your catalog has more or fewer values than the 
example data file. The model's parameters allow you to adjust the number 
of values of each variable that you are supplying in your data file.

kind regards,

  David



On 07/01/2017 06:59, S.O.Daei.N via TRNSYS-users wrote:
> Hi All,
> As mentioned in catalog in attachment, I have specification data of my 
> heat pump.
> I have total flow rate of 944 l/s (but i don't have return and outside 
> air flow rates separately how can i find them?), and liquid flow rate 
> 0.354 l/s and DHW flow rate 0.14 l/s (one fewer than mentioned in 
> sample catalog data) , but in catalog i have 12 values for 4 
> temperature in cooling mode and 12 values for 4 temperature in heating 
> mode.
> In sample catalog data i need 24 values,how can i reach that other 12 
> values in both heating and cooling mode in that catalog data?
> Please help me with this problem
> Thanks
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170703/f046a621/attachment.htm>


More information about the TRNSYS-users mailing list