[TRNSYS-users] Generating Shading/insolation matrix - Success and fail with two different TRNSYS versions
Roberto Ruiz
doppler83 at gmail.com
Tue May 12 07:25:43 PDT 2015
Dear all,
I'm experiencing a problem when try to generate the shading/insolation
matrices for the detailed model of /Beam/diffused distribution/ (TRNBUILD).
I have the TRNSYS version 17.02.0004 (in my computer).
The error is the following:
/TRNSHD Message 14 : The internal solar distribution did not sum up
1. Make sure that the zones with detailed beam radiation mode are CONVEX
and CLOSED!!//"/
The file (shd) indicates the surface and thermal zone (external wall -
surface 237 - zone B6_F2_OF) that is failing.
After verifying again the idf file I could not find any error in the
geometrical model (.idf).
I have also the TRNSYS version 17.01.0025 (in the server of the lab) and
when I do the same exercise: importing the same idf to TRNSYS, selecting
detailed radiation model for all the zones and generating
shading/insolation matrices. Everything goes well!
In order to understand better the problem, I modified the .bui model
used in the version 17.02.0004 by setting the standard radiation model
only for problematic zone (B6_F2_OF) and the remaining zones were kept
as detailed. Then I could get the shading/insolation matrices.
Then looking at the matrix files (_vfm) provided by the 2 versions
(below), I realized that version 17.02.0004 doesn't calculate the matrix
for the zone in question (what was supposed to happen) but at the same
time, it means that the version 17.01.0025 does not see any problem
with this zone (B6_F2_OF). /*
Version 17.02.0004*/
/*Version 17.01.0025*/
Since the idf file used is exactly the same in both cases, the problem
must come from the TRNSYS version.
Any of you have experience something similar? Any clue?
I attach the idf file used and the shd file providing the error.
Best Regards,
Roberto Ruiz
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150512/8ea66d31/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 44997 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150512/8ea66d31/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 79458 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150512/8ea66d31/attachment-0003.png>
-------------- next part --------------
!- =========== BUI-Template for TRNSYS 17 ==========
!-T17_Template_Start
!-*********************************************************************************************************************************************************************************************************
!-* TRNBuild 1.0.142
!-*********************************************************************************************************************************************************************************************************
!-* BUILDING DESCRIPTIONS FILE TRNSYS
!-* FOR BUILDING:
!-* GET BY WORKING WITH TRNBuild 1.0 for Windows
!-*********************************************************************************************************************************************************************************************************
!-*
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-* C o m m e n t s
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-* P r o j e c t
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*+++ PROJECT
!-*+++ TITLE=BELGIAN DEMO - ISIL BUILDING
!-*+++ DESCRIPTION=EDUCATIONAL BUILDING (HEPL)
!-*+++ CREATED=ROBERTO RUIZ
!-*+++ ADDRESS=UNIVERSITÉ DE LIÈGE (ULG)
!-*+++ CITY=LIEGE
!-*+++ SWITCH=UNDEFINED
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-* P r o p e r t i e s
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-PROPERTIES
!- DENSITY=1.204 : CAPACITY=1.012 : PRESSURE=101325.000 : HVAPOR=2454.0 : SIGMA=2.041e-007 : RTEMP=293.15
!-*--- alpha calculation -------------------
!- KFLOORUP=7.2 : EFLOORUP=0.31 : KFLOORDOWN=3.888 : EFLOORDOWN=0.31
!- KCEILUP=7.2 : ECEILUP=0.31 : KCEILDOWN=3.888 : ECEILDOWN=0.31
!- KVERTICAL=5.76 : EVERTICAL=0.3
!-*
!-*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
!-TYPES
!-*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
!-*
!-*--------------------------------------------------------------------------------------
!-* L a y e r s
!-*--------------------------------------------------------------------------------------
!-LAYER PLASTERBOA
!- CONDUCTIVITY= 0.576 : CAPACITY= 0.84 : DENSITY= 950
!-LAYER FBRGLS_ASHRAE
!- CONDUCTIVITY= 0.144 : CAPACITY= 0.84 : DENSITY= 12
!-LAYER WD_SIDN_ASHRA
!- CONDUCTIVITY= 0.504 : CAPACITY= 0.9 : DENSITY= 530
!-LAYER TMBR_FLR_ASHR
!- CONDUCTIVITY= 0.504 : CAPACITY= 1.2 : DENSITY= 650
!-LAYER INS_FLR_ASH
!- RESISTANCE= 6.965
!-LAYER RFDCK_ASHRAE
!- CONDUCTIVITY= 0.504 : CAPACITY= 0.9 : DENSITY= 530
!-LAYER CONC_SLAB
!- CONDUCTIVITY= 4.068 : CAPACITY= 1 : DENSITY= 1400
!-LAYER INS_FLR_ASH_900
!- RESISTANCE= 6.993
!-LAYER CONCRETE
!- CONDUCTIVITY= 4.068 : CAPACITY= 1 : DENSITY= 1400
!-LAYER WATERPROOFING
!- CONDUCTIVITY= 0.61 : CAPACITY= 1 : DENSITY= 1200
!-LAYER MINERAL_WOOL
!- CONDUCTIVITY= 0.16 : CAPACITY= 0.9 : DENSITY= 80
!-LAYER MORTAR
!- CONDUCTIVITY= 5.04 : CAPACITY= 1 : DENSITY= 2000
!-LAYER STEELPROFILED
!- CONDUCTIVITY=407.942 : CAPACITY= 0.418 : DENSITY= 6600
!-LAYER BRICK_SOLID
!- CONDUCTIVITY= 3.132 : CAPACITY= 1.4 : DENSITY= 1800
!-LAYER BRICK_PERFORATED
!- CONDUCTIVITY= 2.736 : CAPACITY= 1 : DENSITY= 1600
!-LAYER VERTICAL_AIR_LAYER
!- RESISTANCE= 0.047
!-LAYER HORIZONTAL_AIR_LAYER
!- RESISTANCE= 0.047
!-LAYER LIMESTONE
!- CONDUCTIVITY= 3.56 : CAPACITY= 1 : DENSITY= 1800
!-LAYER TILE
!- CONDUCTIVITY= 3.6 : CAPACITY= 1 : DENSITY= 2000
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-* I n p u t s
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-INPUTS TGROUND TBOUNDARY BRIGHT
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-* S c h e d u l e s
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-SCHEDULE WORKDAY
!- HOURS =0.000 8.000 18.000 24.0
!- VALUES=0 1. 0 0
!-SCHEDULE WEEKEND
!- HOURS =0.000 1.000 24.0
!- VALUES=0 0 0
!-SCHEDULE WORKLIGHT
!- HOURS =0.000 8.000 18.000 24.0
!- VALUES=0 1. 0 0
!-SCHEDULE DAYNIGHT
!- HOURS =0.000 6.000 18.000 24.0
!- VALUES=0 1. 0 0
!-SCHEDULE USE
!- DAYS=1 2 3 4 5 6 7
!- HOURLY=WORKDAY WORKDAY WORKDAY WORKDAY WORKDAY WEEKEND WEEKEND
!-SCHEDULE LIGHT
!- DAYS=1 2 3 4 5 6 7
!- HOURLY=WORKLIGHT WORKLIGHT WORKLIGHT WORKLIGHT WORKLIGHT WEEKEND WEEKEND
!-SCHEDULE SETOFF
!- DAYS=1 2 3 4 5 6 7
!- HOURLY=DAYNIGHT DAYNIGHT DAYNIGHT DAYNIGHT DAYNIGHT WEEKEND WEEKEND
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-* W a l l s
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-WALL BND_WALL
!- LAYERS = CONCRETE MORTAR
!- THICKNESS= 0.2 0.08
!- ABS-FRONT= 0.6 : ABS-BACK= 0.6
!- EPS-FRONT= 0.9 : EPS-BACK= 0.9
!- HFRONT = 27.7 : HBACK= 27.7
!-WALL EXT_WALL_NE_EF_AL
!- LAYERS = CONCRETE BRICK_SOLID
!- THICKNESS= 0.3 0.12
!- ABS-FRONT= 0.6 : ABS-BACK= 0.6
!- EPS-FRONT= 0.9 : EPS-BACK= 0.9
!- HFRONT = 27.7 : HBACK= 90
!-WALL EXT_ROOF_SR
!- LAYERS = CONCRETE HORIZONTAL_AIR_LAYER
!- THICKNESS= 0.2 0
!- ABS-FRONT= 0.6 : ABS-BACK= 0.6
!- EPS-FRONT= 0.9 : EPS-BACK= 0.9
!- HFRONT = 36 : HBACK= 90
!-WALL EXT_FLOOR
!- LAYERS = TMBR_FLR_ASHR INS_FLR_ASH
!- THICKNESS= 0.03 0
!- ABS-FRONT= 0.6 : ABS-BACK= 0.6
!- EPS-FRONT= 0.9 : EPS-BACK= 0.9
!- HFRONT = 11 : HBACK= 11
!-WALL BND_CEILING
!- LAYERS = CONC_SLAB
!- THICKNESS= 0.08
!- ABS-FRONT= 0.6 : ABS-BACK= 0.6
!- EPS-FRONT= 0.9 : EPS-BACK= 0.9
!- HFRONT = 11 : HBACK= 11
!-WALL BND_FLOOR
!- LAYERS = TMBR_FLR_ASHR INS_FLR_ASH
!- THICKNESS= 0.03 0
!- ABS-FRONT= 0.6 : ABS-BACK= 0.6
!- EPS-FRONT= 0.9 : EPS-BACK= 0.9
!- HFRONT = 11 : HBACK= 11
!-WALL GROUND_FLOOR
!- LAYERS = CONCRETE MORTAR TILE
!- THICKNESS= 0.2 0.08 0.02
!- ABS-FRONT= 0.6 : ABS-BACK= 0.6
!- EPS-FRONT= 0.9 : EPS-BACK= 0.9
!- HFRONT = 21.2 : HBACK= 0.001
!-WALL ADJ_WALL
!- LAYERS = CONCRETE MORTAR
!- THICKNESS= 0.2 0.08
!- ABS-FRONT= 0.6 : ABS-BACK= 0.6
!- EPS-FRONT= 0.9 : EPS-BACK= 0.9
!- HFRONT = 27.7 : HBACK= 27.7
!-WALL ADJ_CEILING
!- LAYERS = CONCRETE MORTAR TILE
!- THICKNESS= 0.2 0.08 0.02
!- ABS-FRONT= 0.6 : ABS-BACK= 0.6
!- EPS-FRONT= 0.9 : EPS-BACK= 0.9
!- HFRONT = 21.2 : HBACK= 21.2
!-WALL EXT_WALL_SW_EF_L0
!- LAYERS = CONCRETE LIMESTONE
!- THICKNESS= 0.38 0.1
!- ABS-FRONT= 0.6 : ABS-BACK= 0.6
!- EPS-FRONT= 0.9 : EPS-BACK= 0.9
!- HFRONT = 27.7 : HBACK= 90
!-WALL EXT_WALL_SW_EF_RL
!- LAYERS = CONCRETE LIMESTONE
!- THICKNESS= 0.3 0.1
!- ABS-FRONT= 0.6 : ABS-BACK= 0.6
!- EPS-FRONT= 0.9 : EPS-BACK= 0.9
!- HFRONT = 27.7 : HBACK= 90
!-WALL EXT_WALL_SW_EF_GL
!- LAYERS = CONCRETE MINERAL_WOOL HORIZONTAL_AIR_LAYER
!- THICKNESS= 0.2 0.02 0
!- ABS-FRONT= 0.6 : ABS-BACK= 0.6
!- EPS-FRONT= 0.9 : EPS-BACK= 0.9
!- HFRONT = 27.7 : HBACK= 90
!-WALL EXT_WALL_IF_S0
!- LAYERS = CONCRETE LIMESTONE
!- THICKNESS= 0.38 0.1
!- ABS-FRONT= 0.6 : ABS-BACK= 0.6
!- EPS-FRONT= 0.9 : EPS-BACK= 0.9
!- HFRONT = 27.7 : HBACK= 90
!-WALL EXT_WALL_IF_RL
!- LAYERS = CONCRETE BRICK_PERFORATED
!- THICKNESS= 0.38 0.12
!- ABS-FRONT= 0.6 : ABS-BACK= 0.6
!- EPS-FRONT= 0.9 : EPS-BACK= 0.9
!- HFRONT = 27.7 : HBACK= 90
!-WALL EXT_ROOF_FR
!- LAYERS = CONCRETE WATERPROOFING
!- THICKNESS= 0.2 0.08
!- ABS-FRONT= 0.6 : ABS-BACK= 0.6
!- EPS-FRONT= 0.9 : EPS-BACK= 0.9
!- HFRONT = 36 : HBACK= 90
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-* W i n d o w s
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-WINDOW EXT_WINDOW_SG
!- WINID=6001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.3 : UFRAME=10.9091 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
!- CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
!-WINDOW EXT_WINDOW_DG
!- WINID=6001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.3 : UFRAME=10.9091 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
!- CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
!-WINDOW ADJ_WINDOW
!- WINID=6001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.3 : UFRAME=10.9091 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
!- CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-* D e f a u l t G a i n s
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-* O t h e r G a i n s
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-* C o m f o r t
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-* I n f i l t r a t i o n
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-* V e n t i l a t i o n
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-* C o o l i n g
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-* H e a t i n g
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-*
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-* Z o n e s
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-ZONES
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-* O r i e n t a t i o n s
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-ORIENTATIONS H_0_0
!-*
!-*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
!-BUILDING
!-*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
!-
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-* O u t p u t s
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-OUTPUTS
!- TRANSFER : TIMEBASE=1.000
!- DEFAULT
!-*
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-* E n d
!-*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
!-END
!-
!-_EXTENSION_WINPOOL_START_
!-Window 5.2 v5.2.17 DOE-2 Data File : Multi Band Calculation
!-Unit System : SI
!-Name : DOE-2 WINDOW LIB
!-Desc : ASH140 DBLE - MOD
!-Window ID : 6001
!-Tilt : 90.0
!-Glazings : 2
!-Frame : 2 Al w/break 5.680
!-Spacer : 1 Class1 2.330 -0.010 0.138
!-Total Height: 1500.0 mm
!-Total Width : 1200.0 mm
!-Glass Height: 1385.7 mm
!-Glass Width : 1085.7 mm
!-Mullion : None
!-Gap Thick Cond dCond Vis dVis Dens dDens Pr dPr
!-1 Air 13.0 0.02407 7.760 1.722 4.940 1.292 -0.0046 0.720 -0.0002
!-2 0 0 0 0 0 0 0 0 0
!-3 0 0 0 0 0 0 0 0 0
!-4 0 0 0 0 0 0 0 0 0
!-5 0 0 0 0 0 0 0 0 0
!-Angle 0 10 20 30 40 50 60 70 80 90 Hemis
!-Tsol 0.747 0.747 0.745 0.740 0.730 0.707 0.652 0.517 0.263 0.000 0.652
!-Abs1 0.064 0.065 0.066 0.068 0.071 0.075 0.080 0.086 0.094 0.000 0.080
!-Abs2 0.052 0.053 0.053 0.055 0.057 0.058 0.059 0.054 0.041 0.000 0.059
!-Abs3 0 0 0 0 0 0 0 0 0 0 0
!-Abs4 0 0 0 0 0 0 0 0 0 0 0
!-Abs5 0 0 0 0 0 0 0 0 0 0 0
!-Abs6 0 0 0 0 0 0 0 0 0 0 0
!-Rfsol 0.136 0.136 0.136 0.137 0.143 0.160 0.210 0.343 0.602 1.000 0.210
!-Rbsol 0.136 0.136 0.136 0.137 0.143 0.160 0.210 0.343 0.602 1.000 0.210
!-Tvis 0.747 0.747 0.745 0.740 0.730 0.707 0.652 0.517 0.263 0.000 0.652
!-Rfvis 0.136 0.136 0.136 0.137 0.143 0.160 0.210 0.343 0.602 1.000 0.210
!-Rbvis 0.136 0.136 0.136 0.137 0.143 0.160 0.210 0.343 0.602 1.000 0.210
!-SHGC 0.789 0.789 0.787 0.782 0.769 0.739 0.668 0.519 0.267 0.000 0.688
!-SC: 0.81
!-Layer ID# 9991 9991 0 0 0 0
!-Tir 0.000 0.000 0 0 0 0
!-Emis F 0.840 0.840 0 0 0 0
!-Emis B 0.840 0.840 0 0 0 0
!-Thickness(mm) 3.2 3.2 0 0 0 0
!-Cond(W/m2-K ) 333.9 333.9 0 0 0 0
!-Spectral File None None None None None None
!-Overall and Center of Glass Ig U-values (W/m2-K)
!-Outdoor Temperature -17.8 C 15.6 C 26.7 C 37.8 C
!-Solar WdSpd hcout hrout hin
!-(W/m2) (m/s) (W/m2-K)
!-0 0.00 4.00 3.39 2.43 2.12 2.12 2.24 2.24 2.32 2.32 2.49 2.49
!-0 6.71 30.84 3.23 2.58 2.72 2.72 2.80 2.80 2.89 2.89 3.13 3.13
!-783 0.00 4.00 3.52 2.03 2.12 2.12 2.24 2.24 2.32 2.32 2.49 2.49
!-783 6.71 30.84 3.27 2.39 2.72 2.72 2.80 2.80 2.89 2.89 3.13 3.13
!-*** END OF LIBRARY ***
!-***************************************************************************************************
!-*WinID Description Design U-Value g-value T-sol Rf-sol T-vis
!-***************************************************************************************************
!- 6001 ASH140 DBLE - MOD 3.2/13/3.2 2.89 0.789 0.747 0.136 0.747
!-_EXTENSION_WINPOOL_END_
!-
!-_EXTENSION_BuildingGeometry_START_
!-
!-_EXTENSION_BuildingGeometry_END_
!-
!-
!-_EXTENSION_ExternalShadingGeometry_START_
!-
!-_EXTENSION_ExternalShadingGeometry_END_
!-
!-
!-_EXTENSION_GeoPositionGeometry_START_
!-_EXTENSION_GeoPositionGeometry_END_
!-
!-T17_Template_Stop
!- =========== ALL OBJECTS IN CLASS: VERSION ===========
Version,4;
!- =========== ALL OBJECTS IN CLASS: BUILDING ===========
Building,
ISIL BUILDING, !- Name
0.0, !- North Axis {deg}
City, !- Terrain
0, !- Loads Convergence Tolerance Value
0, !- Temperature Convergence Tolerance Value {deltaC}
FullInteriorAndExterior, !- Solar Distribution
0; !- Maximum Number of Warmup Days
!- =========== ALL OBJECTS IN CLASS: LOCATION ===========
Site:Location,
not used, !- LocationName
0.0, !- Latitude {deg}
0.0, !- Longitude {deg}
0.0, !- TimeZone {hr}
0; !- Elevation {m}
GlobalGeometryRules,
UpperLeftCorner, !- Starting Vertex Position
Counterclockwise, !- Vertex Entry Direction
Absolute; !- Coordinate System
!- =========== ALL OBJECTS IN CLASS: CONSTRUCTION ===========
Construction,
GROUND_FLOOR; !- Name
Construction,
EXT_WALL_NE_EF_AL; !- Name
Construction,
EXT_WALL_SW_EF_L0; !- Name
Construction,
EXT_WALL_SW_EF_RL; !- Name
Construction,
EXT_WALL_SW_EF_GL; !- Name
Construction,
EXT_WALL_IF_S0; !- Name
Construction,
EXT_WALL_IF_RL; !- Name
Construction,
EXT_FLOOR; !- Name
Construction,
EXT_ROOF_SR; !- Name
Construction,
EXT_ROOF_FR; !- Name
Construction,
BND_WALL; !- Name
Construction,
BND_FLOOR; !- Name
Construction,
BND_CEILING; !- Name
Construction,
ADJ_WALL; !- Name
Construction,
ADJ_CEILING; !- Name
Construction,
VirtualSurface; !- Name
Construction,
EXT_WINDOW_SG; !- Name
Construction,
EXT_WINDOW_DG; !- Name
Construction,
ADJ_WINDOW; !- Name
!- =========== ALL OBJECTS IN CLASS: SurfaceProperty:OtherSideCoefficients ===========
SurfaceProperty:OtherSideCoefficients,
BOUNDARY=IDENTICAL;
SurfaceProperty:OtherSideCoefficients,
BOUNDARY=INPUT 1*TBOUNDARY;
SurfaceProperty:OtherSideCoefficients,
BOUNDARY=INPUT 1*TGROUND;
SurfaceProperty:OtherSideCoefficients,
BOUNDARY=20;
SurfaceProperty:OtherSideCoefficients,
BOUNDARY=15;
!- =========== ALL OBJECTS IN CLASS: OUPUT ===========
Output:VariableDictionary,Regular;
!- =========== ALL OBJECTS IN CLASS: Zone, Surface ===========
Zone,
B2_S1_UN, !- Name
0.0, !- Direction of Relative North {deg}
39.326026, !- X Origin {m}
0.0, !- Y Origin {m}
0.0, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
23C717, !- Name
Floor, !- Surface Type
GROUND_FLOOR, !- Construction Name
B2_S1_UN, !- Zone Name
Ground, !- Outside Boundary Condition
BOUNDARY=INPUT 1*TGROUND, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.593766518227, !- Vertex 1 X-coordinate {m}
67.937044189933, !- Vertex 1 Y-coordinate {m}
0.000000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
-5.353906496095, !- Vertex 3 X-coordinate {m}
50.238035124848, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
-6.830235325721, !- Vertex 4 X-coordinate {m}
67.112550863540, !- Vertex 4 Y-coordinate {m}
0.000000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
80EE45, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B2_S1_UN, !- Zone Name
Ground, !- Outside Boundary Condition
BOUNDARY=INPUT 1*TGROUND, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.593766518227, !- Vertex 1 X-coordinate {m}
67.937044189933, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
2.593766518227, !- Vertex 2 X-coordinate {m}
67.937044189933, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
-6.830235325721, !- Vertex 3 X-coordinate {m}
67.112550863540, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
-6.830235325721, !- Vertex 4 X-coordinate {m}
67.112550863540, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
D25484, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_S1_UN, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F0_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-6.830235325721, !- Vertex 1 X-coordinate {m}
67.112550863540, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
-5.353906496095, !- Vertex 2 X-coordinate {m}
50.238035124848, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
2.593766518227, !- Vertex 4 X-coordinate {m}
67.937044189933, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
C83B57, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_L0, !- Construction Name
B2_S1_UN, !- Zone Name
Ground, !- Outside Boundary Condition
BOUNDARY=INPUT 1*TGROUND, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-6.830235325721, !- Vertex 1 X-coordinate {m}
67.112550863540, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
-6.830235325721, !- Vertex 2 X-coordinate {m}
67.112550863540, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
-5.353906496095, !- Vertex 3 X-coordinate {m}
50.238035124848, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
-5.353906496095, !- Vertex 4 X-coordinate {m}
50.238035124848, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
A54EC0, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_L0, !- Construction Name
B2_S1_UN, !- Zone Name
Ground, !- Outside Boundary Condition
BOUNDARY=INPUT 1*TGROUND, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-5.353906496095, !- Vertex 1 X-coordinate {m}
50.238035124848, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
-5.353906496095, !- Vertex 2 X-coordinate {m}
50.238035124848, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
-4.402540559418, !- Vertex 3 X-coordinate {m}
50.321268859172, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
-4.402540559418, !- Vertex 4 X-coordinate {m}
50.321268859172, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
4C3C38, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_S1_UN, !- Zone Name
Zone, !- Outside Boundary Condition
B1_S1_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-4.402540559418, !- Vertex 1 X-coordinate {m}
50.321268859172, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
-4.402540559418, !- Vertex 2 X-coordinate {m}
50.321268859172, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
3E54D6, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_S1_UN, !- Zone Name
Zone, !- Outside Boundary Condition
B2_S1_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
2.593766518227, !- Vertex 3 X-coordinate {m}
67.937044189933, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
2.593766518227, !- Vertex 4 X-coordinate {m}
67.937044189933, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B2_S1_SC, !- Name
0.0, !- Direction of Relative North {deg}
39.326026, !- X Origin {m}
9.46, !- Y Origin {m}
0.0, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
B32CE0, !- Name
Floor, !- Surface Type
GROUND_FLOOR, !- Construction Name
B2_S1_SC, !- Zone Name
Ground, !- Outside Boundary Condition
BOUNDARY=INPUT 1*TGROUND, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.187071739319, !- Vertex 1 X-coordinate {m}
68.776349642523, !- Vertex 1 Y-coordinate {m}
0.000000000000, !- Vertex 1 Z-coordinate {m}
13.663400568944, !- Vertex 2 X-coordinate {m}
51.901833903830, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
2.593766518227, !- Vertex 4 X-coordinate {m}
67.937044189933, !- Vertex 4 Y-coordinate {m}
0.000000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
20FD6C, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_S1_SC, !- Zone Name
OtherSideCoefficients, !- Outside Boundary Condition
BOUNDARY=IDENTICAL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.663400568944, !- Vertex 1 X-coordinate {m}
51.901833903830, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
13.663400568944, !- Vertex 2 X-coordinate {m}
51.901833903830, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
12.187071739319, !- Vertex 3 X-coordinate {m}
68.776349642523, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
12.187071739319, !- Vertex 4 X-coordinate {m}
68.776349642523, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
3BE9A4, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_S1_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F0_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.593766518227, !- Vertex 1 X-coordinate {m}
67.937044189933, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
13.663400568944, !- Vertex 3 X-coordinate {m}
51.901833903830, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
12.187071739319, !- Vertex 4 X-coordinate {m}
68.776349642523, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
BDED90, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_S1_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B2_S1_UN, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.593766518227, !- Vertex 1 X-coordinate {m}
67.937044189933, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
2.593766518227, !- Vertex 2 X-coordinate {m}
67.937044189933, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
EFFF39, !- Name
Wall, !- Surface Type
EXT_WALL_IF_S0, !- Construction Name
B2_S1_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.707103380308, !- Vertex 1 X-coordinate {m}
51.818168740863, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
12.707103380308, !- Vertex 2 X-coordinate {m}
51.818168740863, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
13.663400568944, !- Vertex 3 X-coordinate {m}
51.901833903830, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
13.663400568944, !- Vertex 4 X-coordinate {m}
51.901833903830, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
BA0E45, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B2_S1_SC, !- Zone Name
Ground, !- Outside Boundary Condition
BOUNDARY=INPUT 1*TGROUND, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.187071739319, !- Vertex 1 X-coordinate {m}
68.776349642523, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
12.187071739319, !- Vertex 2 X-coordinate {m}
68.776349642523, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
2.593766518227, !- Vertex 3 X-coordinate {m}
67.937044189933, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
2.593766518227, !- Vertex 4 X-coordinate {m}
67.937044189933, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
B26397, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_S1_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B1_S1_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
12.707103380308, !- Vertex 3 X-coordinate {m}
51.818168740863, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
12.707103380308, !- Vertex 4 X-coordinate {m}
51.818168740863, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B6_S1_CL1, !- Name
0.0, !- Direction of Relative North {deg}
56.729463, !- X Origin {m}
67.860144, !- Y Origin {m}
0.0, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
C2F74F, !- Name
Floor, !- Surface Type
GROUND_FLOOR, !- Construction Name
B6_S1_CL1, !- Zone Name
Ground, !- Outside Boundary Condition
BOUNDARY=INPUT 1*TGROUND, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
73.517257553134, !- Vertex 1 X-coordinate {m}
50.190783041650, !- Vertex 1 Y-coordinate {m}
0.000000000000, !- Vertex 1 Z-coordinate {m}
56.911828519733, !- Vertex 2 X-coordinate {m}
16.357320878178, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
45.689599808048, !- Vertex 3 X-coordinate {m}
21.864319033099, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
62.288489505666, !- Vertex 4 X-coordinate {m}
55.689741033696, !- Vertex 4 Y-coordinate {m}
0.000000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
FD4A8F, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B6_S1_CL1, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F1_LB, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
62.288489505666, !- Vertex 1 X-coordinate {m}
55.689741033696, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
45.689599808048, !- Vertex 2 X-coordinate {m}
21.864319033099, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
56.911828519733, !- Vertex 3 X-coordinate {m}
16.357320878178, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
73.517257553134, !- Vertex 4 X-coordinate {m}
50.190783041650, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
9AFB19, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B6_S1_CL1, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F0_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
45.689599808048, !- Vertex 1 X-coordinate {m}
21.864319033099, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
45.689599808048, !- Vertex 2 X-coordinate {m}
21.864319033099, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
56.911828519733, !- Vertex 3 X-coordinate {m}
16.357320878178, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
56.911828519733, !- Vertex 4 X-coordinate {m}
16.357320878178, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
199120, !- Name
Wall, !- Surface Type
EXT_WALL_IF_S0, !- Construction Name
B6_S1_CL1, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
62.288489505666, !- Vertex 1 X-coordinate {m}
55.689741033696, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
62.288489505666, !- Vertex 2 X-coordinate {m}
55.689741033696, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
45.689599808048, !- Vertex 3 X-coordinate {m}
21.864319033099, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
45.689599808048, !- Vertex 4 X-coordinate {m}
21.864319033099, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
EE5EC2, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B6_S1_CL1, !- Zone Name
OtherSideCoefficients, !- Outside Boundary Condition
BOUNDARY=IDENTICAL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
73.517257553134, !- Vertex 1 X-coordinate {m}
50.190783041650, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
73.517257553134, !- Vertex 2 X-coordinate {m}
50.190783041650, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
62.288489505666, !- Vertex 3 X-coordinate {m}
55.689741033696, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
62.288489505666, !- Vertex 4 X-coordinate {m}
55.689741033696, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
7C3219, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B6_S1_CL1, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
