Ravindra,
Models for the expansion valve and heat exchangers for vapor
compression cycles don't exist in TRNSYS as far as I am aware. In order
to write such a model you would need to know what refrigerant is being
used in the cycle and you'd need a routine to give you refrigerant
properties.
I am not sure if TRNSYS is the right tool to use to model a vapor
compression cycle. Typically we work with systems in TRNSYS that have
transient behavior on the order of a minute or longer. The transients in
the individual components of a vapor compression cycle are much shorter
than that. At one minute intervals such a refrigeration cycle looks
quite steady state and so we typically use performance maps to model
them. When I need to look inside the cycle, I typically use a program
called EES (Engineering Equation Solver).
kind regards,
David
On 06/30/2017 01:51, v ravindra via TRNSYS-users wrote:
> Which component (Type) can i use to represent a Suction line heat
> exchanger having sub cooling and super heating while setting up a
> Vapour compression cycle in TRNSYS 17.
>
> V.Ravindra
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170703/f558c0df/attachment.htm>
More information about the TRNSYS-users
mailing list