<p>Niket,</p>
<p> Your attachment does not seem to have come through with your
email. If you want to see the building's response ONLY to the
ambient temperature then you'll need to open the building file
(*.b17) in TRNBuild and change the radiation calculation method
from "internal" to "external by another component." To do so,
navigate in TRNBuild to the "project" window and you'll see a list
of "orientations." Click on each orientation and change from
internal to external. Once you have saved the *.b17 file, return
to the Studio, right click on the Type56 and select "update
building variable list" from the context menu. Now when you open
the building inputs, you'll see that there are three new inputs
for each orientation (total solar, beam solar, and angle of
incidence). Remember that any input whose value is not connected
will remain constant at the given initial value. Set the initial
value of all solar radiation inputs (as well as that of solar
zenith and azimuth angles) to zero but leave the dry bulb
temperature connection from Type15 to Type56 and your building
will be subject only to an ambient temperature.</p>
<p>kind regards,</p>
<p> David</p>
<p><br>
</p>
<br>
<div class="moz-cite-prefix">On 01/06/2017 05:18, Niket Kumar via
TRNSYS-users wrote:<br>
</div>
<blockquote
cite="mid:CAOPoHZJKmPZ5c29tKaassMgh47AFtmtq0SU-LpaQpAiCpgXJDQ@mail.gmail.com"
type="cite">
<div dir="ltr">Dear All,
<div><br>
</div>
<div>The type 56 when linked with weather data (to be specific
meteonorm type 15-6 weather files) links to a number of
parameters after importing *.idf file (like solar zenith
angle, total tilted surface radiation for surface-1, beam
radiation for surface-1 etc.), as shown in the attached
figure. </div>
<div><br>
</div>
<div>But I want to link the type 56 to dry bulb temperature (as
an input to type 56), and see the simulations with respect to
variation in temperature only.</div>
<div><br>
</div>
<div>Please let me know how can I do this since in the attached
figure condition simulation is showing error.</div>
<div><br>
</div>
<div>thanking you,</div>
<div><br>
</div>
<div>Niket Kumar</div>
<div> </div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>