56.911828519733, !- Vertex 1 X-coordinate {m}
16.357320878178, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
56.911828519733, !- Vertex 2 X-coordinate {m}
16.357320878178, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
73.517257553134, !- Vertex 3 X-coordinate {m}
50.190783041650, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
73.517257553134, !- Vertex 4 X-coordinate {m}
50.190783041650, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B6_S1_CL2, !- Name
0.0, !- Direction of Relative North {deg}
88.97948, !- X Origin {m}
48.376338, !- Y Origin {m}
0.0, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
2D0686, !- Name
Floor, !- Surface Type
GROUND_FLOOR, !- Construction Name
B6_S1_CL2, !- Zone Name
Ground, !- Outside Boundary Condition
BOUNDARY=INPUT 1*TGROUND, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
56.911828519733, !- Vertex 1 X-coordinate {m}
16.357320878178, !- Vertex 1 Y-coordinate {m}
0.000000000000, !- Vertex 1 Z-coordinate {m}
52.505893082225, !- Vertex 2 X-coordinate {m}
7.380253822592, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
41.284559262741, !- Vertex 3 X-coordinate {m}
12.887673119476, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
45.689599808048, !- Vertex 4 X-coordinate {m}
21.864319033099, !- Vertex 4 Y-coordinate {m}
0.000000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
70E33E, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B6_S1_CL2, !- Zone Name
OtherSideCoefficients, !- Outside Boundary Condition
BOUNDARY=IDENTICAL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
41.284559262741, !- Vertex 1 X-coordinate {m}
12.887673119476, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
41.284559262741, !- Vertex 2 X-coordinate {m}
12.887673119476, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
52.505893082225, !- Vertex 3 X-coordinate {m}
7.380253822592, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
52.505893082225, !- Vertex 4 X-coordinate {m}
7.380253822592, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
D7C7B0, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B6_S1_CL2, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
52.505893082225, !- Vertex 1 X-coordinate {m}
7.380253822592, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
52.505893082225, !- Vertex 2 X-coordinate {m}
7.380253822592, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
56.911828519733, !- Vertex 3 X-coordinate {m}
16.357320878178, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
56.911828519733, !- Vertex 4 X-coordinate {m}
16.357320878178, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
F2B258, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B6_S1_CL2, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F0_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
45.689599808048, !- Vertex 1 X-coordinate {m}
21.864319033099, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
41.284559262741, !- Vertex 2 X-coordinate {m}
12.887673119476, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
52.505893082225, !- Vertex 3 X-coordinate {m}
7.380253822592, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
56.911828519733, !- Vertex 4 X-coordinate {m}
16.357320878178, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
12F867, !- Name
Wall, !- Surface Type
EXT_WALL_IF_S0, !- Construction Name
B6_S1_CL2, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
45.689599808048, !- Vertex 1 X-coordinate {m}
21.864319033099, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
45.689599808048, !- Vertex 2 X-coordinate {m}
21.864319033099, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
41.284559262741, !- Vertex 3 X-coordinate {m}
12.887673119476, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
41.284559262741, !- Vertex 4 X-coordinate {m}
12.887673119476, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
478C64, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B6_S1_CL2, !- Zone Name
Zone, !- Outside Boundary Condition
B6_S1_CL1, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
56.911828519733, !- Vertex 1 X-coordinate {m}
16.357320878178, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
56.911828519733, !- Vertex 2 X-coordinate {m}
16.357320878178, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
45.689599808048, !- Vertex 3 X-coordinate {m}
21.864319033099, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
45.689599808048, !- Vertex 4 X-coordinate {m}
21.864319033099, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
45717D, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B6_S1_CL1, !- Zone Name
Zone, !- Outside Boundary Condition
B6_S1_CL2, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
45.689599808048, !- Vertex 1 X-coordinate {m}
21.864319033099, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
45.689599808048, !- Vertex 2 X-coordinate {m}
21.864319033099, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
56.911828519733, !- Vertex 3 X-coordinate {m}
16.357320878178, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
56.911828519733, !- Vertex 4 X-coordinate {m}
16.357320878178, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B1_S1_CL, !- Name
0.0, !- Direction of Relative North {deg}
56.265, !- X Origin {m}
0.955, !- Y Origin {m}
0.0, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
EEE41B, !- Name
Floor, !- Surface Type
GROUND_FLOOR, !- Construction Name
B1_S1_CL, !- Zone Name
Ground, !- Outside Boundary Condition
BOUNDARY=INPUT 1*TGROUND, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.707103380308, !- Vertex 1 X-coordinate {m}
51.818168740863, !- Vertex 1 Y-coordinate {m}
0.000000000000, !- Vertex 1 Z-coordinate {m}
16.201612885775, !- Vertex 2 X-coordinate {m}
11.875742320874, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
-4.402540559418, !- Vertex 4 X-coordinate {m}
50.321268859172, !- Vertex 4 Y-coordinate {m}
0.000000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
A1B870, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_S1_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F0_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-4.402540559418, !- Vertex 1 X-coordinate {m}
50.321268859172, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053950, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
16.201612885775, !- Vertex 3 X-coordinate {m}
11.875742320874, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
12.707103380308, !- Vertex 4 X-coordinate {m}
51.818168740863, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
6EE34E, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_L0, !- Construction Name
B1_S1_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-4.402540559418, !- Vertex 1 X-coordinate {m}
50.321268859172, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
-4.402540559418, !- Vertex 2 X-coordinate {m}
50.321268859172, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
45F5C3, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_S1_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B2_S1_UN, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
-4.402540559418, !- Vertex 3 X-coordinate {m}
50.321268859172, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
-4.402540559418, !- Vertex 4 X-coordinate {m}
50.321268859172, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
14EE47, !- Name
Wall, !- Surface Type
EXT_WALL_IF_S0, !- Construction Name
B1_S1_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
16.201612885775, !- Vertex 1 X-coordinate {m}
11.875742320874, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
16.201612885775, !- Vertex 2 X-coordinate {m}
11.875742320874, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
12.707103380308, !- Vertex 3 X-coordinate {m}
51.818168740863, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
12.707103380308, !- Vertex 4 X-coordinate {m}
51.818168740863, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
413510, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_S1_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B2_S1_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.707103380308, !- Vertex 1 X-coordinate {m}
51.818168740863, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
12.707103380308, !- Vertex 2 X-coordinate {m}
51.818168740863, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
F91CA1, !- Name
Wall, !- Surface Type
EXT_WALL_IF_S0, !- Construction Name
B1_S1_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.893796264487, !- Vertex 1 X-coordinate {m}
11.673834529015, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
13.893796264487, !- Vertex 2 X-coordinate {m}
11.673834529015, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
16.201612885775, !- Vertex 3 X-coordinate {m}
11.875742320874, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
16.201612885775, !- Vertex 4 X-coordinate {m}
11.875742320874, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
FE6CD6, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_S1_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B1_S1_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-0.908031053950, !- Vertex 1 X-coordinate {m}
10.378842439183, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053950, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
13.893796264487, !- Vertex 3 X-coordinate {m}
11.673834529015, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
13.893796264487, !- Vertex 4 X-coordinate {m}
11.673834529015, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B2_F0_OF, !- Name
0.0, !- Direction of Relative North {deg}
39.326026, !- X Origin {m}
0.0, !- Y Origin {m}
3.91, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
84742A, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_F0_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B2_S1_UN, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.593766518227, !- Vertex 1 X-coordinate {m}
67.937044189933, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
-5.353906496095, !- Vertex 3 X-coordinate {m}
50.238035124848, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
-6.830235325721, !- Vertex 4 X-coordinate {m}
67.112550863540, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
55CA96, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F0_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F0_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-4.402540559418, !- Vertex 1 X-coordinate {m}
50.321268859172, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
-4.402540559418, !- Vertex 2 X-coordinate {m}
50.321268859172, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
3CEA5C, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_F0_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F1_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-6.830235325721, !- Vertex 1 X-coordinate {m}
67.112550863540, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
-5.353906496095, !- Vertex 2 X-coordinate {m}
50.238035124848, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
2.593766518227, !- Vertex 4 X-coordinate {m}
67.937044189933, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
40DD51, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_L0, !- Construction Name
B2_F0_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-6.830235325721, !- Vertex 1 X-coordinate {m}
67.112550863540, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
-6.830235325721, !- Vertex 2 X-coordinate {m}
67.112550863540, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
-5.353906496095, !- Vertex 3 X-coordinate {m}
50.238035124848, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
-5.353906496095, !- Vertex 4 X-coordinate {m}
50.238035124848, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
F2A5E9, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_L0, !- Construction Name
B2_F0_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-5.353906496095, !- Vertex 1 X-coordinate {m}
50.238035124848, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
-5.353906496095, !- Vertex 2 X-coordinate {m}
50.238035124848, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
-4.402540559418, !- Vertex 3 X-coordinate {m}
50.321268859172, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
-4.402540559418, !- Vertex 4 X-coordinate {m}
50.321268859172, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
617641, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B2_F0_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.593766518227, !- Vertex 1 X-coordinate {m}
67.937044189933, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
2.593766518227, !- Vertex 2 X-coordinate {m}
67.937044189933, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
-6.830235325721, !- Vertex 3 X-coordinate {m}
67.112550863540, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
-6.830235325721, !- Vertex 4 X-coordinate {m}
67.112550863540, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
127407, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F0_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F0_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
2.593766518227, !- Vertex 3 X-coordinate {m}
67.937044189933, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
2.593766518227, !- Vertex 4 X-coordinate {m}
67.937044189933, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B2_F0_SC, !- Name
0.0, !- Direction of Relative North {deg}
39.326026, !- X Origin {m}
9.46, !- Y Origin {m}
3.91, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
7423F1, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_F0_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B2_S1_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.187071708591, !- Vertex 1 X-coordinate {m}
68.776349993744, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
13.663400568944, !- Vertex 2 X-coordinate {m}
51.901833903830, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
2.593766487499, !- Vertex 4 X-coordinate {m}
67.937044541155, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
D31381, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_F0_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F1_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.988928359068, !- Vertex 1 X-coordinate {m}
63.420323681069, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
13.663400568944, !- Vertex 3 X-coordinate {m}
51.901833903830, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
12.582233580160, !- Vertex 4 X-coordinate {m}
64.259629133658, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
6554B6, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F0_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F0_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.593766487499, !- Vertex 1 X-coordinate {m}
67.937044541155, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
2.593766487499, !- Vertex 2 X-coordinate {m}
67.937044541155, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
63C225, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B2_F0_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.187071708591, !- Vertex 1 X-coordinate {m}
68.776349993744, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
12.187071708591, !- Vertex 2 X-coordinate {m}
68.776349993744, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
2.593766487499, !- Vertex 3 X-coordinate {m}
67.937044541155, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
2.593766487499, !- Vertex 4 X-coordinate {m}
67.937044541155, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
5BB221, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F0_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F0_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
12.707103380308, !- Vertex 3 X-coordinate {m}
51.818168740863, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
12.707103380308, !- Vertex 4 X-coordinate {m}
51.818168740863, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
7CFF97, !- Name
Wall, !- Surface Type
EXT_WALL_IF_S0, !- Construction Name
B2_F0_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.707103380308, !- Vertex 1 X-coordinate {m}
51.818168740863, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
12.707103380308, !- Vertex 2 X-coordinate {m}
51.818168740863, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
13.663400568944, !- Vertex 3 X-coordinate {m}
51.901833903830, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
13.663400568944, !- Vertex 4 X-coordinate {m}
51.901833903830, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
B9A925, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F0_SC, !- Zone Name
OtherSideCoefficients, !- Outside Boundary Condition
BOUNDARY=IDENTICAL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.663400568944, !- Vertex 1 X-coordinate {m}
51.901833903830, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
13.663400568944, !- Vertex 2 X-coordinate {m}
51.901833903830, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
12.187071708591, !- Vertex 3 X-coordinate {m}
68.776349993744, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
12.187071708591, !- Vertex 4 X-coordinate {m}
68.776349993744, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B6_F0_CL, !- Name
0.0, !- Direction of Relative North {deg}
88.97948, !- X Origin {m}
48.376338, !- Y Origin {m}
3.91, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
C16D0F, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B6_F0_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B6_S1_CL2, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
56.911828519733, !- Vertex 1 X-coordinate {m}
16.357320878178, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
52.505893082225, !- Vertex 2 X-coordinate {m}
7.380253822592, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
41.284559262741, !- Vertex 3 X-coordinate {m}
12.887673119476, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
45.689599808048, !- Vertex 4 X-coordinate {m}
21.864319033099, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
626131, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B6_F0_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B6_S1_CL1, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
56.911828519733, !- Vertex 1 X-coordinate {m}
16.357320878178, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
56.911828519733, !- Vertex 2 X-coordinate {m}
16.357320878178, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
45.689599808048, !- Vertex 3 X-coordinate {m}
21.864319033099, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
45.689599808048, !- Vertex 4 X-coordinate {m}
21.864319033099, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
732C9E, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B6_F0_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F1_LB, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
45.689599808048, !- Vertex 1 X-coordinate {m}
21.864319033099, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
41.284559262741, !- Vertex 2 X-coordinate {m}
12.887673119476, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
52.505893082225, !- Vertex 3 X-coordinate {m}
7.380253822592, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
56.911828519733, !- Vertex 4 X-coordinate {m}
16.357320878178, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
EBDC5E, !- Name
Wall, !- Surface Type
EXT_WALL_IF_S0, !- Construction Name
B6_F0_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
45.689599808048, !- Vertex 1 X-coordinate {m}
21.864319033099, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
45.689599808048, !- Vertex 2 X-coordinate {m}
21.864319033099, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
41.284559262741, !- Vertex 3 X-coordinate {m}
12.887673119476, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
41.284559262741, !- Vertex 4 X-coordinate {m}
12.887673119476, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
EB9389, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B6_F0_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
52.505893082225, !- Vertex 1 X-coordinate {m}
7.380253822592, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
52.505893082225, !- Vertex 2 X-coordinate {m}
7.380253822592, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
56.911828519733, !- Vertex 3 X-coordinate {m}
16.357320878178, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
56.911828519733, !- Vertex 4 X-coordinate {m}
16.357320878178, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
FD0BE5, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B6_F0_CL, !- Zone Name
OtherSideCoefficients, !- Outside Boundary Condition
BOUNDARY=IDENTICAL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
41.284559262741, !- Vertex 1 X-coordinate {m}
12.887673119476, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
41.284559262741, !- Vertex 2 X-coordinate {m}
12.887673119476, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
52.505893082225, !- Vertex 3 X-coordinate {m}
7.380253822592, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
52.505893082225, !- Vertex 4 X-coordinate {m}
7.380253822592, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B1_S1_SC, !- Name
0.0, !- Direction of Relative North {deg}
96.36, !- X Origin {m}
0.955, !- Y Origin {m}
0.0, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
FC0E6F, !- Name
Floor, !- Surface Type
GROUND_FLOOR, !- Construction Name
B1_S1_SC, !- Zone Name
Ground, !- Outside Boundary Condition
BOUNDARY=INPUT 1*TGROUND, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.893796264487, !- Vertex 1 X-coordinate {m}
11.673834529015, !- Vertex 1 Y-coordinate {m}
0.000000000000, !- Vertex 1 Z-coordinate {m}
11.024619423024, !- Vertex 2 X-coordinate {m}
-2.268709539582, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
0.000000000000, !- Vertex 3 X-coordinate {m}
0.000000000000, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
0.000000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
CDB830, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_S1_SC, !- Zone Name
OtherSideCoefficients, !- Outside Boundary Condition
BOUNDARY=IDENTICAL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
11.024619423024, !- Vertex 1 X-coordinate {m}
-2.268709539582, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
11.024619423024, !- Vertex 2 X-coordinate {m}
-2.268709539582, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
13.313760665876, !- Vertex 3 X-coordinate {m}
8.855196326266, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
13.313760665876, !- Vertex 4 X-coordinate {m}
8.855196326266, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
89A01B, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_S1_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F0_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-0.908031053950, !- Vertex 1 X-coordinate {m}
10.378842439183, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
0.000000000000, !- Vertex 2 X-coordinate {m}
0.000000000000, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
11.024619423024, !- Vertex 3 X-coordinate {m}
-2.268709539582, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
13.893796264487, !- Vertex 4 X-coordinate {m}
11.673834529015, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
376070, !- Name
Wall, !- Surface Type
EXT_WALL_IF_S0, !- Construction Name
B1_S1_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.313760665876, !- Vertex 1 X-coordinate {m}
8.855196326266, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
13.313760665876, !- Vertex 2 X-coordinate {m}
8.855196326266, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
13.893796264487, !- Vertex 3 X-coordinate {m}
11.673834529015, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
13.893796264487, !- Vertex 4 X-coordinate {m}
11.673834529015, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
7D4F97, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_S1_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B1_S1_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.893796264487, !- Vertex 1 X-coordinate {m}
11.673834529015, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
13.893796264487, !- Vertex 2 X-coordinate {m}
11.673834529015, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
840AA7, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_L0, !- Construction Name
B1_S1_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-0.908031053950, !- Vertex 1 X-coordinate {m}
10.378842439183, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053950, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
0.000000000000, !- Vertex 3 X-coordinate {m}
0.000000000000, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
0.000000000000, !- Vertex 4 X-coordinate {m}
0.000000000000, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
CE3450, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_L0, !- Construction Name
B1_S1_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
0.000000000000, !- Vertex 1 X-coordinate {m}
0.000000000000, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
0.000000000000, !- Vertex 2 X-coordinate {m}
0.000000000000, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
11.024619423024, !- Vertex 3 X-coordinate {m}
-2.268709539582, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
11.024619423024, !- Vertex 4 X-coordinate {m}
-2.268709539582, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B1_F0_SC, !- Name
0.0, !- Direction of Relative North {deg}
96.36, !- X Origin {m}
0.955, !- Y Origin {m}
3.91, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
4E001F, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F0_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B1_S1_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.893796264487, !- Vertex 1 X-coordinate {m}
11.673834529015, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
11.024619423024, !- Vertex 2 X-coordinate {m}
-2.268709539582, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
0.000000000000, !- Vertex 3 X-coordinate {m}
0.000000000000, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
F227CB, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F0_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F2_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-0.908031053950, !- Vertex 1 X-coordinate {m}
10.378842439183, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
0.000000000000, !- Vertex 2 X-coordinate {m}
0.000000000000, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
11.024619423024, !- Vertex 3 X-coordinate {m}
-2.268709539582, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
13.893796264487, !- Vertex 4 X-coordinate {m}
11.673834529015, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
C8D5D3, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F0_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F1_KT, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.893796264487, !- Vertex 1 X-coordinate {m}
11.673834529015, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
13.893796264487, !- Vertex 2 X-coordinate {m}
11.673834529015, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
7.564604853320, !- Vertex 3 X-coordinate {m}
11.120102031252, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
7.564604853320, !- Vertex 4 X-coordinate {m}
11.120102031252, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
D5890F, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_GL, !- Construction Name
B1_F0_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-0.908031053950, !- Vertex 1 X-coordinate {m}
10.378842439183, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053950, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
-0.592963043918, !- Vertex 3 X-coordinate {m}
