    <p>Ravindra,</p>
    <p>  Models for the expansion valve and heat exchangers for vapor
      compression cycles don't exist in TRNSYS as far as I am aware. In
      order to write such a model you would need to know what
      refrigerant is being used in the cycle and you'd need a routine to
      give you refrigerant properties.</p>
    <p>  I am not sure if TRNSYS is the right tool to use to model a
      vapor compression cycle. Typically we work with systems in TRNSYS
      that have transient behavior on the order of a minute or longer.
      The transients in the individual components of a vapor compression
      cycle are much shorter than that. At one minute intervals such a
      refrigeration cycle looks quite steady state and so we typically
      use performance maps to model them. When I need to look inside the
      cycle, I typically use a program called EES (Engineering Equation
      Solver).</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 06/30/2017 01:51, v ravindra via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CADb1Z3Lvve+hoPCrhAC92i-XJYX-yQY_o=VP0aHw3zWdBr7SUg@mail.gmail.com">
      <div dir="ltr"><span style="font-size:12.8px">Which component
          (Type) can i use to represent a Suction line heat exchanger
          having sub cooling and super heating while setting up a Vapour
          compression cycle in TRNSYS 17.</span>
        <div><span style="font-size:12.8px"><br clear="all">
          </span>
          <div>
            <div class="gmail_signature">
              <div dir="ltr">
                <div dir="ltr">V.Ravindra<br>
                  <br>
                </div>
              </div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>