Antoine,

  That is correct so long as "A" is the area of the full array (12 times 
the area of a single module) and so long as "M" is twice the flow rate 
that you want to go through each collector. Mathematically:

M = X * Ntotal / Nseries

where M is the pump flow rate, X is the flow rate per collector, Ntotal 
is the total number of collectors (12), and Nseries is the number of 
collectors in series per parallel path (6).

best,

  David



On 10/20/2016 14:20, Antoine Gautier wrote:
>
> Sorry David I still have some doubts…
>
> Here is a schematic.
>
> Within each row, the collectors are connected in series.
>
> The pump flowrate is M. The total array area is A.
>
> I can model this with Type1 considering:
>
> Number in series=6
>
> Collector area=A
>
> Inlet flowrate=M
>
> Is this correct?
>
> Thanks again.
>
> --
>
> Antoine Gautier
>
> Solamen
>
> +33 6 58 24 02 60
>
> antoine.gautier at solamen.fr
>
> *De :*David BRADLEY [mailto:d.bradley at tess-inc.com]
> *Envoyé :* jeudi 20 octobre 2016 20:44
> *À :* Antoine Gautier <antoine.gautier at solamen.fr>; 'TRNSYS users 
> mailing list at OneBuilding.org' <trnsys-users at lists.onebuilding.org>
> *Objet :* Re: [TRNSYS-users] Type1 Number of identical collectors in 
> series has no effect
>
> Antoine,
>
>   I'm not 100% sure that I follow your logic but you can model that 
> array with a single instance of Type1. If your single module has an 
> area of 1m2 and wants a flow rate of 400kg/h then the full array of 50 
> modules (10 in parallel, 5 in series) would have:
>
> area = 50 m2
>
> number in series = 5
>
> flow rate = 4000kg/h (400kg/h x 10 in parallel)
>
> best,
>
>  David
>
> On 10/20/2016 13:30, Antoine Gautier wrote:
>
>     Thanks David
>
>     Just to be sure…
>
>     Considering an array of 50 collectors = 10 parallel-connected rows
>     of 5 series-connected collectors, total inlet flowrate of array =
>     M, total area = A.
>
>     I cannot model the whole array with Type1 only: I need to add an
>     equation multiplying the flowrate and energy rate computed by
>     Type1 by the number of rows. Type1 parameters and inputs being the
>     following:
>
>     Number in series=5
>
>     Collector area=A/10
>
>     Inlet flowrate=M/10
>
>     Right?
>
>     --
>
>     Antoine Gautier
>
>     Solamen
>
>     +33 6 58 24 02 60
>
>     antoine.gautier at solamen.fr <mailto:antoine.gautier at solamen.fr>
>
>     *De :*David BRADLEY [mailto:d.bradley at tess-inc.com]
>     *Envoyé :* jeudi 20 octobre 2016 19:24
>     *À :* Antoine Gautier <antoine.gautier at solamen.fr>
>     <mailto:antoine.gautier at solamen.fr>; TRNSYS users mailing list at
>     OneBuilding.org <trnsys-users at lists.onebuilding.org>
>     <mailto:trnsys-users at lists.onebuilding.org>
>     *Objet :* Re: [TRNSYS-users] Type1 Number of identical collectors
>     in series has no effect
>
>     Antoine,
>
>       This is a common source of confusion. Two points are important
>     to keep in mind. First, the collector array area parameter is the
>     area of the entire array, not just the area of one module in the
>     array. Second, if you add a second collector you have to be
>     careful about what you do with the flow rate. If you are adding a
>     second collector in parallel to the first one you should double
>     the collector array area, leave the "number in series" parameter
>     set to 1, and double the liquid flow rate to the array. If you are
>     adding a second collector in series with the first one, you should
>     double the collector array area, set the number in series to 2,
>     and leave the liquid flow rate unchanged.
>
>     kind regards,
>
>      David
>
>     On 10/20/2016 11:46, Antoine Gautier via TRNSYS-users wrote:
>
>         Hi
>
>         I cannot figure out why the number of collectors in series has
>         no effect on the collectors array efficiency: see attached
>         project.
>
>         Computing equations from source code manually I would state
>         the opposite…
>
>         Thanks for your help.
>
>         Best regards
>
>         --
>
>         Antoine Gautier
>
>         Solamen
>
>         +33 6 58 24 02 60
>
>         antoine.gautier at solamen.fr <mailto:antoine.gautier at solamen.fr>
>
>
>
>
>
>         _______________________________________________
>
>         TRNSYS-users mailing list
>
>         TRNSYS-users at lists.onebuilding.org
>         <mailto:TRNSYS-users at lists.onebuilding.org>
>
>         http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>
>
>
>
>     -- 
>
>     ***************************
>
>     David BRADLEY
>
>     Principal
>
>     Thermal Energy Systems Specialists, LLC
>
>     22 North Carroll Street - suite 370
>
>     Madison, WI  53703 USA
>
>       
>
>     P:+1.608.274.2577
>
>     F:+1.608.278.1475
>
>     d.bradley at tess-inc.com <mailto:d.bradley at tess-inc.com>
>
>       
>
>     http://www.tess-inc.com
>
>     http://www.trnsys.com
>
>
>
> -- 
> ***************************
> David BRADLEY
> Principal
> Thermal Energy Systems Specialists, LLC
> 22 North Carroll Street - suite 370
> Madison, WI  53703 USA
> P:+1.608.274.2577
> F:+1.608.278.1475
> d.bradley at tess-inc.com <mailto:d.bradley at tess-inc.com>
> http://www.tess-inc.com
> http://www.trnsys.com

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20161020/d293ffb9/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 48878 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20161020/d293ffb9/attachment-0001.png>


More information about the TRNSYS-users mailing list