6.777598605582, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
-0.592963043918, !- Vertex 4 X-coordinate {m}
6.777598605582, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
60CF3B, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F0_SC, !- Zone Name
OtherSideCoefficients, !- Outside Boundary Condition
BOUNDARY=IDENTICAL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
11.024619423024, !- Vertex 1 X-coordinate {m}
-2.268709539582, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
11.024619423024, !- Vertex 2 X-coordinate {m}
-2.268709539582, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
13.313760665876, !- Vertex 3 X-coordinate {m}
8.855196326266, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
13.313760665876, !- Vertex 4 X-coordinate {m}
8.855196326266, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
5C186E, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_L0, !- Construction Name
B1_F0_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
0.000000000000, !- Vertex 1 X-coordinate {m}
0.000000000000, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
0.000000000000, !- Vertex 2 X-coordinate {m}
0.000000000000, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
7.772760005483, !- Vertex 3 X-coordinate {m}
-1.599523221318, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
7.772760005483, !- Vertex 4 X-coordinate {m}
-1.599523221318, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
1C1421, !- Name
Wall, !- Surface Type
EXT_WALL_IF_S0, !- Construction Name
B1_F0_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.313760665876, !- Vertex 1 X-coordinate {m}
8.855196326266, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
13.313760665876, !- Vertex 2 X-coordinate {m}
8.855196326266, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
13.893796264487, !- Vertex 3 X-coordinate {m}
11.673834529015, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
13.893796264487, !- Vertex 4 X-coordinate {m}
11.673834529015, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B1_F0_OF, !- Name
0.0, !- Direction of Relative North {deg}
56.265, !- X Origin {m}
0.955, !- Y Origin {m}
3.91, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
3A243C, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F0_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B1_S1_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.707103380308, !- Vertex 1 X-coordinate {m}
51.818168740863, !- Vertex 1 Y-coordinate {m}
3.910000000000, !- Vertex 1 Z-coordinate {m}
16.201612885775, !- Vertex 2 X-coordinate {m}
11.875742320874, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
-4.402540559418, !- Vertex 4 X-coordinate {m}
50.321268859172, !- Vertex 4 Y-coordinate {m}
3.910000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
38D5CC, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F0_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F0_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
-4.402540559418, !- Vertex 3 X-coordinate {m}
50.321268859172, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
-4.402540559418, !- Vertex 4 X-coordinate {m}
50.321268859172, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
97B41B, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F0_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F0_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.707103380308, !- Vertex 1 X-coordinate {m}
51.818168740863, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
12.707103380308, !- Vertex 2 X-coordinate {m}
51.818168740863, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
6A5530, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_L0, !- Construction Name
B1_F0_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-4.402540559418, !- Vertex 1 X-coordinate {m}
50.321268859172, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
-4.402540559418, !- Vertex 2 X-coordinate {m}
50.321268859172, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
46356F, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F0_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F1_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
6.518735940348, !- Vertex 2 X-coordinate {m}
23.074438408353, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
15.155743972804, !- Vertex 3 X-coordinate {m}
23.830078697975, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
12.707103380308, !- Vertex 4 X-coordinate {m}
51.818168740863, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
D87908, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F0_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F0_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-0.908031053950, !- Vertex 1 X-coordinate {m}
10.378842439183, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053950, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
13.893796264487, !- Vertex 3 X-coordinate {m}
11.673834529015, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
13.893796264487, !- Vertex 4 X-coordinate {m}
11.673834529015, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
F9E7FE, !- Name
Wall, !- Surface Type
EXT_WALL_IF_S0, !- Construction Name
B1_F0_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.893796264487, !- Vertex 1 X-coordinate {m}
11.673834529015, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
13.893796264487, !- Vertex 2 X-coordinate {m}
11.673834529015, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
16.201612885775, !- Vertex 3 X-coordinate {m}
11.875742320874, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
16.201612885775, !- Vertex 4 X-coordinate {m}
11.875742320874, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
7E2443, !- Name
Wall, !- Surface Type
EXT_WALL_IF_S0, !- Construction Name
B1_F0_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
16.201612885775, !- Vertex 1 X-coordinate {m}
11.875742320874, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
16.201612885775, !- Vertex 2 X-coordinate {m}
11.875742320874, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
12.707103380308, !- Vertex 3 X-coordinate {m}
51.818168740863, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
12.707103380308, !- Vertex 4 X-coordinate {m}
51.818168740863, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
287889, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F0_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F0_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.893796264487, !- Vertex 1 X-coordinate {m}
11.673834529015, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
13.893796264487, !- Vertex 2 X-coordinate {m}
11.673834529015, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
17DCA3, !- Name
Roof, !- Surface Type
EXT_ROOF_SR, !- Construction Name
B2_F0_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.593766487499, !- Vertex 1 X-coordinate {m}
67.937044541155, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
2.988928359068, !- Vertex 2 X-coordinate {m}
63.420323681069, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
12.582233580160, !- Vertex 3 X-coordinate {m}
64.259629133658, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
12.187071708591, !- Vertex 4 X-coordinate {m}
68.776349993744, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B2_F1_OF, !- Name
0.0, !- Direction of Relative North {deg}
39.326026, !- X Origin {m}
0.0, !- Y Origin {m}
7.99, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
EB8C35, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_F1_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F0_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.593766518227, !- Vertex 1 X-coordinate {m}
67.937044189933, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
-5.353906496095, !- Vertex 3 X-coordinate {m}
50.238035124848, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
-6.830235325721, !- Vertex 4 X-coordinate {m}
67.112550863540, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
1FC3FA, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B2_F1_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.988928359068, !- Vertex 1 X-coordinate {m}
63.420323681069, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
2.988928359068, !- Vertex 2 X-coordinate {m}
63.420323681069, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
2.593766518227, !- Vertex 3 X-coordinate {m}
67.937044189933, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
2.593766518227, !- Vertex 4 X-coordinate {m}
67.937044189933, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
18C3EE, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F1_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F1_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
2.988928359068, !- Vertex 3 X-coordinate {m}
63.420323681069, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
2.988928359068, !- Vertex 4 X-coordinate {m}
63.420323681069, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
E0DFF8, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_F1_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F2_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-6.830235325721, !- Vertex 1 X-coordinate {m}
67.112550863540, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
-5.353906496095, !- Vertex 2 X-coordinate {m}
50.238035124848, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
2.593766518227, !- Vertex 4 X-coordinate {m}
67.937044189933, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
946C4F, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B2_F1_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.593766518227, !- Vertex 1 X-coordinate {m}
67.937044189933, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
2.593766518227, !- Vertex 2 X-coordinate {m}
67.937044189933, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
-6.830235325721, !- Vertex 3 X-coordinate {m}
67.112550863540, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
-6.830235325721, !- Vertex 4 X-coordinate {m}
67.112550863540, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
FDD4D5, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B2_F1_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-6.830235325721, !- Vertex 1 X-coordinate {m}
67.112550863540, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
-6.830235325721, !- Vertex 2 X-coordinate {m}
67.112550863540, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
-6.660281627363, !- Vertex 3 X-coordinate {m}
65.169971202261, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
-6.660281627363, !- Vertex 4 X-coordinate {m}
65.169971202261, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
5C4A2A, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B2_F1_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-5.353906496095, !- Vertex 1 X-coordinate {m}
50.238035124848, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
-5.353906496095, !- Vertex 2 X-coordinate {m}
50.238035124848, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
-4.402540559418, !- Vertex 3 X-coordinate {m}
50.321268859172, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
-4.402540559418, !- Vertex 4 X-coordinate {m}
50.321268859172, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
74FAD5, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F1_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F1_CN, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-4.402540559418, !- Vertex 1 X-coordinate {m}
50.321268859172, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
-4.402540559418, !- Vertex 2 X-coordinate {m}
50.321268859172, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B2_F1_SC, !- Name
0.0, !- Direction of Relative North {deg}
43.86, !- X Origin {m}
9.46, !- Y Origin {m}
7.99, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
F7C48B, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_F1_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F0_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.582233580160, !- Vertex 1 X-coordinate {m}
64.259629133658, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
13.663400568944, !- Vertex 2 X-coordinate {m}
51.901833903830, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
2.988928359068, !- Vertex 4 X-coordinate {m}
63.420323681069, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
9CFC37, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_F1_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F2_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.988928359068, !- Vertex 1 X-coordinate {m}
63.420323681069, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
13.663400568944, !- Vertex 3 X-coordinate {m}
51.901833903830, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
12.582233580160, !- Vertex 4 X-coordinate {m}
64.259629133658, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
CF716B, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B2_F1_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.582233580160, !- Vertex 1 X-coordinate {m}
64.259629133658, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
12.582233580160, !- Vertex 2 X-coordinate {m}
64.259629133658, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
2.988928359068, !- Vertex 3 X-coordinate {m}
63.420323681069, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
2.988928359068, !- Vertex 4 X-coordinate {m}
63.420323681069, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
D1A9FE, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B2_F1_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.707103380308, !- Vertex 1 X-coordinate {m}
51.818168740863, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
12.707103380308, !- Vertex 2 X-coordinate {m}
51.818168740863, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
13.663400568944, !- Vertex 3 X-coordinate {m}
51.901833903830, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
13.663400568944, !- Vertex 4 X-coordinate {m}
51.901833903830, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
C2DF83, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F1_SC, !- Zone Name
OtherSideCoefficients, !- Outside Boundary Condition
BOUNDARY=IDENTICAL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.663400568944, !- Vertex 1 X-coordinate {m}
51.901833903830, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
13.663400568944, !- Vertex 2 X-coordinate {m}
51.901833903830, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
12.582233580160, !- Vertex 3 X-coordinate {m}
64.259629133658, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
12.582233580160, !- Vertex 4 X-coordinate {m}
64.259629133658, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
F77CA4, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F1_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F1_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.988928359068, !- Vertex 1 X-coordinate {m}
63.420323681069, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
2.988928359068, !- Vertex 2 X-coordinate {m}
63.420323681069, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
E88351, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F1_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F1_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
12.707103380308, !- Vertex 3 X-coordinate {m}
51.818168740863, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
12.707103380308, !- Vertex 4 X-coordinate {m}
51.818168740863, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B6_F1_LB, !- Name
0.0, !- Direction of Relative North {deg}
56.729463, !- X Origin {m}
67.860144, !- Y Origin {m}
7.99, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
FC7B7A, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B6_F1_LB, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F0_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
56.911828519733, !- Vertex 1 X-coordinate {m}
16.357320878178, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
52.505893082225, !- Vertex 2 X-coordinate {m}
7.380253822592, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
41.284559262741, !- Vertex 3 X-coordinate {m}
12.887673119476, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
45.689599808048, !- Vertex 4 X-coordinate {m}
21.864319033099, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
36CA0C, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B6_F1_LB, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F2_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
44.808863897137, !- Vertex 1 X-coordinate {m}
20.069544539119, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
41.284559262741, !- Vertex 2 X-coordinate {m}
12.887673119476, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
52.505893082225, !- Vertex 3 X-coordinate {m}
7.380253822592, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
56.030641432231, !- Vertex 4 X-coordinate {m}
14.561907467061, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
C08D7D, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B6_F1_LB, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
62.288489505666, !- Vertex 1 X-coordinate {m}
55.689741033696, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
62.288489505666, !- Vertex 2 X-coordinate {m}
55.689741033696, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
41.284559262741, !- Vertex 3 X-coordinate {m}
12.887673119476, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
41.284559262741, !- Vertex 4 X-coordinate {m}
12.887673119476, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
A2C15B, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B6_F1_LB, !- Zone Name
OtherSideCoefficients, !- Outside Boundary Condition
BOUNDARY=IDENTICAL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
73.517257553134, !- Vertex 1 X-coordinate {m}
50.190783041650, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
73.517257553134, !- Vertex 2 X-coordinate {m}
50.190783041650, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
62.288489505666, !- Vertex 3 X-coordinate {m}
55.689741033696, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
62.288489505666, !- Vertex 4 X-coordinate {m}
55.689741033696, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
9456BF, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B6_F1_LB, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
52.505893082225, !- Vertex 1 X-coordinate {m}
7.380253822592, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
52.505893082225, !- Vertex 2 X-coordinate {m}
7.380253822592, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
73.517257553134, !- Vertex 3 X-coordinate {m}
50.190783041650, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
73.517257553134, !- Vertex 4 X-coordinate {m}
50.190783041650, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
DE6A87, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B6_F1_LB, !- Zone Name
OtherSideCoefficients, !- Outside Boundary Condition
BOUNDARY=IDENTICAL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
41.284559262741, !- Vertex 1 X-coordinate {m}
12.887673119476, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
41.284559262741, !- Vertex 2 X-coordinate {m}
12.887673119476, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
52.505893082225, !- Vertex 3 X-coordinate {m}
7.380253822592, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
52.505893082225, !- Vertex 4 X-coordinate {m}
7.380253822592, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
707F7B, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B6_F1_LB, !- Zone Name
Zone, !- Outside Boundary Condition
B6_S1_CL1, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
73.517257553134, !- Vertex 1 X-coordinate {m}
50.190783041650, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
56.911828519733, !- Vertex 2 X-coordinate {m}
16.357320878178, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
45.689599808048, !- Vertex 3 X-coordinate {m}
21.864319033099, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
62.288489505666, !- Vertex 4 X-coordinate {m}
55.689741033696, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
B9FFCF, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F0_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F1_CN, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-4.402540559418, !- Vertex 1 X-coordinate {m}
50.321268859172, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053950, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
7.564604853320, !- Vertex 3 X-coordinate {m}
11.120102031252, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
5643E4, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F0_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F1_KT, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
6.518735940348, !- Vertex 1 X-coordinate {m}
23.074438408353, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
7.564604853320, !- Vertex 2 X-coordinate {m}
11.120102031252, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
16.201612885775, !- Vertex 3 X-coordinate {m}
11.875742320874, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
15.155743972804, !- Vertex 4 X-coordinate {m}
23.830078697975, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B1_F1_KT, !- Name
0.0, !- Direction of Relative North {deg}
84.36, !- X Origin {m}
9.46, !- Y Origin {m}
7.99, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
5105E3, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F1_KT, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F0_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
15.155743972804, !- Vertex 1 X-coordinate {m}
23.830078697975, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
16.201612885775, !- Vertex 2 X-coordinate {m}
11.875742320874, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
7.564604853320, !- Vertex 3 X-coordinate {m}
11.120102031252, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
6.518735940348, !- Vertex 4 X-coordinate {m}
23.074438408353, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
F25638, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F1_KT, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F2_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
6.518735940348, !- Vertex 1 X-coordinate {m}
23.074438408353, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
7.564604853320, !- Vertex 2 X-coordinate {m}
11.120102031252, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
16.201612885775, !- Vertex 3 X-coordinate {m}
11.875742320874, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
15.155743972804, !- Vertex 4 X-coordinate {m}
23.830078697975, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
49B1AA, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B1_F1_KT, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.893796264487, !- Vertex 1 X-coordinate {m}
11.673834529015, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
13.893796264487, !- Vertex 2 X-coordinate {m}
11.673834529015, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
16.201612885775, !- Vertex 3 X-coordinate {m}
11.875742320874, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
16.201612885775, !- Vertex 4 X-coordinate {m}
11.875742320874, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
57E632, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F1_KT, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F1_CN, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
6.518735940348, !- Vertex 1 X-coordinate {m}
23.074438408353, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
6.518735940348, !- Vertex 2 X-coordinate {m}
23.074438408353, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
7.564604853320, !- Vertex 3 X-coordinate {m}
11.120102031252, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
7.564604853320, !- Vertex 4 X-coordinate {m}
11.120102031252, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
F5E0B3, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F1_KT, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F1_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
15.155743972804, !- Vertex 1 X-coordinate {m}
23.830078697975, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
15.155743972804, !- Vertex 2 X-coordinate {m}
23.830078697975, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
6.518735940348, !- Vertex 3 X-coordinate {m}
23.074438408353, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
6.518735940348, !- Vertex 4 X-coordinate {m}
23.074438408353, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
7786F1, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F1_KT, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F0_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
7.564604853320, !- Vertex 1 X-coordinate {m}
11.120102031252, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
7.564604853320, !- Vertex 2 X-coordinate {m}
11.120102031252, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
13.893796264487, !- Vertex 3 X-coordinate {m}
11.673834529015, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
13.893796264487, !- Vertex 4 X-coordinate {m}
11.673834529015, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
4977E0, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B1_F1_KT, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
16.201612885775, !- Vertex 1 X-coordinate {m}
11.875742320874, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
16.201612885775, !- Vertex 2 X-coordinate {m}
11.875742320874, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
15.155743972804, !- Vertex 3 X-coordinate {m}
23.830078697975, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
15.155743972804, !- Vertex 4 X-coordinate {m}
23.830078697975, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B1_F1_CL, !- Name
0.0, !- Direction of Relative North {deg}
56.265, !- X Origin {m}
9.46, !- Y Origin {m}
7.99, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
B99612, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F1_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F0_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.707103380308, !- Vertex 1 X-coordinate {m}
51.818168740863, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
15.155743972804, !- Vertex 2 X-coordinate {m}
23.830078697975, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
6.518735940348, !- Vertex 3 X-coordinate {m}
23.074438408353, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
E0BB02, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B1_F1_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
15.155743972804, !- Vertex 1 X-coordinate {m}
23.830078697975, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
15.155743972804, !- Vertex 2 X-coordinate {m}
23.830078697975, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
12.707103380308, !- Vertex 3 X-coordinate {m}
51.818168740863, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
12.707103380308, !- Vertex 4 X-coordinate {m}
51.818168740863, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
F41E3B, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F1_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F2_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
6.518735940348, !- Vertex 2 X-coordinate {m}
23.074438408353, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
15.155743972804, !- Vertex 3 X-coordinate {m}
23.830078697975, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
12.707103380308, !- Vertex 4 X-coordinate {m}
51.818168740863, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
55FAA5, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F1_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F1_KT, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
6.518735940348, !- Vertex 1 X-coordinate {m}
23.074438408353, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
6.518735940348, !- Vertex 2 X-coordinate {m}
