[TRNSYS-users] Not able to put custom input in Type 56 (Multi zone Building)
David BRADLEY via TRNSYS-users
trnsys-users at lists.onebuilding.org
Fri Jan 6 07:05:24 PST 2017
Niket,
Your attachment does not seem to have come through with your email.
If you want to see the building's response ONLY to the ambient
temperature then you'll need to open the building file (*.b17) in
TRNBuild and change the radiation calculation method from "internal" to
"external by another component." To do so, navigate in TRNBuild to the
"project" window and you'll see a list of "orientations." Click on each
orientation and change from internal to external. Once you have saved
the *.b17 file, return to the Studio, right click on the Type56 and
select "update building variable list" from the context menu. Now when
you open the building inputs, you'll see that there are three new inputs
for each orientation (total solar, beam solar, and angle of incidence).
Remember that any input whose value is not connected will remain
constant at the given initial value. Set the initial value of all solar
radiation inputs (as well as that of solar zenith and azimuth angles) to
zero but leave the dry bulb temperature connection from Type15 to Type56
and your building will be subject only to an ambient temperature.
kind regards,
David
On 01/06/2017 05:18, Niket Kumar via TRNSYS-users wrote:
> Dear All,
>
> The type 56 when linked with weather data (to be specific
> meteonorm type 15-6 weather files) links to a number of parameters
> after importing *.idf file (like solar zenith angle, total tilted
> surface radiation for surface-1, beam radiation for surface-1 etc.),
> as shown in the attached figure.
>
> But I want to link the type 56 to dry bulb temperature (as an input to
> type 56), and see the simulations with respect to variation in
> temperature only.
>
> Please let me know how can I do this since in the attached figure
> condition simulation is showing error.
>
> thanking you,
>
> Niket Kumar
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170106/574deb33/attachment-0003.htm>
More information about the TRNSYS-users
mailing list