[TRNSYS-users] Type1 Number of identical collectors in series has no effect
Antoine Gautier via TRNSYS-users
trnsys-users at lists.onebuilding.org
Thu Oct 20 13:09:19 PDT 2016
Thanks a lot David!
Sorry I had you taking me by the hand like that.
I must say that my insistence pertains to the following observation: only
changing "number in series" from 6 to 1 leads to the exact same results.
I find it really strange
The new system modelled should be an array of Ntotal collectors connected in
parallel and thus receiving M/Ntotal flowrate (Nseries=1).
Does this mean that the drop in efficiency due to lower flowrate is exactly
balanced by the raise in efficiency due to lower average temperature (each
collector now being supplied directly with water at array inlet
temperature)?
--
Antoine Gautier
Solamen
+33 6 58 24 02 60
antoine.gautier at solamen.fr
De : David BRADLEY [mailto:d.bradley at tess-inc.com]
Envoyé : jeudi 20 octobre 2016 21:43
À : Antoine Gautier <antoine.gautier at solamen.fr>; 'TRNSYS users mailing list
at OneBuilding.org' <trnsys-users at lists.onebuilding.org>
Objet : Re: [TRNSYS-users] Type1 Number of identical collectors in series
has no effect
Antoine,
That is correct so long as "A" is the area of the full array (12 times the
area of a single module) and so long as "M" is twice the flow rate that you
want to go through each collector. Mathematically:
M = X * Ntotal / Nseries
where M is the pump flow rate, X is the flow rate per collector, Ntotal is
the total number of collectors (12), and Nseries is the number of collectors
in series per parallel path (6).
best,
David
On 10/20/2016 14:20, Antoine Gautier wrote:
Sorry David I still have some doubts
Here is a schematic.
Within each row, the collectors are connected in series.
The pump flowrate is M. The total array area is A.
I can model this with Type1 considering:
Number in series=6
Collector area=A
Inlet flowrate=M
Is this correct?
Thanks again.
--
Antoine Gautier
Solamen
+33 6 58 24 02 60
antoine.gautier at solamen.fr <mailto:antoine.gautier at solamen.fr>
De : David BRADLEY [mailto:d.bradley at tess-inc.com]
Envoyé : jeudi 20 octobre 2016 20:44
À : Antoine Gautier <mailto:antoine.gautier at solamen.fr>
<antoine.gautier at solamen.fr>; 'TRNSYS users mailing list at OneBuilding.org'
<mailto:trnsys-users at lists.onebuilding.org>
<trnsys-users at lists.onebuilding.org>
Objet : Re: [TRNSYS-users] Type1 Number of identical collectors in series
has no effect
Antoine,
I'm not 100% sure that I follow your logic but you can model that array
with a single instance of Type1. If your single module has an area of 1m2
and wants a flow rate of 400kg/h then the full array of 50 modules (10 in
parallel, 5 in series) would have:
area = 50 m2
number in series = 5
flow rate = 4000kg/h (400kg/h x 10 in parallel)
best,
David
On 10/20/2016 13:30, Antoine Gautier wrote:
Thanks David
Just to be sure
Considering an array of 50 collectors = 10 parallel-connected rows of 5
series-connected collectors, total inlet flowrate of array = M, total area =
A.
I cannot model the whole array with Type1 only: I need to add an equation
multiplying the flowrate and energy rate computed by Type1 by the number of
rows. Type1 parameters and inputs being the following:
Number in series=5
Collector area=A/10
Inlet flowrate=M/10
Right?
--
Antoine Gautier
Solamen
+33 6 58 24 02 60
antoine.gautier at solamen.fr <mailto:antoine.gautier at solamen.fr>
De : David BRADLEY [mailto:d.bradley at tess-inc.com]
Envoyé : jeudi 20 octobre 2016 19:24
À : Antoine Gautier <mailto:antoine.gautier at solamen.fr>
<antoine.gautier at solamen.fr>; TRNSYS users mailing list at OneBuilding.org
<mailto:trnsys-users at lists.onebuilding.org>
<trnsys-users at lists.onebuilding.org>
Objet : Re: [TRNSYS-users] Type1 Number of identical collectors in series
has no effect
Antoine,
This is a common source of confusion. Two points are important to keep in
mind. First, the collector array area parameter is the area of the entire
array, not just the area of one module in the array. Second, if you add a
second collector you have to be careful about what you do with the flow
rate. If you are adding a second collector in parallel to the first one you
should double the collector array area, leave the "number in series"
parameter set to 1, and double the liquid flow rate to the array. If you are
adding a second collector in series with the first one, you should double
the collector array area, set the number in series to 2, and leave the
liquid flow rate unchanged.
kind regards,
David
On 10/20/2016 11:46, Antoine Gautier via TRNSYS-users wrote:
Hi
I cannot figure out why the number of collectors in series has no effect on
the collectors array efficiency: see attached project.
Computing equations from source code manually I would state the opposite
Thanks for your help.
Best regards
--
Antoine Gautier
Solamen
+33 6 58 24 02 60
antoine.gautier at solamen.fr <mailto:antoine.gautier at solamen.fr>
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org
<mailto:TRNSYS-users at lists.onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com <mailto:d.bradley at tess-inc.com>
http://www.tess-inc.com
http://www.trnsys.com
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com <mailto:d.bradley at tess-inc.com>
http://www.tess-inc.com
http://www.trnsys.com
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com <mailto:d.bradley at tess-inc.com>
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20161020/74f88041/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 48878 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20161020/74f88041/attachment-0001.png>
More information about the TRNSYS-users
mailing list