23.074438408353, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
15.155743972804, !- Vertex 3 X-coordinate {m}
23.830078697975, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
15.155743972804, !- Vertex 4 X-coordinate {m}
23.830078697975, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
32B9BE, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F1_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F1_CN, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
6.518735940348, !- Vertex 3 X-coordinate {m}
23.074438408353, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
6.518735940348, !- Vertex 4 X-coordinate {m}
23.074438408353, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
35ABBF, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F1_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F1_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.707103380308, !- Vertex 1 X-coordinate {m}
51.818168740863, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
12.707103380308, !- Vertex 2 X-coordinate {m}
51.818168740863, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B1_F1_CN, !- Name
0.0, !- Direction of Relative North {deg}
56.265, !- X Origin {m}
0.955, !- Y Origin {m}
7.99, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
A844AF, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F1_CN, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F0_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
7.564604853320, !- Vertex 2 X-coordinate {m}
11.120102031252, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
-4.402540559418, !- Vertex 4 X-coordinate {m}
50.321268859172, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
3438A6, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F1_CN, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F0_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-0.908031053950, !- Vertex 1 X-coordinate {m}
10.378842439183, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053950, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
7.564604853320, !- Vertex 3 X-coordinate {m}
11.120102031252, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
7.564604853320, !- Vertex 4 X-coordinate {m}
11.120102031252, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
D87E19, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F1_CN, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F2_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-4.402540559418, !- Vertex 1 X-coordinate {m}
50.321268859172, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053950, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
7.564604853320, !- Vertex 3 X-coordinate {m}
11.120102031252, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
3604FB, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B1_F1_CN, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-4.402540559418, !- Vertex 1 X-coordinate {m}
50.321268859172, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
-4.402540559418, !- Vertex 2 X-coordinate {m}
50.321268859172, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
-3.888321677206, !- Vertex 3 X-coordinate {m}
44.443720140431, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
-3.888321677206, !- Vertex 4 X-coordinate {m}
44.443720140431, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
C37EE7, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F1_CN, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F1_KT, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
7.564604853320, !- Vertex 1 X-coordinate {m}
11.120102031252, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
7.564604853320, !- Vertex 2 X-coordinate {m}
11.120102031252, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
6.518735940348, !- Vertex 3 X-coordinate {m}
23.074438408353, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
6.518735940348, !- Vertex 4 X-coordinate {m}
23.074438408353, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
231A9F, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F1_CN, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F1_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
-4.402540559418, !- Vertex 3 X-coordinate {m}
50.321268859172, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
-4.402540559418, !- Vertex 4 X-coordinate {m}
50.321268859172, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
AAAA20, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F1_CN, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F1_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
6.518735940348, !- Vertex 1 X-coordinate {m}
23.074438408353, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
6.518735940348, !- Vertex 2 X-coordinate {m}
23.074438408353, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B2_F2_SC, !- Name
0.0, !- Direction of Relative North {deg}
43.86, !- X Origin {m}
9.46, !- Y Origin {m}
12.58, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
17EB69, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_F2_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F1_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.582233580160, !- Vertex 1 X-coordinate {m}
64.259629133658, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
13.663400568944, !- Vertex 2 X-coordinate {m}
51.901833903830, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
2.988928359068, !- Vertex 4 X-coordinate {m}
63.420323681069, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
320018, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F2_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F2_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
12.707103380308, !- Vertex 3 X-coordinate {m}
51.818168740863, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
12.707103380308, !- Vertex 4 X-coordinate {m}
51.818168740863, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
EB93F2, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_F2_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F3_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.988928359068, !- Vertex 1 X-coordinate {m}
63.420323681069, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
13.663400568944, !- Vertex 3 X-coordinate {m}
51.901833903830, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
12.582233580160, !- Vertex 4 X-coordinate {m}
64.259629133658, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
68AEB4, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B2_F2_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.707103380308, !- Vertex 1 X-coordinate {m}
51.818168740863, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
12.707103380308, !- Vertex 2 X-coordinate {m}
51.818168740863, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
13.663400568944, !- Vertex 3 X-coordinate {m}
51.901833903830, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
13.663400568944, !- Vertex 4 X-coordinate {m}
51.901833903830, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
20A48A, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F2_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F2_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.988928359068, !- Vertex 1 X-coordinate {m}
63.420323681069, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
2.988928359068, !- Vertex 2 X-coordinate {m}
63.420323681069, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
611B27, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B2_F2_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.582233580160, !- Vertex 1 X-coordinate {m}
64.259629133658, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
12.582233580160, !- Vertex 2 X-coordinate {m}
64.259629133658, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
2.988928359068, !- Vertex 3 X-coordinate {m}
63.420323681069, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
2.988928359068, !- Vertex 4 X-coordinate {m}
63.420323681069, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
D3C8F7, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F2_SC, !- Zone Name
OtherSideCoefficients, !- Outside Boundary Condition
BOUNDARY=IDENTICAL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.663400568944, !- Vertex 1 X-coordinate {m}
51.901833903830, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
13.663400568944, !- Vertex 2 X-coordinate {m}
51.901833903830, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
12.582233580160, !- Vertex 3 X-coordinate {m}
64.259629133658, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
12.582233580160, !- Vertex 4 X-coordinate {m}
64.259629133658, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B2_F2_CL, !- Name
0.0, !- Direction of Relative North {deg}
39.326026, !- X Origin {m}
0.0, !- Y Origin {m}
12.58, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
495408, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_F2_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F1_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.593766487499, !- Vertex 1 X-coordinate {m}
67.937044541155, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
-5.353906496095, !- Vertex 3 X-coordinate {m}
50.238035124848, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
-6.830235356449, !- Vertex 4 X-coordinate {m}
67.112551214762, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
BB3B32, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F2_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F2_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
2.988928359068, !- Vertex 3 X-coordinate {m}
63.420323681069, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
2.988928359068, !- Vertex 4 X-coordinate {m}
63.420323681069, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
A8F124, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_F2_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F3_LB, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-6.830235356449, !- Vertex 1 X-coordinate {m}
67.112551214762, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
-5.353906496095, !- Vertex 2 X-coordinate {m}
50.238035124848, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
2.593766487499, !- Vertex 4 X-coordinate {m}
67.937044541155, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
262966, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B2_F2_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-6.830235356449, !- Vertex 1 X-coordinate {m}
67.112551214762, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
-6.830235356449, !- Vertex 2 X-coordinate {m}
67.112551214762, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
-6.660281627363, !- Vertex 3 X-coordinate {m}
65.169971202261, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
-6.660281627363, !- Vertex 4 X-coordinate {m}
65.169971202261, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
64F9A2, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F2_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F2_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-4.402540559418, !- Vertex 1 X-coordinate {m}
50.321268859172, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
-4.402540559418, !- Vertex 2 X-coordinate {m}
50.321268859172, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
8F0FDF, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B2_F2_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.593766487499, !- Vertex 1 X-coordinate {m}
67.937044541155, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
2.593766487499, !- Vertex 2 X-coordinate {m}
67.937044541155, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
-6.830235356449, !- Vertex 3 X-coordinate {m}
67.112551214762, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
-6.830235356449, !- Vertex 4 X-coordinate {m}
67.112551214762, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
BDE2EC, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B2_F2_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.988928359068, !- Vertex 1 X-coordinate {m}
63.420323681069, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
2.988928359068, !- Vertex 2 X-coordinate {m}
63.420323681069, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
2.593766487499, !- Vertex 3 X-coordinate {m}
67.937044541155, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
2.593766487499, !- Vertex 4 X-coordinate {m}
67.937044541155, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
59E4F9, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B2_F2_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-5.353906496095, !- Vertex 1 X-coordinate {m}
50.238035124848, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
-5.353906496095, !- Vertex 2 X-coordinate {m}
50.238035124848, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
-4.402540559418, !- Vertex 3 X-coordinate {m}
50.321268859172, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
-4.402540559418, !- Vertex 4 X-coordinate {m}
50.321268859172, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B1_F2_CL, !- Name
0.0, !- Direction of Relative North {deg}
56.265, !- X Origin {m}
0.955, !- Y Origin {m}
12.58, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
B4CB7E, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F2_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F1_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.707103380308, !- Vertex 1 X-coordinate {m}
51.818168740863, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
15.155743972804, !- Vertex 2 X-coordinate {m}
23.830078697975, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
6.518735940348, !- Vertex 3 X-coordinate {m}
23.074438408353, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
C6A3C2, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F2_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F3_LB, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-4.402540559418, !- Vertex 1 X-coordinate {m}
50.321268859172, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053950, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
16.201612885775, !- Vertex 3 X-coordinate {m}
11.875742320874, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
12.707103380308, !- Vertex 4 X-coordinate {m}
51.818168740863, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
766882, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B1_F2_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-4.402540559418, !- Vertex 1 X-coordinate {m}
50.321268859172, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
-4.402540559418, !- Vertex 2 X-coordinate {m}
50.321268859172, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
-3.888321677206, !- Vertex 3 X-coordinate {m}
44.443720140431, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
-3.888321677206, !- Vertex 4 X-coordinate {m}
44.443720140431, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
D942A5, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B1_F2_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.893796264487, !- Vertex 1 X-coordinate {m}
11.673834529015, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
13.893796264487, !- Vertex 2 X-coordinate {m}
11.673834529015, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
16.201612885775, !- Vertex 3 X-coordinate {m}
11.875742320874, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
16.201612885775, !- Vertex 4 X-coordinate {m}
11.875742320874, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
EC500A, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F2_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F2_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
-4.402540559418, !- Vertex 3 X-coordinate {m}
50.321268859172, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
-4.402540559418, !- Vertex 4 X-coordinate {m}
50.321268859172, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
664829, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F2_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F2_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-0.908031053950, !- Vertex 1 X-coordinate {m}
10.378842439183, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053950, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
13.893796264487, !- Vertex 3 X-coordinate {m}
11.673834529015, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
13.893796264487, !- Vertex 4 X-coordinate {m}
11.673834529015, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
F1FBD4, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F2_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F2_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.707103380308, !- Vertex 1 X-coordinate {m}
51.818168740863, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
12.707103380308, !- Vertex 2 X-coordinate {m}
51.818168740863, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
A867DC, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B1_F2_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
16.201612885775, !- Vertex 1 X-coordinate {m}
11.875742320874, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
16.201612885775, !- Vertex 2 X-coordinate {m}
11.875742320874, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
12.707103380308, !- Vertex 3 X-coordinate {m}
51.818168740863, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
12.707103380308, !- Vertex 4 X-coordinate {m}
51.818168740863, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
A1C97B, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F2_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F1_CN, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
7.564604853320, !- Vertex 2 X-coordinate {m}
11.120102031252, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
-4.402540559418, !- Vertex 4 X-coordinate {m}
50.321268859172, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
E5B160, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F2_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F1_KT, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
15.155743972804, !- Vertex 1 X-coordinate {m}
23.830078697975, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
16.201612885775, !- Vertex 2 X-coordinate {m}
11.875742320874, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
7.564604853320, !- Vertex 3 X-coordinate {m}
11.120102031252, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
6.518735940348, !- Vertex 4 X-coordinate {m}
23.074438408353, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B1_F2_SC, !- Name
0.0, !- Direction of Relative North {deg}
96.36, !- X Origin {m}
0.955, !- Y Origin {m}
12.58, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
8D1A7D, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F2_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F0_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.893796264487, !- Vertex 1 X-coordinate {m}
11.673834529015, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
11.024619423024, !- Vertex 2 X-coordinate {m}
-2.268709539582, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
0.000000000000, !- Vertex 3 X-coordinate {m}
0.000000000000, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
50F275, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F2_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F4_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-0.908031053950, !- Vertex 1 X-coordinate {m}
10.378842439183, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
0.000000000000, !- Vertex 2 X-coordinate {m}
0.000000000000, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
11.024619423024, !- Vertex 3 X-coordinate {m}
-2.268709539582, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
13.893796264487, !- Vertex 4 X-coordinate {m}
11.673834529015, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
748F07, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_GL, !- Construction Name
B1_F2_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-0.908031053950, !- Vertex 1 X-coordinate {m}
10.378842439183, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053950, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
-0.592963043918, !- Vertex 3 X-coordinate {m}
6.777598605582, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
-0.592963043918, !- Vertex 4 X-coordinate {m}
6.777598605582, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
A998F9, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F2_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F3_LB, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.893796264487, !- Vertex 1 X-coordinate {m}
11.673834529015, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
13.893796264487, !- Vertex 2 X-coordinate {m}
11.673834529015, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
BDBCDF, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B1_F2_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.313760665876, !- Vertex 1 X-coordinate {m}
8.855196326266, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
13.313760665876, !- Vertex 2 X-coordinate {m}
8.855196326266, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
13.893796264487, !- Vertex 3 X-coordinate {m}
11.673834529015, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
13.893796264487, !- Vertex 4 X-coordinate {m}
11.673834529015, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
593347, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F2_SC, !- Zone Name
OtherSideCoefficients, !- Outside Boundary Condition
BOUNDARY=IDENTICAL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
11.024619423024, !- Vertex 1 X-coordinate {m}
-2.268709539582, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
11.024619423024, !- Vertex 2 X-coordinate {m}
-2.268709539582, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
13.313760665876, !- Vertex 3 X-coordinate {m}
8.855196326266, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
13.313760665876, !- Vertex 4 X-coordinate {m}
8.855196326266, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
349964, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F2_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F2_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.893796264487, !- Vertex 1 X-coordinate {m}
11.673834529015, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
13.893796264487, !- Vertex 2 X-coordinate {m}
11.673834529015, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
90A76B, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B6_F1_LB, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F2_LB, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
62.288489505666, !- Vertex 1 X-coordinate {m}
55.689741033696, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
44.808863897137, !- Vertex 2 X-coordinate {m}
20.069544539119, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
56.030641432231, !- Vertex 3 X-coordinate {m}
14.561907467061, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
73.517257553134, !- Vertex 4 X-coordinate {m}
50.190783041650, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B6_F2_LB, !- Name
0.0, !- Direction of Relative North {deg}
56.729463, !- X Origin {m}
67.860144, !- Y Origin {m}
12.58, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
F17E03, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B6_F2_LB, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F1_LB, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
73.517257553134, !- Vertex 1 X-coordinate {m}
50.190783041650, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
56.030641432231, !- Vertex 2 X-coordinate {m}
14.561907467061, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
44.808863897137, !- Vertex 3 X-coordinate {m}
20.069544539119, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
62.288489786191, !- Vertex 4 X-coordinate {m}
55.689740800071, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
3EB900, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B6_F2_LB, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F3_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
46.571016269985, !- Vertex 1 X-coordinate {m}
23.660480281161, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
44.808863897137, !- Vertex 2 X-coordinate {m}
20.069544539119, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
56.030641432231, !- Vertex 3 X-coordinate {m}
14.561907467061, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
57.793015607234, !- Vertex 4 X-coordinate {m}
18.152734289297, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
6CFA21, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B6_F2_LB, !- Zone Name
OtherSideCoefficients, !- Outside Boundary Condition
BOUNDARY=IDENTICAL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
73.517257553134, !- Vertex 1 X-coordinate {m}
50.190783041650, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
73.517257553134, !- Vertex 2 X-coordinate {m}
50.190783041650, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
62.288489786191, !- Vertex 3 X-coordinate {m}
55.689740800071, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
62.288489786191, !- Vertex 4 X-coordinate {m}
55.689740800071, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
C33312, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B6_F2_LB, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
62.288489786191, !- Vertex 1 X-coordinate {m}
55.689740800071, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
62.288489786191, !- Vertex 2 X-coordinate {m}
55.689740800071, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
44.808863897137, !- Vertex 3 X-coordinate {m}
20.069544539119, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
44.808863897137, !- Vertex 4 X-coordinate {m}
20.069544539119, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
E6F13C, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B6_F2_LB, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
56.030641432231, !- Vertex 1 X-coordinate {m}
14.561907467061, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
56.030641432231, !- Vertex 2 X-coordinate {m}
14.561907467061, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
73.517257553134, !- Vertex 3 X-coordinate {m}
50.190783041650, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
73.517257553134, !- Vertex 4 X-coordinate {m}
50.190783041650, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
4DBB16, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B6_F2_LB, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F2_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
44.808863897137, !- Vertex 1 X-coordinate {m}
20.069544539119, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
44.808863897137, !- Vertex 2 X-coordinate {m}
20.069544539119, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
56.030641432231, !- Vertex 3 X-coordinate {m}
14.561907467061, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
56.030641432231, !- Vertex 4 X-coordinate {m}
14.561907467061, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B6_F2_OF, !- Name
0.0, !- Direction of Relative North {deg}
90.690664, !- X Origin {m}
47.342529, !- Y Origin {m}
12.58, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
548454, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B6_F2_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F1_LB, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
56.030641432231, !- Vertex 1 X-coordinate {m}
14.561907467061, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
52.505893082225, !- Vertex 2 X-coordinate {m}
7.380253822592, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
41.284559262741, !- Vertex 3 X-coordinate {m}
12.887673119476, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
44.808864203461, !- Vertex 4 X-coordinate {m}
20.069544448307, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
