[TRNSYS-users] Type 2d
David BRADLEY
d.bradley at tess-inc.com
Wed Apr 27 09:51:39 PDT 2016
Massimo,
Make sure that you are using a small enough timestep (1-5 minutes is
usually best). Type2 can only make one control decision per time step
and if your timestep is too long then controllers either cannot converge
on a decision or they don't do a good job of maintaining the setpoint.
You might also look at Type108. It sounds as though you have set up
Type2 properly but Type108 offers a somewhat more intuitive thermostat
model. You can disable stages 2 and 3 by setting very high (or low, as
appropriate) setpoints for those stages.
kind regards,
David
On 04/27/2016 11:39, massimo truant wrote:
>
> Good afternoon,
>
> I have a problem with type 2d. I use it like a thermostat but it
> doesnt work always. In my project type 2d activates a ventilation
> system when the difference between imput 1 and imput 2 is less than
> 2°C and it has to stop the system when that difference is less than -2.
>
> Example
>
> 25° is the temperature that I want
>
> The system should be activated when temperature reaches 27°C and
> should stop its action when the temperature reaches 23°C.
>
> But it doesn’t work sometimes the system is activated when the
> temperature is near 26°C and it is stopped when the temperature is
> near 24.
>
> Someone knows the reason of that?
>
> Thanks to all
>
> Inviato da Posta <https://go.microsoft.com/fwlink/?LinkId=550986> per
> Windows 10
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20160427/b6e8710e/attachment-0001.htm>
More information about the TRNSYS-users
mailing list