Hi again!
Jeff, after your response, I've tried several things. The interesting
results I've got is that in the same configuration I have, supressing Type
93 (I put that to soften the control function before noticing this problem)
and connecting the "Fraction of Maximum Flow" directly to the pump's
"Control function" input, I get good results. As soon as I put the proper
capacitance of the collector's array, the negative peaks start to pop up
again.
Trying with the "Control Colector technique" it's the same. I've set the
control collector without mass and connecting the control output to Type
695 pump. Then, if I set the real collector without mass, i get good
results, if I put mass on the real collector, I get the negative peaks.
Is it really a control/numerical problem, or is it that because the
capacitance of the collectors, everytime the pump starts, the collectors
must heat first with the energy from the solar tank?
Again, I attach some pictures and plots.
Thanks in advance,
Javier Vega Benavente
Mechanical Engineering Student, Universidad de Concepción, Chile
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20161214/27adb83a/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Massless Collector Direct Control to pump.png
Type: image/png
Size: 118600 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20161214/27adb83a/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Negative peaks with massless control collector.png
Type: image/png
Size: 92492 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20161214/27adb83a/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Project with Massless Control Collectors.png
Type: image/png
Size: 182733 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20161214/27adb83a/attachment-0005.png>
More information about the TRNSYS-users
mailing list