57144B, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B6_F2_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F3_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
44.808864203461, !- Vertex 1 X-coordinate {m}
20.069544448307, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
41.284559262741, !- Vertex 2 X-coordinate {m}
12.887673119476, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
52.505893082225, !- Vertex 3 X-coordinate {m}
7.380253822592, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
56.030641432231, !- Vertex 4 X-coordinate {m}
14.561907467061, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
DB206A, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B6_F2_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
52.505893082225, !- Vertex 1 X-coordinate {m}
7.380253822592, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
52.505893082225, !- Vertex 2 X-coordinate {m}
7.380253822592, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
56.030641432231, !- Vertex 3 X-coordinate {m}
14.561907467061, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
56.030641432231, !- Vertex 4 X-coordinate {m}
14.561907467061, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
FD319A, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B6_F2_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
44.808864203461, !- Vertex 1 X-coordinate {m}
20.069544448307, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
44.808864203461, !- Vertex 2 X-coordinate {m}
20.069544448307, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
41.284559262741, !- Vertex 3 X-coordinate {m}
12.887673119476, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
41.284559262741, !- Vertex 4 X-coordinate {m}
12.887673119476, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
1B78AC, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B6_F2_OF, !- Zone Name
OtherSideCoefficients, !- Outside Boundary Condition
BOUNDARY=IDENTICAL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
41.284559262741, !- Vertex 1 X-coordinate {m}
12.887673119476, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
41.284559262741, !- Vertex 2 X-coordinate {m}
12.887673119476, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
52.505893082225, !- Vertex 3 X-coordinate {m}
7.380253822592, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
52.505893082225, !- Vertex 4 X-coordinate {m}
7.380253822592, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
D5613A, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B6_F2_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F2_LB, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
56.030641432231, !- Vertex 1 X-coordinate {m}
14.561907467061, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
56.030641432231, !- Vertex 2 X-coordinate {m}
14.561907467061, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
44.808864203461, !- Vertex 3 X-coordinate {m}
20.069544448307, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
44.808864203461, !- Vertex 4 X-coordinate {m}
20.069544448307, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B2_F3_SC, !- Name
0.0, !- Direction of Relative North {deg}
43.86, !- X Origin {m}
9.46, !- Y Origin {m}
17.17, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
CFBF21, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_F3_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F2_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.582233491957, !- Vertex 1 X-coordinate {m}
64.259629125942, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
13.663400568944, !- Vertex 2 X-coordinate {m}
51.901833903830, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
2.988928359068, !- Vertex 4 X-coordinate {m}
63.420323681069, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
53850F, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F3_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F3_LB, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
12.707103380308, !- Vertex 3 X-coordinate {m}
51.818168740863, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
12.707103380308, !- Vertex 4 X-coordinate {m}
51.818168740863, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
8F9F23, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_F3_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F4_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.988928359068, !- Vertex 1 X-coordinate {m}
63.420323681069, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
13.663400568944, !- Vertex 3 X-coordinate {m}
51.901833903830, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
12.582233491957, !- Vertex 4 X-coordinate {m}
64.259629125942, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
72FD7F, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B2_F3_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.707103380308, !- Vertex 1 X-coordinate {m}
51.818168740863, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
12.707103380308, !- Vertex 2 X-coordinate {m}
51.818168740863, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
13.663400568944, !- Vertex 3 X-coordinate {m}
51.901833903830, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
13.663400568944, !- Vertex 4 X-coordinate {m}
51.901833903830, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
439FB8, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F3_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F3_LB, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.988928359068, !- Vertex 1 X-coordinate {m}
63.420323681069, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
2.988928359068, !- Vertex 2 X-coordinate {m}
63.420323681069, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
E2F99C, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B2_F3_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.582233491957, !- Vertex 1 X-coordinate {m}
64.259629125942, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
12.582233491957, !- Vertex 2 X-coordinate {m}
64.259629125942, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
2.988928359068, !- Vertex 3 X-coordinate {m}
63.420323681069, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
2.988928359068, !- Vertex 4 X-coordinate {m}
63.420323681069, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
6B1E35, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F3_SC, !- Zone Name
OtherSideCoefficients, !- Outside Boundary Condition
BOUNDARY=IDENTICAL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.663400568944, !- Vertex 1 X-coordinate {m}
51.901833903830, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
13.663400568944, !- Vertex 2 X-coordinate {m}
51.901833903830, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
12.582233491957, !- Vertex 3 X-coordinate {m}
64.259629125942, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
12.582233491957, !- Vertex 4 X-coordinate {m}
64.259629125942, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B2_F3_LB, !- Name
0.0, !- Direction of Relative North {deg}
39.326026, !- X Origin {m}
0.0, !- Y Origin {m}
17.17, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
BC1F83, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_F3_LB, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F2_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.593766487499, !- Vertex 1 X-coordinate {m}
67.937044541155, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
-5.353906496095, !- Vertex 3 X-coordinate {m}
50.238035124848, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
-6.830235356449, !- Vertex 4 X-coordinate {m}
67.112551214762, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
5DAEDD, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B2_F3_LB, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-5.353906496095, !- Vertex 1 X-coordinate {m}
50.238035124848, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
-5.353906496095, !- Vertex 2 X-coordinate {m}
50.238035124848, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
-4.402540559418, !- Vertex 3 X-coordinate {m}
50.321268859172, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
-4.402540559418, !- Vertex 4 X-coordinate {m}
50.321268859172, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
4A5EC2, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F3_LB, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F3_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
2.988928359068, !- Vertex 3 X-coordinate {m}
63.420323681069, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
2.988928359068, !- Vertex 4 X-coordinate {m}
63.420323681069, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
FC7F93, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_F3_LB, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F4_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-6.830235356449, !- Vertex 1 X-coordinate {m}
67.112551214762, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
-5.353906496095, !- Vertex 2 X-coordinate {m}
50.238035124848, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
2.593766487499, !- Vertex 4 X-coordinate {m}
67.937044541155, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
BB6519, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B2_F3_LB, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-6.830235356449, !- Vertex 1 X-coordinate {m}
67.112551214762, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
-6.830235356449, !- Vertex 2 X-coordinate {m}
67.112551214762, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
-6.660281627363, !- Vertex 3 X-coordinate {m}
65.169971202261, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
-6.660281627363, !- Vertex 4 X-coordinate {m}
65.169971202261, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
A82EBD, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F3_LB, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F3_LB, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-4.402540559418, !- Vertex 1 X-coordinate {m}
50.321268859172, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
-4.402540559418, !- Vertex 2 X-coordinate {m}
50.321268859172, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
36A241, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B2_F3_LB, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.593766487499, !- Vertex 1 X-coordinate {m}
67.937044541155, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
2.593766487499, !- Vertex 2 X-coordinate {m}
67.937044541155, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
-6.830235356449, !- Vertex 3 X-coordinate {m}
67.112551214762, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
-6.830235356449, !- Vertex 4 X-coordinate {m}
67.112551214762, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
C32016, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B2_F3_LB, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.988928359068, !- Vertex 1 X-coordinate {m}
63.420323681069, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
2.988928359068, !- Vertex 2 X-coordinate {m}
63.420323681069, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
2.593766487499, !- Vertex 3 X-coordinate {m}
67.937044541155, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
2.593766487499, !- Vertex 4 X-coordinate {m}
67.937044541155, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B1_F3_LB, !- Name
0.0, !- Direction of Relative North {deg}
56.265, !- X Origin {m}
0.955, !- Y Origin {m}
17.17, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
F4977A, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F3_LB, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F2_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.707103380308, !- Vertex 1 X-coordinate {m}
51.818168740863, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
16.201612885775, !- Vertex 2 X-coordinate {m}
11.875742320874, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
-4.402540559418, !- Vertex 4 X-coordinate {m}
50.321268859172, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
298928, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F3_LB, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F4_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-4.402540559418, !- Vertex 1 X-coordinate {m}
50.321268859172, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053950, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
16.201612885775, !- Vertex 3 X-coordinate {m}
11.875742320874, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
12.707103380308, !- Vertex 4 X-coordinate {m}
51.818168740863, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
A5579D, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B1_F3_LB, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-4.402540559418, !- Vertex 1 X-coordinate {m}
50.321268859172, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
-4.402540559418, !- Vertex 2 X-coordinate {m}
50.321268859172, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
-3.888321677206, !- Vertex 3 X-coordinate {m}
44.443720140431, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
-3.888321677206, !- Vertex 4 X-coordinate {m}
44.443720140431, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
ABD3DB, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F3_LB, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F2_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-0.908031053950, !- Vertex 1 X-coordinate {m}
10.378842439183, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053950, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
13.893796264487, !- Vertex 3 X-coordinate {m}
11.673834529015, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
13.893796264487, !- Vertex 4 X-coordinate {m}
11.673834529015, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
C576E9, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B1_F3_LB, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.893796264487, !- Vertex 1 X-coordinate {m}
11.673834529015, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
13.893796264487, !- Vertex 2 X-coordinate {m}
11.673834529015, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
16.201612885775, !- Vertex 3 X-coordinate {m}
11.875742320874, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
16.201612885775, !- Vertex 4 X-coordinate {m}
11.875742320874, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
90F15A, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F3_LB, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F3_LB, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
-4.402540559418, !- Vertex 3 X-coordinate {m}
50.321268859172, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
-4.402540559418, !- Vertex 4 X-coordinate {m}
50.321268859172, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
230544, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F3_LB, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F3_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.707103380308, !- Vertex 1 X-coordinate {m}
51.818168740863, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
12.707103380308, !- Vertex 2 X-coordinate {m}
51.818168740863, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
E78E15, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B1_F3_LB, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
16.201612885775, !- Vertex 1 X-coordinate {m}
11.875742320874, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
16.201612885775, !- Vertex 2 X-coordinate {m}
11.875742320874, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
12.707103380308, !- Vertex 3 X-coordinate {m}
51.818168740863, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
12.707103380308, !- Vertex 4 X-coordinate {m}
51.818168740863, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
777ED8, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B6_F2_LB, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F3_LB, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
62.288489786191, !- Vertex 1 X-coordinate {m}
55.689740800071, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
46.571016269985, !- Vertex 2 X-coordinate {m}
23.660480281161, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
57.793015607234, !- Vertex 3 X-coordinate {m}
18.152734289297, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
73.517257553134, !- Vertex 4 X-coordinate {m}
50.190783041650, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B6_F3_LB, !- Name
0.0, !- Direction of Relative North {deg}
56.729463, !- X Origin {m}
67.860144, !- Y Origin {m}
17.17, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
BD59DB, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B6_F3_LB, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F2_LB, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
73.517257553134, !- Vertex 1 X-coordinate {m}
50.190783041650, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
57.793015607234, !- Vertex 2 X-coordinate {m}
18.152734289297, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
46.571016269985, !- Vertex 3 X-coordinate {m}
23.660480281161, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
62.288489505666, !- Vertex 4 X-coordinate {m}
55.689741033696, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
1E46D9, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B6_F3_LB, !- Zone Name
OtherSideCoefficients, !- Outside Boundary Condition
BOUNDARY=IDENTICAL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
73.517257553134, !- Vertex 1 X-coordinate {m}
50.190783041650, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
73.517257553134, !- Vertex 2 X-coordinate {m}
50.190783041650, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
62.288489505666, !- Vertex 3 X-coordinate {m}
55.689741033696, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
62.288489505666, !- Vertex 4 X-coordinate {m}
55.689741033696, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
23C9E7, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B6_F3_LB, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F4_LB, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
62.288489505666, !- Vertex 1 X-coordinate {m}
55.689741033696, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
46.571016269985, !- Vertex 2 X-coordinate {m}
23.660480281161, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
57.793015607234, !- Vertex 3 X-coordinate {m}
18.152734289297, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
73.517257553134, !- Vertex 4 X-coordinate {m}
50.190783041650, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
EB5B01, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B6_F3_LB, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
62.288489505666, !- Vertex 1 X-coordinate {m}
55.689741033696, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
62.288489505666, !- Vertex 2 X-coordinate {m}
55.689741033696, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
46.571016269985, !- Vertex 3 X-coordinate {m}
23.660480281161, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
46.571016269985, !- Vertex 4 X-coordinate {m}
23.660480281161, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
D6F34C, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B6_F3_LB, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F3_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
46.571016269985, !- Vertex 1 X-coordinate {m}
23.660480281161, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
46.571016269985, !- Vertex 2 X-coordinate {m}
23.660480281161, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
57.793015607234, !- Vertex 3 X-coordinate {m}
18.152734289297, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
57.793015607234, !- Vertex 4 X-coordinate {m}
18.152734289297, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
545B0F, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B6_F3_LB, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
57.793015607234, !- Vertex 1 X-coordinate {m}
18.152734289297, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
57.793015607234, !- Vertex 2 X-coordinate {m}
18.152734289297, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
73.517257553134, !- Vertex 3 X-coordinate {m}
50.190783041650, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
73.517257553134, !- Vertex 4 X-coordinate {m}
50.190783041650, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B6_F3_OF, !- Name
0.0, !- Direction of Relative North {deg}
87.266974, !- X Origin {m}
49.410946, !- Y Origin {m}
17.17, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
24CD83, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B6_F3_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F2_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
56.030641432231, !- Vertex 1 X-coordinate {m}
14.561907467061, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
52.505893082225, !- Vertex 2 X-coordinate {m}
7.380253822592, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
41.284559262741, !- Vertex 3 X-coordinate {m}
12.887673119476, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
44.808864203461, !- Vertex 4 X-coordinate {m}
20.069544448307, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
2376E9, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B6_F3_OF, !- Zone Name
OtherSideCoefficients, !- Outside Boundary Condition
BOUNDARY=IDENTICAL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
41.284559262741, !- Vertex 1 X-coordinate {m}
12.887673119476, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
41.284559262741, !- Vertex 2 X-coordinate {m}
12.887673119476, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
52.505893082225, !- Vertex 3 X-coordinate {m}
7.380253822592, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
52.505893082225, !- Vertex 4 X-coordinate {m}
7.380253822592, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
5973A4, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B6_F3_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F4_LB, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
46.571016269985, !- Vertex 1 X-coordinate {m}
23.660480281161, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
41.284559262741, !- Vertex 2 X-coordinate {m}
12.887673119476, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
52.505893082225, !- Vertex 3 X-coordinate {m}
7.380253822592, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
57.793015607234, !- Vertex 4 X-coordinate {m}
18.152734289297, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
F73EBB, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B6_F3_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
46.571016269985, !- Vertex 1 X-coordinate {m}
23.660480281161, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
46.571016269985, !- Vertex 2 X-coordinate {m}
23.660480281161, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
41.284559262741, !- Vertex 3 X-coordinate {m}
12.887673119476, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
41.284559262741, !- Vertex 4 X-coordinate {m}
12.887673119476, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
CB1377, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B6_F3_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F3_LB, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
57.793015607234, !- Vertex 1 X-coordinate {m}
18.152734289297, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
57.793015607234, !- Vertex 2 X-coordinate {m}
18.152734289297, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
46.571016269985, !- Vertex 3 X-coordinate {m}
23.660480281161, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
46.571016269985, !- Vertex 4 X-coordinate {m}
23.660480281161, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
8E85EC, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B6_F3_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
52.505893082225, !- Vertex 1 X-coordinate {m}
7.380253822592, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
52.505893082225, !- Vertex 2 X-coordinate {m}
7.380253822592, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
57.793015607234, !- Vertex 3 X-coordinate {m}
18.152734289297, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
57.793015607234, !- Vertex 4 X-coordinate {m}
18.152734289297, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
207770, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B6_F3_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F2_LB, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
57.793015607234, !- Vertex 1 X-coordinate {m}
18.152734289297, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
56.030641432231, !- Vertex 2 X-coordinate {m}
14.561907467061, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
44.808864203461, !- Vertex 3 X-coordinate {m}
20.069544448307, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
46.571016269985, !- Vertex 4 X-coordinate {m}
23.660480281161, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B2_F4_SC, !- Name
0.0, !- Direction of Relative North {deg}
43.86, !- X Origin {m}
9.46, !- Y Origin {m}
21.76, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
CF6319, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_F4_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F3_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.582233580160, !- Vertex 1 X-coordinate {m}
64.259629133658, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
13.663400568944, !- Vertex 2 X-coordinate {m}
51.901833903830, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
2.988928359068, !- Vertex 4 X-coordinate {m}
63.420323681069, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
6AF848, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_F4_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F5_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.988928359068, !- Vertex 1 X-coordinate {m}
63.420323681069, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
13.663400568944, !- Vertex 3 X-coordinate {m}
51.901833903830, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
12.582233580160, !- Vertex 4 X-coordinate {m}
64.259629133658, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
F1FA20, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B2_F4_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.707103380308, !- Vertex 1 X-coordinate {m}
51.818168740863, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
12.707103380308, !- Vertex 2 X-coordinate {m}
51.818168740863, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
13.663400568944, !- Vertex 3 X-coordinate {m}
51.901833903830, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
13.663400568944, !- Vertex 4 X-coordinate {m}
51.901833903830, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
1C4DEB, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F4_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F4_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.988928359068, !- Vertex 1 X-coordinate {m}
63.420323681069, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
2.988928359068, !- Vertex 2 X-coordinate {m}
63.420323681069, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
EDC019, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B2_F4_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.582233580160, !- Vertex 1 X-coordinate {m}
64.259629133658, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
12.582233580160, !- Vertex 2 X-coordinate {m}
64.259629133658, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
2.988928359068, !- Vertex 3 X-coordinate {m}
63.420323681069, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
2.988928359068, !- Vertex 4 X-coordinate {m}
63.420323681069, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
8972A5, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F4_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F4_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
