    Massimo,<br>
      Make sure that you are using a small enough timestep (1-5 minutes
    is usually best). Type2 can only make one control decision per time
    step and if your timestep is too long then controllers either cannot
    converge on a decision or they don't do a good job of maintaining
    the setpoint. You might also look at Type108. It sounds as though
    you have set up Type2 properly but Type108 offers a somewhat more
    intuitive thermostat model.  You can disable stages 2 and 3 by
    setting very high (or low, as appropriate) setpoints for those
    stages.<br>
    kind regards,<br>
     David<br>
    <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 04/27/2016 11:39, massimo truant
      wrote:<br>
    </div>
    <blockquote cite="mid:5720eb3c.81da1c0a.6564a.6bdb@mx.google.com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=windows-1252">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <style><!--
/* Font Definitions */
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:#954F72;
        text-decoration:underline;}
.MsoChpDefault
        {mso-style-type:export-only;}
@page WordSection1
        {size:612.0pt 792.0pt;
        margin:70.85pt 2.0cm 2.0cm 2.0cm;}
div.WordSection1
        {page:WordSection1;}
--></style>
      <div class="WordSection1">
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Good afternoon,</p>
        <p class="MsoNormal">I have a problem with type 2d. I use it
          like a thermostat but it doesnt work always. In my project
          type 2d activates a ventilation system when the difference
          between imput 1 and imput 2 is less than 2°C and it has to
          stop the system when that difference is less than -2.</p>
        <p class="MsoNormal">Example</p>
        <p class="MsoNormal">25° is the temperature that I want</p>
        <p class="MsoNormal">The system should be activated when
          temperature reaches 27°C and should stop its action when the
          temperature reaches 23°C.</p>
        <p class="MsoNormal">But it doesn’t work sometimes the system is
          activated when the temperature is near 26°C and it is stopped
          when the temperature is near 24.</p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Someone knows the reason of that?</p>
        <p class="MsoNormal">Thanks to all</p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Inviato da <a moz-do-not-send="true"
            href="https://go.microsoft.com/fwlink/?LinkId=550986">Posta</a>
          per Windows 10</p>
        <p class="MsoNormal"><span
            style="font-size:12.0pt;font-family:"Times New
            Roman",serif"><o:p> </o:p></span></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>