[TRNSYS-users] Outside temperature of an external wall at time XXX not converged!
hotline via TRNSYS-users
trnsys-users at lists.onebuilding.org
Tue Jul 5 07:42:35 PDT 2016
Dear Rabah,
am I understanding you correct:
- Quser, QSKY_S1-ABS and TSO_S1 are outputs of Type 56
- You take these outputs and use them for your surface gains
This will definitely cause convergence problems since you manipulate a balance by using outputs of this balance.
You will have to find a different solution for your task.
Best
Jakob Merk
_________________________________________________________________________________________________
Jakob Merk
TRNSYS Software Team
Transsolar Energietechnik GmbH
Curiestraße 2
70563 Stuttgart
Fax: +49 711 67976-11
Email: hotline at transsolar.com<mailto:hotline at transsolar.com>
Web: www.trnsys.de<http://www.trnsys.de/>
Von: TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org] Im Auftrag von Rabah DJEDJIG via TRNSYS-users
Gesendet: 05 July 2016 15:46
An: TRNSYS-users at lists.onebuilding.org
Betreff: [TRNSYS-users] Outside temperature of an external wall at time XXX not converged!
Dear all,
Please, can any one help me to fix this problem:
For some reason, I try to do the following operation on the outside surface (S1) of an external wall (with type 56 and an equation):
surf. gain outside_S1 = Quser+QSKY_S1-ABS*IT_S1-HCONVO_S1*AREA_S1*(TAMB-TSO_S1)
i.e. eliminate on this surface all gains calculated automatically by Type 56 and add instead a user defined gain Quser.
This seems to work perfectly at the beginning of the simulation before arising this error:
Message: outside temperature of 1 (external) wall in zone 1 at time 2419.00 not converged!
I tried to modify Convergence tolerance, to change the components torder, etc ... fruitlessly
Best regards,
Rabah
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20160705/f2ee6451/attachment.htm>
More information about the TRNSYS-users
mailing list