12.707103380308, !- Vertex 3 X-coordinate {m}
51.818168740863, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
12.707103380308, !- Vertex 4 X-coordinate {m}
51.818168740863, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
2E9111, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F4_SC, !- Zone Name
OtherSideCoefficients, !- Outside Boundary Condition
BOUNDARY=IDENTICAL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.663400568944, !- Vertex 1 X-coordinate {m}
51.901833903830, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
13.663400568944, !- Vertex 2 X-coordinate {m}
51.901833903830, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
12.582233580160, !- Vertex 3 X-coordinate {m}
64.259629133658, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
12.582233580160, !- Vertex 4 X-coordinate {m}
64.259629133658, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B2_F4_CL, !- Name
0.0, !- Direction of Relative North {deg}
39.326026, !- X Origin {m}
0.0, !- Y Origin {m}
21.76, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
A63A83, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_F4_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F3_LB, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.593766487499, !- Vertex 1 X-coordinate {m}
67.937044541155, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
-5.353906496095, !- Vertex 3 X-coordinate {m}
50.238035124848, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
-6.830235356449, !- Vertex 4 X-coordinate {m}
67.112551214762, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
FB4656, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F4_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F4_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-4.402540559418, !- Vertex 1 X-coordinate {m}
50.321268859172, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
-4.402540559418, !- Vertex 2 X-coordinate {m}
50.321268859172, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
4AC671, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_F4_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F5_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-6.830235356449, !- Vertex 1 X-coordinate {m}
67.112551214762, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
-5.353906496095, !- Vertex 2 X-coordinate {m}
50.238035124848, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
2.593766487499, !- Vertex 4 X-coordinate {m}
67.937044541155, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
B43CFA, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B2_F4_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-6.830235356449, !- Vertex 1 X-coordinate {m}
67.112551214762, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
-6.830235356449, !- Vertex 2 X-coordinate {m}
67.112551214762, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
-6.660281627363, !- Vertex 3 X-coordinate {m}
65.169971202261, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
-6.660281627363, !- Vertex 4 X-coordinate {m}
65.169971202261, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
D8FC2A, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B2_F4_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-5.353906496095, !- Vertex 1 X-coordinate {m}
50.238035124848, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
-5.353906496095, !- Vertex 2 X-coordinate {m}
50.238035124848, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
-4.402540559418, !- Vertex 3 X-coordinate {m}
50.321268859172, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
-4.402540559418, !- Vertex 4 X-coordinate {m}
50.321268859172, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
45C0F0, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B2_F4_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.593766487499, !- Vertex 1 X-coordinate {m}
67.937044541155, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
2.593766487499, !- Vertex 2 X-coordinate {m}
67.937044541155, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
-6.830235356449, !- Vertex 3 X-coordinate {m}
67.112551214762, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
-6.830235356449, !- Vertex 4 X-coordinate {m}
67.112551214762, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
E803E3, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B2_F4_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.988928359068, !- Vertex 1 X-coordinate {m}
63.420323681069, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
2.988928359068, !- Vertex 2 X-coordinate {m}
63.420323681069, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
2.593766487499, !- Vertex 3 X-coordinate {m}
67.937044541155, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
2.593766487499, !- Vertex 4 X-coordinate {m}
67.937044541155, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
6DF82A, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F4_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F4_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
2.988928359068, !- Vertex 3 X-coordinate {m}
63.420323681069, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
2.988928359068, !- Vertex 4 X-coordinate {m}
63.420323681069, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B1_F4_CL, !- Name
0.0, !- Direction of Relative North {deg}
56.265, !- X Origin {m}
0.955, !- Y Origin {m}
21.76, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
622B5F, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F4_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F3_LB, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.707103380308, !- Vertex 1 X-coordinate {m}
51.818168740863, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
16.201612885775, !- Vertex 2 X-coordinate {m}
11.875742320874, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
-4.402540559418, !- Vertex 4 X-coordinate {m}
50.321268859172, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
BED4D4, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B1_F4_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
16.201612885775, !- Vertex 1 X-coordinate {m}
11.875742320874, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
16.201612885775, !- Vertex 2 X-coordinate {m}
11.875742320874, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
12.707103380308, !- Vertex 3 X-coordinate {m}
51.818168740863, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
12.707103380308, !- Vertex 4 X-coordinate {m}
51.818168740863, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
63D283, !- Name
Ceiling, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F4_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F5_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-4.402540559418, !- Vertex 1 X-coordinate {m}
50.321268859172, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053950, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
16.201612885775, !- Vertex 3 X-coordinate {m}
11.875742320874, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
12.707103380308, !- Vertex 4 X-coordinate {m}
51.818168740863, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
507FE5, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B1_F4_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-4.402540559418, !- Vertex 1 X-coordinate {m}
50.321268859172, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
-4.402540559418, !- Vertex 2 X-coordinate {m}
50.321268859172, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
-3.888321677206, !- Vertex 3 X-coordinate {m}
44.443720140431, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
-3.888321677206, !- Vertex 4 X-coordinate {m}
44.443720140431, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
14B158, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B1_F4_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.893796264487, !- Vertex 1 X-coordinate {m}
11.673834529015, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
13.893796264487, !- Vertex 2 X-coordinate {m}
11.673834529015, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
16.201612885775, !- Vertex 3 X-coordinate {m}
11.875742320874, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
16.201612885775, !- Vertex 4 X-coordinate {m}
11.875742320874, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
95C5BC, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F4_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F4_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
-4.402540559418, !- Vertex 3 X-coordinate {m}
50.321268859172, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
-4.402540559418, !- Vertex 4 X-coordinate {m}
50.321268859172, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
A43E06, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F4_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F4_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-0.908031053950, !- Vertex 1 X-coordinate {m}
10.378842439183, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053950, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
13.893796264487, !- Vertex 3 X-coordinate {m}
11.673834529015, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
13.893796264487, !- Vertex 4 X-coordinate {m}
11.673834529015, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
46EC59, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F4_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F4_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.707103380308, !- Vertex 1 X-coordinate {m}
51.818168740863, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
12.707103380308, !- Vertex 2 X-coordinate {m}
51.818168740863, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B1_F4_SC, !- Name
0.0, !- Direction of Relative North {deg}
96.36, !- X Origin {m}
0.955, !- Y Origin {m}
21.76, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
2D74C1, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F4_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F2_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.893796264487, !- Vertex 1 X-coordinate {m}
11.673834529015, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
11.024619423024, !- Vertex 2 X-coordinate {m}
-2.268709539582, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
0.000000000000, !- Vertex 3 X-coordinate {m}
0.000000000000, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
93C87D, !- Name
Roof, !- Surface Type
EXT_ROOF_SR, !- Construction Name
B1_F4_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-0.908031053950, !- Vertex 1 X-coordinate {m}
10.378842439183, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
0.000000000000, !- Vertex 2 X-coordinate {m}
0.000000000000, !- Vertex 2 Y-coordinate {m}
30.940000000000, !- Vertex 2 Z-coordinate {m}
11.024619423024, !- Vertex 3 X-coordinate {m}
-2.268709539582, !- Vertex 3 Y-coordinate {m}
30.940000000000, !- Vertex 3 Z-coordinate {m}
13.893796264487, !- Vertex 4 X-coordinate {m}
11.673834529015, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
139156, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F4_SC, !- Zone Name
OtherSideCoefficients, !- Outside Boundary Condition
BOUNDARY=IDENTICAL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
11.024619423024, !- Vertex 1 X-coordinate {m}
-2.268709539582, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
11.024619423024, !- Vertex 2 X-coordinate {m}
-2.268709539582, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
13.313760665876, !- Vertex 3 X-coordinate {m}
8.855196326266, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
13.313760665876, !- Vertex 4 X-coordinate {m}
8.855196326266, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
E2D9E7, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B1_F4_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-0.592963043918, !- Vertex 1 X-coordinate {m}
6.777598605582, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
-0.592963043918, !- Vertex 2 X-coordinate {m}
6.777598605582, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
0.000000000000, !- Vertex 3 X-coordinate {m}
0.000000000000, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
0.000000000000, !- Vertex 4 X-coordinate {m}
0.000000000000, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
809397, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_GL, !- Construction Name
B1_F4_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
7.772760005483, !- Vertex 1 X-coordinate {m}
-1.599523221318, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
7.772760005483, !- Vertex 2 X-coordinate {m}
-1.599523221318, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
11.024619423024, !- Vertex 3 X-coordinate {m}
-2.268709539582, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
11.024619423024, !- Vertex 4 X-coordinate {m}
-2.268709539582, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
9BD55D, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F4_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F5_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.893796264487, !- Vertex 1 X-coordinate {m}
11.673834529015, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
13.893796264487, !- Vertex 2 X-coordinate {m}
11.673834529015, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
52F178, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B1_F4_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.313760665876, !- Vertex 1 X-coordinate {m}
8.855196326266, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
13.313760665876, !- Vertex 2 X-coordinate {m}
8.855196326266, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
13.893796264487, !- Vertex 3 X-coordinate {m}
11.673834529015, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
13.893796264487, !- Vertex 4 X-coordinate {m}
11.673834529015, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B6_F4_LB, !- Name
0.0, !- Direction of Relative North {deg}
56.729463, !- X Origin {m}
67.860144, !- Y Origin {m}
21.76, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
E402BF, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B6_F4_LB, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F3_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
57.793015607234, !- Vertex 1 X-coordinate {m}
18.152734289297, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
52.505893082225, !- Vertex 2 X-coordinate {m}
7.380253822592, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
41.284559262741, !- Vertex 3 X-coordinate {m}
12.887673119476, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
46.571016269985, !- Vertex 4 X-coordinate {m}
23.660480281161, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
631840, !- Name
Roof, !- Surface Type
EXT_ROOF_SR, !- Construction Name
B6_F4_LB, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
62.288489786191, !- Vertex 1 X-coordinate {m}
55.689740800071, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
41.284559262741, !- Vertex 2 X-coordinate {m}
12.887673119476, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
52.505893082225, !- Vertex 3 X-coordinate {m}
7.380253822592, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
73.517257553134, !- Vertex 4 X-coordinate {m}
50.190783041650, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
F1D81E, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B6_F4_LB, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
62.288489786191, !- Vertex 1 X-coordinate {m}
55.689740800071, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
62.288489786191, !- Vertex 2 X-coordinate {m}
55.689740800071, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
41.284559262741, !- Vertex 3 X-coordinate {m}
12.887673119476, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
41.284559262741, !- Vertex 4 X-coordinate {m}
12.887673119476, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
605E6B, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B6_F4_LB, !- Zone Name
OtherSideCoefficients, !- Outside Boundary Condition
BOUNDARY=IDENTICAL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
41.284559262741, !- Vertex 1 X-coordinate {m}
12.887673119476, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
41.284559262741, !- Vertex 2 X-coordinate {m}
12.887673119476, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
52.505893082225, !- Vertex 3 X-coordinate {m}
7.380253822592, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
52.505893082225, !- Vertex 4 X-coordinate {m}
7.380253822592, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
9D348B, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B6_F4_LB, !- Zone Name
OtherSideCoefficients, !- Outside Boundary Condition
BOUNDARY=IDENTICAL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
73.517257553134, !- Vertex 1 X-coordinate {m}
50.190783041650, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
73.517257553134, !- Vertex 2 X-coordinate {m}
50.190783041650, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
62.288489786191, !- Vertex 3 X-coordinate {m}
55.689740800071, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
62.288489786191, !- Vertex 4 X-coordinate {m}
55.689740800071, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
82AE15, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B6_F4_LB, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
52.505893082225, !- Vertex 1 X-coordinate {m}
7.380253822592, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
52.505893082225, !- Vertex 2 X-coordinate {m}
7.380253822592, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
73.517257553134, !- Vertex 3 X-coordinate {m}
50.190783041650, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
73.517257553134, !- Vertex 4 X-coordinate {m}
50.190783041650, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
25717A, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B6_F4_LB, !- Zone Name
Zone, !- Outside Boundary Condition
B6_F3_LB, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
73.517257553134, !- Vertex 1 X-coordinate {m}
50.190783041650, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
57.793015607234, !- Vertex 2 X-coordinate {m}
18.152734289297, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
46.571016269985, !- Vertex 3 X-coordinate {m}
23.660480281161, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
62.288489786191, !- Vertex 4 X-coordinate {m}
55.689740800071, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
AFB758, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F4_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F4_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.893796264487, !- Vertex 1 X-coordinate {m}
11.673834529015, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
13.893796264487, !- Vertex 2 X-coordinate {m}
11.673834529015, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B2_F5_SC, !- Name
0.0, !- Direction of Relative North {deg}
43.86, !- X Origin {m}
9.46, !- Y Origin {m}
26.35, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
F98215, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_F5_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F4_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.582233580160, !- Vertex 1 X-coordinate {m}
64.259629133658, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
13.663400568944, !- Vertex 2 X-coordinate {m}
51.901833903830, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
2.988928359068, !- Vertex 4 X-coordinate {m}
63.420323681069, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
B632D9, !- Name
Roof, !- Surface Type
EXT_ROOF_SR, !- Construction Name
B2_F5_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.988928359068, !- Vertex 1 X-coordinate {m}
63.420323681069, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
30.940000000000, !- Vertex 2 Z-coordinate {m}
13.663400568944, !- Vertex 3 X-coordinate {m}
51.901833903830, !- Vertex 3 Y-coordinate {m}
30.940000000000, !- Vertex 3 Z-coordinate {m}
12.582233580160, !- Vertex 4 X-coordinate {m}
64.259629133658, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
555450, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F5_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F5_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.988928359068, !- Vertex 1 X-coordinate {m}
63.420323681069, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
2.988928359068, !- Vertex 2 X-coordinate {m}
63.420323681069, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
55D449, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B2_F5_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.582233580160, !- Vertex 1 X-coordinate {m}
64.259629133658, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
12.582233580160, !- Vertex 2 X-coordinate {m}
64.259629133658, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
2.988928359068, !- Vertex 3 X-coordinate {m}
63.420323681069, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
2.988928359068, !- Vertex 4 X-coordinate {m}
63.420323681069, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
FCB14A, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F5_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F5_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
12.707103380308, !- Vertex 3 X-coordinate {m}
51.818168740863, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
12.707103380308, !- Vertex 4 X-coordinate {m}
51.818168740863, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
82C51D, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B2_F5_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.707103380308, !- Vertex 1 X-coordinate {m}
51.818168740863, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
12.707103380308, !- Vertex 2 X-coordinate {m}
51.818168740863, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
13.663400568944, !- Vertex 3 X-coordinate {m}
51.901833903830, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
13.663400568944, !- Vertex 4 X-coordinate {m}
51.901833903830, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
188307, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F5_SC, !- Zone Name
OtherSideCoefficients, !- Outside Boundary Condition
BOUNDARY=IDENTICAL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
0.0, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.663400568944, !- Vertex 1 X-coordinate {m}
51.901833903830, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
13.663400568944, !- Vertex 2 X-coordinate {m}
51.901833903830, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
12.582233580160, !- Vertex 3 X-coordinate {m}
64.259629133658, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
12.582233580160, !- Vertex 4 X-coordinate {m}
64.259629133658, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B2_F5_OF, !- Name
0.0, !- Direction of Relative North {deg}
39.326026, !- X Origin {m}
0.0, !- Y Origin {m}
26.35, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
F6B9F8, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B2_F5_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F4_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.593766487499, !- Vertex 1 X-coordinate {m}
67.937044541155, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
-5.353906496095, !- Vertex 3 X-coordinate {m}
50.238035124848, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
-6.830235356449, !- Vertex 4 X-coordinate {m}
67.112551214762, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
87BBAE, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B2_F5_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-5.523860194453, !- Vertex 1 X-coordinate {m}
52.180614786127, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
-5.523860194453, !- Vertex 2 X-coordinate {m}
52.180614786127, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
-5.353906496095, !- Vertex 3 X-coordinate {m}
50.238035124848, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
-5.353906496095, !- Vertex 4 X-coordinate {m}
50.238035124848, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
BE6E2F, !- Name
Roof, !- Surface Type
EXT_ROOF_SR, !- Construction Name
B2_F5_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-6.830235356449, !- Vertex 1 X-coordinate {m}
67.112551214762, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
-5.353906496095, !- Vertex 2 X-coordinate {m}
50.238035124848, !- Vertex 2 Y-coordinate {m}
30.940000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
30.940000000000, !- Vertex 3 Z-coordinate {m}
2.593766487499, !- Vertex 4 X-coordinate {m}
67.937044541155, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
D5CE6D, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B2_F5_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.988928359068, !- Vertex 1 X-coordinate {m}
63.420323681069, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
2.988928359068, !- Vertex 2 X-coordinate {m}
63.420323681069, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
2.593766487499, !- Vertex 3 X-coordinate {m}
67.937044541155, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
2.593766487499, !- Vertex 4 X-coordinate {m}
67.937044541155, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
432105, !- Name
Wall, !- Surface Type
EXT_WALL_NE_EF_AL, !- Construction Name
B2_F5_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
2.593766487499, !- Vertex 1 X-coordinate {m}
67.937044541155, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
2.593766487499, !- Vertex 2 X-coordinate {m}
67.937044541155, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
-6.830235356449, !- Vertex 3 X-coordinate {m}
67.112551214762, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
-6.830235356449, !- Vertex 4 X-coordinate {m}
67.112551214762, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
6396E2, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B2_F5_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-5.353906496095, !- Vertex 1 X-coordinate {m}
50.238035124848, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
-5.353906496095, !- Vertex 2 X-coordinate {m}
50.238035124848, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
-4.402540559418, !- Vertex 3 X-coordinate {m}
50.321268859172, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
-4.402540559418, !- Vertex 4 X-coordinate {m}
50.321268859172, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
7BBF55, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F5_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F5_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-4.402540559418, !- Vertex 1 X-coordinate {m}
50.321268859172, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
-4.402540559418, !- Vertex 2 X-coordinate {m}
50.321268859172, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
EF63C8, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B2_F5_OF, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F5_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
2.988928359068, !- Vertex 3 X-coordinate {m}
63.420323681069, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
2.988928359068, !- Vertex 4 X-coordinate {m}
63.420323681069, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
Zone,
B1_F5_CL, !- Name
0.0, !- Direction of Relative North {deg}
56.265, !- X Origin {m}
0.955, !- Y Origin {m}
26.35, !- Z Origin {m}
, !- Type
1; !- Multiplier
BuildingSurface:Detailed,
794287, !- Name
Floor, !- Surface Type
ADJ_CEILING, !- Construction Name
B1_F5_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F4_CL, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.707103380308, !- Vertex 1 X-coordinate {m}
51.818168740863, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
16.201612885775, !- Vertex 2 X-coordinate {m}
11.875742320874, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
-4.402540559418, !- Vertex 4 X-coordinate {m}
