[TRNSYS-users] Problem using Typa 107 and Type 9e - Solar cooling project
David BRADLEY via TRNSYS-users
trnsys-users at lists.onebuilding.org
Tue Nov 1 07:27:49 PDT 2016
Nuha,
I am not sure what data you are passing from Type9 to Type107 but
Type107 does not take chiller load as an input. It takes the temperature
and flow rate of three streams of water (the hot water (source energy)
stream, the chilled water stream, and the cooling water stream). Unless
you have made some computations outside of TRNSYS in order to convert
the loads that you are reading with Type9 into a temperature and flow
rate of chilled water returning from the load to the absorption chiller
then the connection you have made needs to be revised.
kind regards,
David
On 11/01/2016 04:20, Nuha Juneidi via TRNSYS-users wrote:
> Dear users,
>
> I am working on a project for my masters thesis, it's an solar
> cooling. I almost get closer to acomplish it, but I found some
> difficulties in using *Type 107* (Absorption Chiller) and *Type 9e*
> (Data Readers). Does anyone worked on a similar project? Any ideas
> about using the Types 107 and 9e? Can anyone help?
>
> Please find out in attached file a screenshot of my connections I have
> made.
>
> Kind regards,
> Nuha
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20161101/1091040f/attachment.htm>
More information about the TRNSYS-users
mailing list