50.321268859172, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
4A6C0B, !- Name
Roof, !- Surface Type
EXT_ROOF_SR, !- Construction Name
B1_F5_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-4.402540559418, !- Vertex 1 X-coordinate {m}
50.321268859172, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053950, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
30.940000000000, !- Vertex 2 Z-coordinate {m}
16.201612885775, !- Vertex 3 X-coordinate {m}
11.875742320874, !- Vertex 3 Y-coordinate {m}
30.940000000000, !- Vertex 3 Z-coordinate {m}
12.707103380308, !- Vertex 4 X-coordinate {m}
51.818168740863, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
F87805, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B1_F5_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
16.201612885775, !- Vertex 1 X-coordinate {m}
11.875742320874, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
16.201612885775, !- Vertex 2 X-coordinate {m}
11.875742320874, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
12.707103380308, !- Vertex 3 X-coordinate {m}
51.818168740863, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
12.707103380308, !- Vertex 4 X-coordinate {m}
51.818168740863, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
DECBF0, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_GL, !- Construction Name
B1_F5_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-3.888321677206, !- Vertex 1 X-coordinate {m}
44.443720140431, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
-3.888321677206, !- Vertex 2 X-coordinate {m}
44.443720140431, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
5D6CC0, !- Name
Wall, !- Surface Type
EXT_WALL_IF_RL, !- Construction Name
B1_F5_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
13.893796264487, !- Vertex 1 X-coordinate {m}
11.673834529015, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
13.893796264487, !- Vertex 2 X-coordinate {m}
11.673834529015, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
16.201612885775, !- Vertex 3 X-coordinate {m}
11.875742320874, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
16.201612885775, !- Vertex 4 X-coordinate {m}
11.875742320874, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
7DD381, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F5_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F5_OF, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
4.070095347853, !- Vertex 1 X-coordinate {m}
51.062528451241, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
4.070095347853, !- Vertex 2 X-coordinate {m}
51.062528451241, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
-4.402540559418, !- Vertex 3 X-coordinate {m}
50.321268859172, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
-4.402540559418, !- Vertex 4 X-coordinate {m}
50.321268859172, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
11AFA7, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F5_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F4_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-0.908031053950, !- Vertex 1 X-coordinate {m}
10.378842439183, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053950, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
13.893796264487, !- Vertex 3 X-coordinate {m}
11.673834529015, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
13.893796264487, !- Vertex 4 X-coordinate {m}
11.673834529015, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
24117D, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F5_CL, !- Zone Name
Zone, !- Outside Boundary Condition
B2_F5_SC, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
12.707103380308, !- Vertex 1 X-coordinate {m}
51.818168740863, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
12.707103380308, !- Vertex 2 X-coordinate {m}
51.818168740863, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
4.070095347853, !- Vertex 3 X-coordinate {m}
51.062528451241, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
4.070095347853, !- Vertex 4 X-coordinate {m}
51.062528451241, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
6A73F8, !- Name
Window, !- Surface Type
EXT_WINDOW_DG, !- Construction Name
ED4000, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-6.655923840226, !- Vertex 1 X-coordinate {m}
65.120161467357, !- Vertex 1 Y-coordinate {m}
30.150000000000, !- Vertex 1 Z-coordinate {m}
-6.655923840226, !- Vertex 2 X-coordinate {m}
65.120161467357, !- Vertex 2 Y-coordinate {m}
27.150000000000, !- Vertex 2 Z-coordinate {m}
-5.528217981590, !- Vertex 3 X-coordinate {m}
52.230424521031, !- Vertex 3 Y-coordinate {m}
27.150000000000, !- Vertex 3 Z-coordinate {m}
-5.528217981590, !- Vertex 4 X-coordinate {m}
52.230424521031, !- Vertex 4 Y-coordinate {m}
30.150000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
726ECC, !- Name
Window, !- Surface Type
EXT_WINDOW_DG, !- Construction Name
FC7733, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-6.655923840226, !- Vertex 1 X-coordinate {m}
65.120161467357, !- Vertex 1 Y-coordinate {m}
25.560000000000, !- Vertex 1 Z-coordinate {m}
-6.655923840226, !- Vertex 2 X-coordinate {m}
65.120161467357, !- Vertex 2 Y-coordinate {m}
22.560000000000, !- Vertex 2 Z-coordinate {m}
-5.528217981590, !- Vertex 3 X-coordinate {m}
52.230424521031, !- Vertex 3 Y-coordinate {m}
22.560000000000, !- Vertex 3 Z-coordinate {m}
-5.528217981590, !- Vertex 4 X-coordinate {m}
52.230424521031, !- Vertex 4 Y-coordinate {m}
25.560000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
A33B41, !- Name
Window, !- Surface Type
EXT_WINDOW_DG, !- Construction Name
ADCA2B, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-6.655923840226, !- Vertex 1 X-coordinate {m}
65.120161467357, !- Vertex 1 Y-coordinate {m}
20.970000000000, !- Vertex 1 Z-coordinate {m}
-6.655923840226, !- Vertex 2 X-coordinate {m}
65.120161467357, !- Vertex 2 Y-coordinate {m}
17.970000000000, !- Vertex 2 Z-coordinate {m}
-5.528217981590, !- Vertex 3 X-coordinate {m}
52.230424521031, !- Vertex 3 Y-coordinate {m}
17.970000000000, !- Vertex 3 Z-coordinate {m}
-5.528217981590, !- Vertex 4 X-coordinate {m}
52.230424521031, !- Vertex 4 Y-coordinate {m}
20.970000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
34EAC1, !- Name
Window, !- Surface Type
EXT_WINDOW_DG, !- Construction Name
26574F, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-6.655923840226, !- Vertex 1 X-coordinate {m}
65.120161467357, !- Vertex 1 Y-coordinate {m}
16.380000000000, !- Vertex 1 Z-coordinate {m}
-6.655923840226, !- Vertex 2 X-coordinate {m}
65.120161467357, !- Vertex 2 Y-coordinate {m}
13.380000000000, !- Vertex 2 Z-coordinate {m}
-5.528217981590, !- Vertex 3 X-coordinate {m}
52.230424521031, !- Vertex 3 Y-coordinate {m}
13.380000000000, !- Vertex 3 Z-coordinate {m}
-5.528217981590, !- Vertex 4 X-coordinate {m}
52.230424521031, !- Vertex 4 Y-coordinate {m}
16.380000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
B5D342, !- Name
Window, !- Surface Type
EXT_WINDOW_DG, !- Construction Name
EBA029, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-6.655923840226, !- Vertex 1 X-coordinate {m}
65.120161467357, !- Vertex 1 Y-coordinate {m}
11.790000000000, !- Vertex 1 Z-coordinate {m}
-6.655923840226, !- Vertex 2 X-coordinate {m}
65.120161467357, !- Vertex 2 Y-coordinate {m}
8.790000000000, !- Vertex 2 Z-coordinate {m}
-5.528217981590, !- Vertex 3 X-coordinate {m}
52.230424521031, !- Vertex 3 Y-coordinate {m}
8.790000000000, !- Vertex 3 Z-coordinate {m}
-5.528217981590, !- Vertex 4 X-coordinate {m}
52.230424521031, !- Vertex 4 Y-coordinate {m}
11.790000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
FF631B, !- Name
Window, !- Surface Type
EXT_WINDOW_DG, !- Construction Name
DECBF0, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-3.883963890069, !- Vertex 1 X-coordinate {m}
44.393910405526, !- Vertex 1 Y-coordinate {m}
30.150000000000, !- Vertex 1 Z-coordinate {m}
-3.883963890069, !- Vertex 2 X-coordinate {m}
44.393910405526, !- Vertex 2 Y-coordinate {m}
27.150000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
27.150000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
30.150000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
A2357C, !- Name
Window, !- Surface Type
EXT_WINDOW_DG, !- Construction Name
46D347, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-3.883963890069, !- Vertex 1 X-coordinate {m}
44.393910405526, !- Vertex 1 Y-coordinate {m}
25.560000000000, !- Vertex 1 Z-coordinate {m}
-3.883963890069, !- Vertex 2 X-coordinate {m}
44.393910405526, !- Vertex 2 Y-coordinate {m}
22.560000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
22.560000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
25.560000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
DFB579, !- Name
Window, !- Surface Type
EXT_WINDOW_DG, !- Construction Name
4BF298, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-3.883963890069, !- Vertex 1 X-coordinate {m}
44.393910405526, !- Vertex 1 Y-coordinate {m}
20.970000000000, !- Vertex 1 Z-coordinate {m}
-3.883963890069, !- Vertex 2 X-coordinate {m}
44.393910405526, !- Vertex 2 Y-coordinate {m}
17.970000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
17.970000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
20.970000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
428C4E, !- Name
Window, !- Surface Type
EXT_WINDOW_DG, !- Construction Name
645F2E, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-3.883963890069, !- Vertex 1 X-coordinate {m}
44.393910405526, !- Vertex 1 Y-coordinate {m}
16.380000000000, !- Vertex 1 Z-coordinate {m}
-3.883963890069, !- Vertex 2 X-coordinate {m}
44.393910405526, !- Vertex 2 Y-coordinate {m}
13.380000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
13.380000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
16.380000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
9C1079, !- Name
Window, !- Surface Type
EXT_WINDOW_DG, !- Construction Name
566494, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-3.883963890069, !- Vertex 1 X-coordinate {m}
44.393910405526, !- Vertex 1 Y-coordinate {m}
11.790000000000, !- Vertex 1 Z-coordinate {m}
-3.883963890069, !- Vertex 2 X-coordinate {m}
44.393910405526, !- Vertex 2 Y-coordinate {m}
8.790000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
8.790000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
11.790000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
FE33C0, !- Name
Window, !- Surface Type
EXT_WINDOW_DG, !- Construction Name
E6FDFE, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-0.908031053948, !- Vertex 1 X-coordinate {m}
10.378842439183, !- Vertex 1 Y-coordinate {m}
30.150000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053948, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
27.150000000000, !- Vertex 2 Z-coordinate {m}
-0.597320831053, !- Vertex 3 X-coordinate {m}
6.827408340486, !- Vertex 3 Y-coordinate {m}
27.150000000000, !- Vertex 3 Z-coordinate {m}
-0.597320831053, !- Vertex 4 X-coordinate {m}
6.827408340486, !- Vertex 4 Y-coordinate {m}
30.150000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
7B1659, !- Name
Window, !- Surface Type
EXT_WINDOW_DG, !- Construction Name
E6FDFE, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-0.908031053948, !- Vertex 1 X-coordinate {m}
10.378842439183, !- Vertex 1 Y-coordinate {m}
25.560000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053948, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
22.560000000000, !- Vertex 2 Z-coordinate {m}
-0.597320831053, !- Vertex 3 X-coordinate {m}
6.827408340486, !- Vertex 3 Y-coordinate {m}
22.560000000000, !- Vertex 3 Z-coordinate {m}
-0.597320831053, !- Vertex 4 X-coordinate {m}
6.827408340486, !- Vertex 4 Y-coordinate {m}
25.560000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
DBBFF6, !- Name
Window, !- Surface Type
EXT_WINDOW_DG, !- Construction Name
748F07, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-0.908031053948, !- Vertex 1 X-coordinate {m}
10.378842439183, !- Vertex 1 Y-coordinate {m}
20.970000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053948, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
17.970000000000, !- Vertex 2 Z-coordinate {m}
-0.597320831053, !- Vertex 3 X-coordinate {m}
6.827408340486, !- Vertex 3 Y-coordinate {m}
17.970000000000, !- Vertex 3 Z-coordinate {m}
-0.597320831053, !- Vertex 4 X-coordinate {m}
6.827408340486, !- Vertex 4 Y-coordinate {m}
20.970000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
79E171, !- Name
Window, !- Surface Type
EXT_WINDOW_DG, !- Construction Name
748F07, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-0.908031053948, !- Vertex 1 X-coordinate {m}
10.378842439183, !- Vertex 1 Y-coordinate {m}
16.380000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053948, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
13.380000000000, !- Vertex 2 Z-coordinate {m}
-0.597320831053, !- Vertex 3 X-coordinate {m}
6.827408340486, !- Vertex 3 Y-coordinate {m}
13.380000000000, !- Vertex 3 Z-coordinate {m}
-0.597320831053, !- Vertex 4 X-coordinate {m}
6.827408340486, !- Vertex 4 Y-coordinate {m}
16.380000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
4661BC, !- Name
Window, !- Surface Type
EXT_WINDOW_DG, !- Construction Name
D5890F, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-0.908031053948, !- Vertex 1 X-coordinate {m}
10.378842439183, !- Vertex 1 Y-coordinate {m}
11.790000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053948, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
8.790000000000, !- Vertex 2 Z-coordinate {m}
-0.597320831053, !- Vertex 3 X-coordinate {m}
6.827408340486, !- Vertex 3 Y-coordinate {m}
8.790000000000, !- Vertex 3 Z-coordinate {m}
-0.597320831053, !- Vertex 4 X-coordinate {m}
6.827408340486, !- Vertex 4 Y-coordinate {m}
11.790000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
D65126, !- Name
Wall, !- Surface Type
ADJ_WALL, !- Construction Name
B1_F0_SC, !- Zone Name
Zone, !- Outside Boundary Condition
B1_F1_CN, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
7.564604853320, !- Vertex 1 X-coordinate {m}
11.120102031252, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
7.564604853320, !- Vertex 2 X-coordinate {m}
11.120102031252, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
193B92, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
14E777, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-0.867939412284, !- Vertex 1 X-coordinate {m}
9.920592878061, !- Vertex 1 Y-coordinate {m}
6.910000000000, !- Vertex 1 Z-coordinate {m}
-0.867939412284, !- Vertex 2 X-coordinate {m}
9.920592878061, !- Vertex 2 Y-coordinate {m}
4.710000000000, !- Vertex 2 Z-coordinate {m}
-0.619545545454, !- Vertex 3 X-coordinate {m}
7.081437988500, !- Vertex 3 Y-coordinate {m}
4.710000000000, !- Vertex 3 Z-coordinate {m}
-0.619545545454, !- Vertex 4 X-coordinate {m}
7.081437988500, !- Vertex 4 Y-coordinate {m}
6.910000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
1FC373, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
6A5530, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-3.759984846011, !- Vertex 1 X-coordinate {m}
42.976823447490, !- Vertex 1 Y-coordinate {m}
6.910000000000, !- Vertex 1 Z-coordinate {m}
-3.759984846011, !- Vertex 2 X-coordinate {m}
42.976823447490, !- Vertex 2 Y-coordinate {m}
4.710000000000, !- Vertex 2 Z-coordinate {m}
-1.550586767358, !- Vertex 3 X-coordinate {m}
17.723287850865, !- Vertex 3 Y-coordinate {m}
4.710000000000, !- Vertex 3 Z-coordinate {m}
-1.550586767358, !- Vertex 4 X-coordinate {m}
17.723287850865, !- Vertex 4 Y-coordinate {m}
6.910000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
532ABB, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
E2D9E7, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-0.386403933606, !- Vertex 1 X-coordinate {m}
4.416617171104, !- Vertex 1 Y-coordinate {m}
27.850000000000, !- Vertex 1 Z-coordinate {m}
-0.386403933606, !- Vertex 2 X-coordinate {m}
4.416617171104, !- Vertex 2 Y-coordinate {m}
24.850000000000, !- Vertex 2 Z-coordinate {m}
-0.200762201553, !- Vertex 3 X-coordinate {m}
2.294722464169, !- Vertex 3 Y-coordinate {m}
24.850000000000, !- Vertex 3 Z-coordinate {m}
-0.200762201553, !- Vertex 4 X-coordinate {m}
2.294722464169, !- Vertex 4 Y-coordinate {m}
27.850000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
4E48C4, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
3F7AEE, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-0.386403933606, !- Vertex 1 X-coordinate {m}
4.416617171104, !- Vertex 1 Y-coordinate {m}
19.170000000000, !- Vertex 1 Z-coordinate {m}
-0.386403933606, !- Vertex 2 X-coordinate {m}
4.416617171104, !- Vertex 2 Y-coordinate {m}
15.170000000000, !- Vertex 2 Z-coordinate {m}
-0.200762201553, !- Vertex 3 X-coordinate {m}
2.294722464169, !- Vertex 3 Y-coordinate {m}
15.170000000000, !- Vertex 3 Z-coordinate {m}
-0.200762201553, !- Vertex 4 X-coordinate {m}
2.294722464169, !- Vertex 4 Y-coordinate {m}
19.170000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
2958D3, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
719426, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-0.386403933606, !- Vertex 1 X-coordinate {m}
4.416617171104, !- Vertex 1 Y-coordinate {m}
9.490000000000, !- Vertex 1 Z-coordinate {m}
-0.386403933606, !- Vertex 2 X-coordinate {m}
4.416617171104, !- Vertex 2 Y-coordinate {m}
6.490000000000, !- Vertex 2 Z-coordinate {m}
-0.200762201553, !- Vertex 3 X-coordinate {m}
2.294722464169, !- Vertex 3 Y-coordinate {m}
6.490000000000, !- Vertex 3 Z-coordinate {m}
-0.200762201553, !- Vertex 4 X-coordinate {m}
2.294722464169, !- Vertex 4 Y-coordinate {m}
9.490000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
47152E, !- Name
Door, !- Surface Type
, !- Construction Name
40DD51, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-6.397114862136, !- Vertex 1 X-coordinate {m}
62.161961311373, !- Vertex 1 Y-coordinate {m}
6.710000000000, !- Vertex 1 Z-coordinate {m}
-6.397114862136, !- Vertex 2 X-coordinate {m}
62.161961311373, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
-5.787024662902, !- Vertex 3 X-coordinate {m}
55.188598424731, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
-5.787024662902, !- Vertex 4 X-coordinate {m}
55.188598424731, !- Vertex 4 Y-coordinate {m}
6.710000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
1EE283, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
40DD51, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-6.784957917364, !- Vertex 1 X-coordinate {m}
66.595027717882, !- Vertex 1 Y-coordinate {m}
5.985000000000, !- Vertex 1 Z-coordinate {m}
-6.784957917364, !- Vertex 2 X-coordinate {m}
66.595027717882, !- Vertex 2 Y-coordinate {m}
4.635000000000, !- Vertex 2 Z-coordinate {m}
-6.440692733510, !- Vertex 3 X-coordinate {m}
62.660058660419, !- Vertex 3 Y-coordinate {m}
4.635000000000, !- Vertex 3 Z-coordinate {m}
-6.440692733510, !- Vertex 4 X-coordinate {m}
62.660058660419, !- Vertex 4 Y-coordinate {m}
5.985000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
564CB1, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
40DD51, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-5.743446791529, !- Vertex 1 X-coordinate {m}
54.690501075685, !- Vertex 1 Y-coordinate {m}
5.985000000000, !- Vertex 1 Z-coordinate {m}
-5.743446791529, !- Vertex 2 X-coordinate {m}
54.690501075685, !- Vertex 2 Y-coordinate {m}
4.635000000000, !- Vertex 2 Z-coordinate {m}
-5.399181607675, !- Vertex 3 X-coordinate {m}
50.755532018223, !- Vertex 3 Y-coordinate {m}
4.635000000000, !- Vertex 3 Z-coordinate {m}
-5.399181607675, !- Vertex 4 X-coordinate {m}
50.755532018223, !- Vertex 4 Y-coordinate {m}
5.985000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
E98102, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
FDD4D5, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-6.821519751446, !- Vertex 1 X-coordinate {m}
67.012931393731, !- Vertex 1 Y-coordinate {m}
12.025000000000, !- Vertex 1 Z-coordinate {m}
-6.821519751446, !- Vertex 2 X-coordinate {m}
67.012931393731, !- Vertex 2 Y-coordinate {m}
8.545000000000, !- Vertex 2 Z-coordinate {m}
-6.664639414500, !- Vertex 3 X-coordinate {m}
65.219780937166, !- Vertex 3 Y-coordinate {m}
8.545000000000, !- Vertex 3 Z-coordinate {m}
-6.664639414500, !- Vertex 4 X-coordinate {m}
65.219780937166, !- Vertex 4 Y-coordinate {m}
12.025000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
F42A75, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
752725, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-5.519502407316, !- Vertex 1 X-coordinate {m}
52.130805051222, !- Vertex 1 Y-coordinate {m}
12.025000000000, !- Vertex 1 Z-coordinate {m}
-5.519502407316, !- Vertex 2 X-coordinate {m}
52.130805051222, !- Vertex 2 Y-coordinate {m}
8.545000000000, !- Vertex 2 Z-coordinate {m}
-5.362622070370, !- Vertex 3 X-coordinate {m}
50.337654594657, !- Vertex 3 Y-coordinate {m}
8.545000000000, !- Vertex 3 Z-coordinate {m}
-5.362622070370, !- Vertex 4 X-coordinate {m}
50.337654594657, !- Vertex 4 Y-coordinate {m}
12.025000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
32E7CC, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B1_F2_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
0.000000000000, !- Vertex 1 X-coordinate {m}
0.000000000000, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
0.000000000000, !- Vertex 2 X-coordinate {m}
0.000000000000, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
7.772760005483, !- Vertex 3 X-coordinate {m}
-1.599523221318, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
7.772760005483, !- Vertex 4 X-coordinate {m}
-1.599523221318, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
32CAB3, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
FBAC5D, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
1.763056310714, !- Vertex 1 X-coordinate {m}
-0.362811859300, !- Vertex 1 Y-coordinate {m}
30.038000000000, !- Vertex 1 Z-coordinate {m}
1.763056310714, !- Vertex 2 X-coordinate {m}
-0.362811859300, !- Vertex 2 Y-coordinate {m}
21.872000000000, !- Vertex 2 Z-coordinate {m}
4.701483495240, !- Vertex 3 X-coordinate {m}
-0.967498291466, !- Vertex 3 Y-coordinate {m}
21.872000000000, !- Vertex 3 Z-coordinate {m}
4.701483495240, !- Vertex 4 X-coordinate {m}
-0.967498291466, !- Vertex 4 Y-coordinate {m}
30.038000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
47705D, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
32E7CC, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
1.763056310714, !- Vertex 1 X-coordinate {m}
-0.362811859300, !- Vertex 1 Y-coordinate {m}
21.637600000000, !- Vertex 1 Z-coordinate {m}
1.763056310714, !- Vertex 2 X-coordinate {m}
-0.362811859300, !- Vertex 2 Y-coordinate {m}
12.702400000000, !- Vertex 2 Z-coordinate {m}
4.701483495240, !- Vertex 3 X-coordinate {m}
-0.967498291466, !- Vertex 3 Y-coordinate {m}
12.702400000000, !- Vertex 3 Z-coordinate {m}
4.701483495240, !- Vertex 4 X-coordinate {m}
-0.967498291466, !- Vertex 4 Y-coordinate {m}
21.637600000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
81B64D, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
5C186E, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
1.763056310714, !- Vertex 1 X-coordinate {m}
-0.362811859300, !- Vertex 1 Y-coordinate {m}
12.464400000000, !- Vertex 1 Z-coordinate {m}
1.763056310714, !- Vertex 2 X-coordinate {m}
-0.362811859300, !- Vertex 2 Y-coordinate {m}
4.025600000000, !- Vertex 2 Z-coordinate {m}
4.701483495240, !- Vertex 3 X-coordinate {m}
-0.967498291466, !- Vertex 3 Y-coordinate {m}
4.025600000000, !- Vertex 3 Z-coordinate {m}
4.701483495240, !- Vertex 4 X-coordinate {m}
-0.967498291466, !- Vertex 4 Y-coordinate {m}
12.464400000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
C113D9, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
147F4F, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
7.823862548410, !- Vertex 1 X-coordinate {m}
-1.610039396270, !- Vertex 1 Y-coordinate {m}
6.908470237396, !- Vertex 1 Z-coordinate {m}
7.823862548410, !- Vertex 2 X-coordinate {m}
-1.610039396270, !- Vertex 2 Y-coordinate {m}
4.708470237396, !- Vertex 2 Z-coordinate {m}
10.762289732936, !- Vertex 3 X-coordinate {m}
-2.214725828437, !- Vertex 3 Y-coordinate {m}
4.708470237396, !- Vertex 3 Z-coordinate {m}
10.762289732936, !- Vertex 4 X-coordinate {m}
-2.214725828437, !- Vertex 4 Y-coordinate {m}
6.908470237396; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
EEE9BD, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
F87805, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
15.859308706134, !- Vertex 1 X-coordinate {m}
15.788296997630, !- Vertex 1 Y-coordinate {m}
30.150000000000, !- Vertex 1 Z-coordinate {m}
15.859308706134, !- Vertex 2 X-coordinate {m}
15.788296997630, !- Vertex 2 Y-coordinate {m}
27.150000000000, !- Vertex 2 Z-coordinate {m}
13.049407559949, !- Vertex 3 X-coordinate {m}
47.905614064108, !- Vertex 3 Y-coordinate {m}
27.150000000000, !- Vertex 3 Z-coordinate {m}
13.049407559949, !- Vertex 4 X-coordinate {m}
47.905614064108, !- Vertex 4 Y-coordinate {m}
30.150000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
14ABEE, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
BED4D4, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
15.859308706134, !- Vertex 1 X-coordinate {m}
15.788296997630, !- Vertex 1 Y-coordinate {m}
25.560000000000, !- Vertex 1 Z-coordinate {m}
15.859308706134, !- Vertex 2 X-coordinate {m}
15.788296997630, !- Vertex 2 Y-coordinate {m}
22.560000000000, !- Vertex 2 Z-coordinate {m}
13.049407559949, !- Vertex 3 X-coordinate {m}
47.905614064108, !- Vertex 3 Y-coordinate {m}
22.560000000000, !- Vertex 3 Z-coordinate {m}
13.049407559949, !- Vertex 4 X-coordinate {m}
47.905614064108, !- Vertex 4 Y-coordinate {m}
25.560000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
CB6837, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
E78E15, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
15.859308706134, !- Vertex 1 X-coordinate {m}
15.788296997630, !- Vertex 1 Y-coordinate {m}
20.970000000000, !- Vertex 1 Z-coordinate {m}
15.859308706134, !- Vertex 2 X-coordinate {m}
15.788296997630, !- Vertex 2 Y-coordinate {m}
17.970000000000, !- Vertex 2 Z-coordinate {m}
13.049407559949, !- Vertex 3 X-coordinate {m}
47.905614064108, !- Vertex 3 Y-coordinate {m}
17.970000000000, !- Vertex 3 Z-coordinate {m}
13.049407559949, !- Vertex 4 X-coordinate {m}
47.905614064108, !- Vertex 4 Y-coordinate {m}
20.970000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
147C92, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
A867DC, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
15.859308706134, !- Vertex 1 X-coordinate {m}
15.788296997630, !- Vertex 1 Y-coordinate {m}
16.380000000000, !- Vertex 1 Z-coordinate {m}
15.859308706134, !- Vertex 2 X-coordinate {m}
15.788296997630, !- Vertex 2 Y-coordinate {m}
13.380000000000, !- Vertex 2 Z-coordinate {m}
13.049407559949, !- Vertex 3 X-coordinate {m}
47.905614064108, !- Vertex 3 Y-coordinate {m}
13.380000000000, !- Vertex 3 Z-coordinate {m}
13.049407559949, !- Vertex 4 X-coordinate {m}
47.905614064108, !- Vertex 4 Y-coordinate {m}
16.380000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
45869F, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
4977E0, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
15.859308706134, !- Vertex 1 X-coordinate {m}
15.788296997630, !- Vertex 1 Y-coordinate {m}
11.790000000000, !- Vertex 1 Z-coordinate {m}
15.859308706134, !- Vertex 2 X-coordinate {m}
15.788296997630, !- Vertex 2 Y-coordinate {m}
8.790000000000, !- Vertex 2 Z-coordinate {m}
15.155743972804, !- Vertex 3 X-coordinate {m}
23.830078697975, !- Vertex 3 Y-coordinate {m}
8.790000000000, !- Vertex 3 Z-coordinate {m}
15.155743972804, !- Vertex 4 X-coordinate {m}
23.830078697975, !- Vertex 4 Y-coordinate {m}
11.790000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
EE2824, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
E0BB02, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
15.155743972804, !- Vertex 1 X-coordinate {m}
23.830078697975, !- Vertex 1 Y-coordinate {m}
11.790000000000, !- Vertex 1 Z-coordinate {m}
15.155743972804, !- Vertex 2 X-coordinate {m}
23.830078697975, !- Vertex 2 Y-coordinate {m}
8.790000000000, !- Vertex 2 Z-coordinate {m}
13.049407559949, !- Vertex 3 X-coordinate {m}
47.905614064108, !- Vertex 3 Y-coordinate {m}
8.790000000000, !- Vertex 3 Z-coordinate {m}
13.049407559949, !- Vertex 4 X-coordinate {m}
47.905614064108, !- Vertex 4 Y-coordinate {m}
11.790000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
6DE9B8, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
7E2443, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
15.834469319450, !- Vertex 1 X-coordinate {m}
16.072212486586, !- Vertex 1 Y-coordinate {m}
7.010000000000, !- Vertex 1 Z-coordinate {m}
15.834469319450, !- Vertex 2 X-coordinate {m}
16.072212486586, !- Vertex 2 Y-coordinate {m}
4.710000000000, !- Vertex 2 Z-coordinate {m}
13.074246946633, !- Vertex 3 X-coordinate {m}
47.621698575151, !- Vertex 3 Y-coordinate {m}
4.710000000000, !- Vertex 3 Z-coordinate {m}
13.074246946633, !- Vertex 4 X-coordinate {m}
47.621698575151, !- Vertex 4 Y-coordinate {m}
7.010000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
570A67, !- Name
Door, !- Surface Type
, !- Construction Name
14EE47, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
14.737614296971, !- Vertex 1 X-coordinate {m}
28.609322762070, !- Vertex 1 Y-coordinate {m}
3.300000000000, !- Vertex 1 Z-coordinate {m}
14.737614296971, !- Vertex 2 X-coordinate {m}
28.609322762070, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
14.171101969112, !- Vertex 3 X-coordinate {m}
35.084588299667, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
14.171101969112, !- Vertex 4 X-coordinate {m}
35.084588299667, !- Vertex 4 Y-coordinate {m}
3.300000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
885B80, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
14EE47, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
15.878047190824, !- Vertex 1 X-coordinate {m}
15.574115137540, !- Vertex 1 Y-coordinate {m}
3.100000000000, !- Vertex 1 Z-coordinate {m}
15.878047190824, !- Vertex 2 X-coordinate {m}
15.574115137540, !- Vertex 2 Y-coordinate {m}
0.800000000000, !- Vertex 2 Z-coordinate {m}
14.781192168345, !- Vertex 3 X-coordinate {m}
28.111225413025, !- Vertex 3 Y-coordinate {m}
0.800000000000, !- Vertex 3 Z-coordinate {m}
14.781192168345, !- Vertex 4 X-coordinate {m}
28.111225413025, !- Vertex 4 Y-coordinate {m}
3.100000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
4AC286, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
14EE47, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
14.127524097738, !- Vertex 1 X-coordinate {m}
35.582685648713, !- Vertex 1 Y-coordinate {m}
3.100000000000, !- Vertex 1 Z-coordinate {m}
14.127524097738, !- Vertex 2 X-coordinate {m}
35.582685648713, !- Vertex 2 Y-coordinate {m}
0.800000000000, !- Vertex 2 Z-coordinate {m}
13.030669075259, !- Vertex 3 X-coordinate {m}
48.119795924197, !- Vertex 3 Y-coordinate {m}
0.800000000000, !- Vertex 3 Z-coordinate {m}
13.030669075259, !- Vertex 4 X-coordinate {m}
48.119795924197, !- Vertex 4 Y-coordinate {m}
3.100000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
8BC98E, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
52F178, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
13.351855913087, !- Vertex 1 X-coordinate {m}
9.040317238483, !- Vertex 1 Y-coordinate {m}
29.350000000000, !- Vertex 1 Z-coordinate {m}
13.351855913087, !- Vertex 2 X-coordinate {m}
9.040317238483, !- Vertex 2 Y-coordinate {m}
23.350000000000, !- Vertex 2 Z-coordinate {m}
13.855761299480, !- Vertex 3 X-coordinate {m}
11.489006553517, !- Vertex 3 Y-coordinate {m}
23.350000000000, !- Vertex 3 Z-coordinate {m}
13.855761299480, !- Vertex 4 X-coordinate {m}
11.489006553517, !- Vertex 4 Y-coordinate {m}
29.350000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
FAEC78, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
BDBCDF, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
13.351855913087, !- Vertex 1 X-coordinate {m}
9.040317238483, !- Vertex 1 Y-coordinate {m}
20.170000000000, !- Vertex 1 Z-coordinate {m}
13.351855913087, !- Vertex 2 X-coordinate {m}
9.040317238483, !- Vertex 2 Y-coordinate {m}
14.170000000000, !- Vertex 2 Z-coordinate {m}
13.855761299480, !- Vertex 3 X-coordinate {m}
11.489006553517, !- Vertex 3 Y-coordinate {m}
14.170000000000, !- Vertex 3 Z-coordinate {m}
13.855761299480, !- Vertex 4 X-coordinate {m}
11.489006553517, !- Vertex 4 Y-coordinate {m}
20.170000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
6A057F, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
1C1421, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
13.351855913087, !- Vertex 1 X-coordinate {m}
9.040317238483, !- Vertex 1 Y-coordinate {m}
10.612400000000, !- Vertex 1 Z-coordinate {m}
13.351855913087, !- Vertex 2 X-coordinate {m}
9.040317238483, !- Vertex 2 Y-coordinate {m}
5.367600000000, !- Vertex 2 Z-coordinate {m}
13.855761299480, !- Vertex 3 X-coordinate {m}
11.489006553517, !- Vertex 3 Y-coordinate {m}
5.367600000000, !- Vertex 3 Z-coordinate {m}
13.855761299480, !- Vertex 4 X-coordinate {m}
11.489006553517, !- Vertex 4 Y-coordinate {m}
10.612400000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
C6B866, !- Name
Door, !- Surface Type
, !- Construction Name
376070, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
13.418371424091, !- Vertex 1 X-coordinate {m}
9.363544228068, !- Vertex 1 Y-coordinate {m}
3.300000000000, !- Vertex 1 Z-coordinate {m}
13.418371424091, !- Vertex 2 X-coordinate {m}
9.363544228068, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
13.789245788476, !- Vertex 3 X-coordinate {m}
11.165779563932, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
13.789245788476, !- Vertex 4 X-coordinate {m}
11.165779563932, !- Vertex 4 Y-coordinate {m}
3.300000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
8D700D, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
F1D81E, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
59.830727809203, !- Vertex 1 X-coordinate {m}
50.681283246644, !- Vertex 1 Y-coordinate {m}
25.460000000000, !- Vertex 1 Z-coordinate {m}
59.830727809203, !- Vertex 2 X-coordinate {m}
50.681283246644, !- Vertex 2 Y-coordinate {m}
22.560000000000, !- Vertex 2 Z-coordinate {m}
43.742276939946, !- Vertex 3 X-coordinate {m}
17.896040398260, !- Vertex 3 Y-coordinate {m}
22.560000000000, !- Vertex 3 Z-coordinate {m}
43.742276939946, !- Vertex 4 X-coordinate {m}
17.896040398261, !- Vertex 4 Y-coordinate {m}
25.460000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
A9A38B, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
EB5B01, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
59.830727533012, !- Vertex 1 X-coordinate {m}
50.681283382177, !- Vertex 1 Y-coordinate {m}
20.870000000000, !- Vertex 1 Z-coordinate {m}
59.830727533012, !- Vertex 2 X-coordinate {m}
50.681283382177, !- Vertex 2 Y-coordinate {m}
17.970000000000, !- Vertex 2 Z-coordinate {m}
46.571016269985, !- Vertex 3 X-coordinate {m}
23.660480281161, !- Vertex 3 Y-coordinate {m}
17.970000000000, !- Vertex 3 Z-coordinate {m}
46.571016269985, !- Vertex 4 X-coordinate {m}
23.660480281161, !- Vertex 4 Y-coordinate {m}
20.870000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
7FDC2A, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
F73EBB, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
46.571016269985, !- Vertex 1 X-coordinate {m}
23.660480281161, !- Vertex 1 Y-coordinate {m}
20.870000000000, !- Vertex 1 Z-coordinate {m}
46.571016269985, !- Vertex 2 X-coordinate {m}
23.660480281161, !- Vertex 2 Y-coordinate {m}
17.970000000000, !- Vertex 2 Z-coordinate {m}
43.742276917607, !- Vertex 3 X-coordinate {m}
17.896040409224, !- Vertex 3 Y-coordinate {m}
17.970000000000, !- Vertex 3 Z-coordinate {m}
43.742276917607, !- Vertex 4 X-coordinate {m}
17.896040409224, !- Vertex 4 Y-coordinate {m}
20.870000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
15A0BC, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
C33312, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
59.830727801689, !- Vertex 1 X-coordinate {m}
50.681283250331, !- Vertex 1 Y-coordinate {m}
16.280000000000, !- Vertex 1 Z-coordinate {m}
59.830727801689, !- Vertex 2 X-coordinate {m}
50.681283250331, !- Vertex 2 Y-coordinate {m}
13.380000000000, !- Vertex 2 Z-coordinate {m}
44.808863920672, !- Vertex 3 X-coordinate {m}
20.069544587079, !- Vertex 3 Y-coordinate {m}
13.380000000000, !- Vertex 3 Z-coordinate {m}
44.808863920672, !- Vertex 4 X-coordinate {m}
20.069544587079, !- Vertex 4 Y-coordinate {m}
16.280000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
98F3B3, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
FD319A, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
44.808864203461, !- Vertex 1 X-coordinate {m}
20.069544448307, !- Vertex 1 Y-coordinate {m}
16.280000000000, !- Vertex 1 Z-coordinate {m}
44.808864203461, !- Vertex 2 X-coordinate {m}
20.069544448307, !- Vertex 2 Y-coordinate {m}
13.380000000000, !- Vertex 2 Z-coordinate {m}
43.742277099886, !- Vertex 3 X-coordinate {m}
17.896040319774, !- Vertex 3 Y-coordinate {m}
13.380000000000, !- Vertex 3 Z-coordinate {m}
43.742277099886, !- Vertex 4 X-coordinate {m}
17.896040319774, !- Vertex 4 Y-coordinate {m}
16.280000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
E9DCE7, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
C08D7D, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
59.830727527992, !- Vertex 1 X-coordinate {m}
50.681283384641, !- Vertex 1 Y-coordinate {m}
11.690000000000, !- Vertex 1 Z-coordinate {m}
59.830727527992, !- Vertex 2 X-coordinate {m}
50.681283384641, !- Vertex 2 Y-coordinate {m}
8.790000000000, !- Vertex 2 Z-coordinate {m}
43.742276902680, !- Vertex 3 X-coordinate {m}
17.896040416548, !- Vertex 3 Y-coordinate {m}
8.790000000000, !- Vertex 3 Z-coordinate {m}
43.742276902680, !- Vertex 4 X-coordinate {m}
17.896040416548, !- Vertex 4 Y-coordinate {m}
11.690000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
71BB7D, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
12F867, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
45.634532548241, !- Vertex 1 X-coordinate {m}
21.752102292381, !- Vertex 1 Y-coordinate {m}
3.300000000000, !- Vertex 1 Z-coordinate {m}
45.634532548241, !- Vertex 2 X-coordinate {m}
21.752102292381, !- Vertex 2 Y-coordinate {m}
1.500000000000, !- Vertex 2 Z-coordinate {m}
41.339626522549, !- Vertex 3 X-coordinate {m}
12.999889860195, !- Vertex 3 Y-coordinate {m}
1.500000000000, !- Vertex 3 Z-coordinate {m}
41.339626522549, !- Vertex 4 X-coordinate {m}
12.999889860195, !- Vertex 4 Y-coordinate {m}
3.300000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
8739EB, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
EBDC5E, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
45.634532548241, !- Vertex 1 X-coordinate {m}
21.752102292381, !- Vertex 1 Y-coordinate {m}
7.210000000000, !- Vertex 1 Z-coordinate {m}
45.634532548241, !- Vertex 2 X-coordinate {m}
21.752102292381, !- Vertex 2 Y-coordinate {m}
4.960000000000, !- Vertex 2 Z-coordinate {m}
41.339626522549, !- Vertex 3 X-coordinate {m}
12.999889860195, !- Vertex 3 Y-coordinate {m}
4.960000000000, !- Vertex 3 Z-coordinate {m}
41.339626522549, !- Vertex 4 X-coordinate {m}
12.999889860195, !- Vertex 4 Y-coordinate {m}
7.210000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
1B8B9B, !- Name
Door, !- Surface Type
, !- Construction Name
199120, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
54.191840123720, !- Vertex 1 X-coordinate {m}
39.190289135145, !- Vertex 1 Y-coordinate {m}
3.300000000000, !- Vertex 1 Z-coordinate {m}
54.191840123720, !- Vertex 2 X-coordinate {m}
39.190289135145, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
51.328342613738, !- Vertex 3 X-coordinate {m}
33.355018617823, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
51.328342613738, !- Vertex 4 X-coordinate {m}
33.355018617823, !- Vertex 4 Y-coordinate {m}
3.300000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
F39C0E, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
199120, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
58.487086388693, !- Vertex 1 X-coordinate {m}
47.943194911129, !- Vertex 1 Y-coordinate {m}
7.210000000000, !- Vertex 1 Z-coordinate {m}
58.487086388693, !- Vertex 2 X-coordinate {m}
47.943194911129, !- Vertex 2 Y-coordinate {m}
3.410000000000, !- Vertex 2 Z-coordinate {m}
47.033096348766, !- Vertex 3 X-coordinate {m}
24.602112841840, !- Vertex 3 Y-coordinate {m}
3.410000000000, !- Vertex 3 Z-coordinate {m}
47.033096348766, !- Vertex 4 X-coordinate {m}
24.602112841840, !- Vertex 4 Y-coordinate {m}
7.210000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
53E402, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
6EE34E, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-3.759984846011, !- Vertex 1 X-coordinate {m}
42.976823447490, !- Vertex 1 Y-coordinate {m}
3.120000000000, !- Vertex 1 Z-coordinate {m}
-3.759984846011, !- Vertex 2 X-coordinate {m}
42.976823447490, !- Vertex 2 Y-coordinate {m}
0.800000000000, !- Vertex 2 Z-coordinate {m}
-1.550586767358, !- Vertex 3 X-coordinate {m}
17.723287850865, !- Vertex 3 Y-coordinate {m}
0.800000000000, !- Vertex 3 Z-coordinate {m}
-1.550586767358, !- Vertex 4 X-coordinate {m}
17.723287850865, !- Vertex 4 Y-coordinate {m}
3.120000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
100B7C, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
840AA7, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
-0.867939412286, !- Vertex 1 X-coordinate {m}
9.920592878061, !- Vertex 1 Y-coordinate {m}
3.120000000000, !- Vertex 1 Z-coordinate {m}
-0.867939412286, !- Vertex 2 X-coordinate {m}
9.920592878061, !- Vertex 2 Y-coordinate {m}
0.800000000000, !- Vertex 2 Z-coordinate {m}
-0.619545545455, !- Vertex 3 X-coordinate {m}
7.081437988500, !- Vertex 3 Y-coordinate {m}
0.800000000000, !- Vertex 3 Z-coordinate {m}
-0.619545545455, !- Vertex 4 X-coordinate {m}
7.081437988500, !- Vertex 4 Y-coordinate {m}
3.120000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
552ECF, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
55D449, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
12.582233491957, !- Vertex 1 X-coordinate {m}
64.259629125941, !- Vertex 1 Y-coordinate {m}
30.250000000000, !- Vertex 1 Z-coordinate {m}
12.582233491957, !- Vertex 2 X-coordinate {m}
64.259629125941, !- Vertex 2 Y-coordinate {m}
27.150000000000, !- Vertex 2 Z-coordinate {m}
5.315042979112, !- Vertex 3 X-coordinate {m}
63.623832340385, !- Vertex 3 Y-coordinate {m}
27.150000000000, !- Vertex 3 Z-coordinate {m}
5.315042979112, !- Vertex 4 X-coordinate {m}
63.623832340385, !- Vertex 4 Y-coordinate {m}
30.250000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
45D0FF, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
EDC019, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
12.582233491957, !- Vertex 1 X-coordinate {m}
64.259629125941, !- Vertex 1 Y-coordinate {m}
25.660000000000, !- Vertex 1 Z-coordinate {m}
12.582233491957, !- Vertex 2 X-coordinate {m}
64.259629125941, !- Vertex 2 Y-coordinate {m}
22.560000000000, !- Vertex 2 Z-coordinate {m}
5.315042979112, !- Vertex 3 X-coordinate {m}
63.623832340385, !- Vertex 3 Y-coordinate {m}
22.560000000000, !- Vertex 3 Z-coordinate {m}
5.315042979112, !- Vertex 4 X-coordinate {m}
63.623832340385, !- Vertex 4 Y-coordinate {m}
25.660000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
A47E39, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
E2F99C, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
12.582233491957, !- Vertex 1 X-coordinate {m}
64.259629125942, !- Vertex 1 Y-coordinate {m}
21.070000000000, !- Vertex 1 Z-coordinate {m}
12.582233491957, !- Vertex 2 X-coordinate {m}
64.259629125942, !- Vertex 2 Y-coordinate {m}
17.970000000000, !- Vertex 2 Z-coordinate {m}
5.315042979112, !- Vertex 3 X-coordinate {m}
63.623832340385, !- Vertex 3 Y-coordinate {m}
17.970000000000, !- Vertex 3 Z-coordinate {m}
5.315042979112, !- Vertex 4 X-coordinate {m}
63.623832340385, !- Vertex 4 Y-coordinate {m}
21.070000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
CD6CA2, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
611B27, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
12.582233580160, !- Vertex 1 X-coordinate {m}
64.259629133658, !- Vertex 1 Y-coordinate {m}
16.480000000000, !- Vertex 1 Z-coordinate {m}
12.582233580160, !- Vertex 2 X-coordinate {m}
64.259629133658, !- Vertex 2 Y-coordinate {m}
13.380000000000, !- Vertex 2 Z-coordinate {m}
5.315042979112, !- Vertex 3 X-coordinate {m}
63.623832340385, !- Vertex 3 Y-coordinate {m}
13.380000000000, !- Vertex 3 Z-coordinate {m}
5.315042979112, !- Vertex 4 X-coordinate {m}
63.623832340385, !- Vertex 4 Y-coordinate {m}
16.480000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
24682D, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
CF716B, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
12.582233580160, !- Vertex 1 X-coordinate {m}
64.259629133658, !- Vertex 1 Y-coordinate {m}
11.890000000000, !- Vertex 1 Z-coordinate {m}
12.582233580160, !- Vertex 2 X-coordinate {m}
64.259629133658, !- Vertex 2 Y-coordinate {m}
8.790000000000, !- Vertex 2 Z-coordinate {m}
5.315042979112, !- Vertex 3 X-coordinate {m}
63.623832340385, !- Vertex 3 Y-coordinate {m}
8.790000000000, !- Vertex 3 Z-coordinate {m}
5.315042979112, !- Vertex 4 X-coordinate {m}
63.623832340385, !- Vertex 4 Y-coordinate {m}
11.890000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
81A1E9, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
63C225, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
12.187071708591, !- Vertex 1 X-coordinate {m}
68.776349993744, !- Vertex 1 Y-coordinate {m}
7.300000000000, !- Vertex 1 Z-coordinate {m}
12.187071708591, !- Vertex 2 X-coordinate {m}
68.776349993744, !- Vertex 2 Y-coordinate {m}
6.600000000000, !- Vertex 2 Z-coordinate {m}
7.390443958811, !- Vertex 3 X-coordinate {m}
68.356699442485, !- Vertex 3 Y-coordinate {m}
6.600000000000, !- Vertex 3 Z-coordinate {m}
7.390443958811, !- Vertex 4 X-coordinate {m}
68.356699442485, !- Vertex 4 Y-coordinate {m}
7.300000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
2C2DA6, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
63C225, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
6.394249260719, !- Vertex 1 X-coordinate {m}
68.269543699737, !- Vertex 1 Y-coordinate {m}
7.300000000000, !- Vertex 1 Z-coordinate {m}
6.394249260719, !- Vertex 2 X-coordinate {m}
68.269543699737, !- Vertex 2 Y-coordinate {m}
5.600000000000, !- Vertex 2 Z-coordinate {m}
3.923686409452, !- Vertex 3 X-coordinate {m}
68.053397457723, !- Vertex 3 Y-coordinate {m}
5.600000000000, !- Vertex 3 Z-coordinate {m}
3.923686409452, !- Vertex 4 X-coordinate {m}
68.053397457723, !- Vertex 4 Y-coordinate {m}
7.300000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
480EBF, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
D5CE6D, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
2.889398766899, !- Vertex 1 X-coordinate {m}
64.557952125227, !- Vertex 1 Y-coordinate {m}
30.250000000000, !- Vertex 1 Z-coordinate {m}
2.889398766899, !- Vertex 2 X-coordinate {m}
64.557952125227, !- Vertex 2 Y-coordinate {m}
27.150000000000, !- Vertex 2 Z-coordinate {m}
2.693298345717, !- Vertex 3 X-coordinate {m}
66.799390195934, !- Vertex 3 Y-coordinate {m}
27.150000000000, !- Vertex 3 Z-coordinate {m}
2.693298345717, !- Vertex 4 X-coordinate {m}
66.799390195934, !- Vertex 4 Y-coordinate {m}
30.250000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
1F886B, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
E803E3, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
2.889398766899, !- Vertex 1 X-coordinate {m}
64.557952125227, !- Vertex 1 Y-coordinate {m}
25.660000000000, !- Vertex 1 Z-coordinate {m}
2.889398766899, !- Vertex 2 X-coordinate {m}
64.557952125227, !- Vertex 2 Y-coordinate {m}
22.560000000000, !- Vertex 2 Z-coordinate {m}
2.693298345717, !- Vertex 3 X-coordinate {m}
66.799390195934, !- Vertex 3 Y-coordinate {m}
22.560000000000, !- Vertex 3 Z-coordinate {m}
2.693298345717, !- Vertex 4 X-coordinate {m}
66.799390195934, !- Vertex 4 Y-coordinate {m}
25.660000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
5635B6, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
C32016, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
2.889398766899, !- Vertex 1 X-coordinate {m}
64.557952125227, !- Vertex 1 Y-coordinate {m}
20.970000000000, !- Vertex 1 Z-coordinate {m}
2.889398766899, !- Vertex 2 X-coordinate {m}
64.557952125227, !- Vertex 2 Y-coordinate {m}
17.970000000000, !- Vertex 2 Z-coordinate {m}
2.693298345717, !- Vertex 3 X-coordinate {m}
66.799390195934, !- Vertex 3 Y-coordinate {m}
17.970000000000, !- Vertex 3 Z-coordinate {m}
2.693298345717, !- Vertex 4 X-coordinate {m}
66.799390195934, !- Vertex 4 Y-coordinate {m}
20.970000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
B47504, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
BDE2EC, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
2.889398766899, !- Vertex 1 X-coordinate {m}
64.557952125227, !- Vertex 1 Y-coordinate {m}
16.480000000000, !- Vertex 1 Z-coordinate {m}
2.889398766899, !- Vertex 2 X-coordinate {m}
64.557952125227, !- Vertex 2 Y-coordinate {m}
13.380000000000, !- Vertex 2 Z-coordinate {m}
2.693298345717, !- Vertex 3 X-coordinate {m}
66.799390195934, !- Vertex 3 Y-coordinate {m}
13.380000000000, !- Vertex 3 Z-coordinate {m}
2.693298345717, !- Vertex 4 X-coordinate {m}
66.799390195934, !- Vertex 4 Y-coordinate {m}
16.480000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
3C3F43, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
1FC3FA, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
2.889398766899, !- Vertex 1 X-coordinate {m}
64.557952125227, !- Vertex 1 Y-coordinate {m}
11.890000000000, !- Vertex 1 Z-coordinate {m}
2.889398766899, !- Vertex 2 X-coordinate {m}
64.557952125227, !- Vertex 2 Y-coordinate {m}
8.790000000000, !- Vertex 2 Z-coordinate {m}
2.693298345717, !- Vertex 3 X-coordinate {m}
66.799390195934, !- Vertex 3 Y-coordinate {m}
8.790000000000, !- Vertex 3 Z-coordinate {m}
2.693298345717, !- Vertex 4 X-coordinate {m}
66.799390195934, !- Vertex 4 Y-coordinate {m}
11.890000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
FC0007, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
82AE15, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
53.607376941602, !- Vertex 1 X-coordinate {m}
9.624520586489, !- Vertex 1 Y-coordinate {m}
25.650000000000, !- Vertex 1 Z-coordinate {m}
53.607376941602, !- Vertex 2 X-coordinate {m}
9.624520586489, !- Vertex 2 Y-coordinate {m}
22.560000000000, !- Vertex 2 Z-coordinate {m}
69.164734971444, !- Vertex 3 X-coordinate {m}
41.322544359767, !- Vertex 3 Y-coordinate {m}
22.560000000000, !- Vertex 3 Z-coordinate {m}
69.164734971444, !- Vertex 4 X-coordinate {m}
41.322544359767, !- Vertex 4 Y-coordinate {m}
25.650000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
C5F9C6, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
82AE15, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
70.300924683753, !- Vertex 1 X-coordinate {m}
43.637524091072, !- Vertex 1 Y-coordinate {m}
25.650000000000, !- Vertex 1 Z-coordinate {m}
70.300924683753, !- Vertex 2 X-coordinate {m}
43.637524091072, !- Vertex 2 Y-coordinate {m}
24.150000000000, !- Vertex 2 Z-coordinate {m}
72.415773693757, !- Vertex 3 X-coordinate {m}
47.946516277754, !- Vertex 3 Y-coordinate {m}
24.150000000000, !- Vertex 3 Z-coordinate {m}
72.415773693757, !- Vertex 4 X-coordinate {m}
47.946516277754, !- Vertex 4 Y-coordinate {m}
25.650000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
2EDE85, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
8E85EC, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
53.607376941602, !- Vertex 1 X-coordinate {m}
9.624520586489, !- Vertex 1 Y-coordinate {m}
21.060000000000, !- Vertex 1 Z-coordinate {m}
53.607376941602, !- Vertex 2 X-coordinate {m}
9.624520586489, !- Vertex 2 Y-coordinate {m}
17.970000000000, !- Vertex 2 Z-coordinate {m}
57.793015607234, !- Vertex 3 X-coordinate {m}
18.152734289297, !- Vertex 3 Y-coordinate {m}
17.970000000000, !- Vertex 3 Z-coordinate {m}
57.793015607234, !- Vertex 4 X-coordinate {m}
18.152734289297, !- Vertex 4 Y-coordinate {m}
21.060000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
E8081B, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
545B0F, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
57.793015607234, !- Vertex 1 X-coordinate {m}
18.152734289297, !- Vertex 1 Y-coordinate {m}
21.060000000000, !- Vertex 1 Z-coordinate {m}
57.793015607234, !- Vertex 2 X-coordinate {m}
18.152734289297, !- Vertex 2 Y-coordinate {m}
17.970000000000, !- Vertex 2 Z-coordinate {m}
69.164734971444, !- Vertex 3 X-coordinate {m}
41.322544359767, !- Vertex 3 Y-coordinate {m}
17.970000000000, !- Vertex 3 Z-coordinate {m}
69.164734971444, !- Vertex 4 X-coordinate {m}
41.322544359767, !- Vertex 4 Y-coordinate {m}
21.060000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
2A95FD, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
545B0F, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
70.300924683753, !- Vertex 1 X-coordinate {m}
43.637524091072, !- Vertex 1 Y-coordinate {m}
21.060000000000, !- Vertex 1 Z-coordinate {m}
70.300924683753, !- Vertex 2 X-coordinate {m}
43.637524091072, !- Vertex 2 Y-coordinate {m}
19.560000000000, !- Vertex 2 Z-coordinate {m}
72.415773693757, !- Vertex 3 X-coordinate {m}
47.946516277754, !- Vertex 3 Y-coordinate {m}
19.560000000000, !- Vertex 3 Z-coordinate {m}
72.415773693757, !- Vertex 4 X-coordinate {m}
47.946516277754, !- Vertex 4 Y-coordinate {m}
21.060000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
355CE5, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
DB206A, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
53.607376941602, !- Vertex 1 X-coordinate {m}
9.624520586489, !- Vertex 1 Y-coordinate {m}
16.470000000000, !- Vertex 1 Z-coordinate {m}
53.607376941602, !- Vertex 2 X-coordinate {m}
9.624520586489, !- Vertex 2 Y-coordinate {m}
13.380000000000, !- Vertex 2 Z-coordinate {m}
56.030641432231, !- Vertex 3 X-coordinate {m}
14.561907467061, !- Vertex 3 Y-coordinate {m}
13.380000000000, !- Vertex 3 Z-coordinate {m}
56.030641432231, !- Vertex 4 X-coordinate {m}
14.561907467061, !- Vertex 4 Y-coordinate {m}
16.470000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
1AE7C4, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
E6F13C, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
56.030641432231, !- Vertex 1 X-coordinate {m}
14.561907467061, !- Vertex 1 Y-coordinate {m}
16.470000000000, !- Vertex 1 Z-coordinate {m}
56.030641432231, !- Vertex 2 X-coordinate {m}
14.561907467061, !- Vertex 2 Y-coordinate {m}
13.380000000000, !- Vertex 2 Z-coordinate {m}
69.164734971444, !- Vertex 3 X-coordinate {m}
41.322544359767, !- Vertex 3 Y-coordinate {m}
13.380000000000, !- Vertex 3 Z-coordinate {m}
69.164734971444, !- Vertex 4 X-coordinate {m}
41.322544359767, !- Vertex 4 Y-coordinate {m}
16.470000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
78D8E1, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
E6F13C, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
70.300924683753, !- Vertex 1 X-coordinate {m}
43.637524091072, !- Vertex 1 Y-coordinate {m}
16.470000000000, !- Vertex 1 Z-coordinate {m}
70.300924683753, !- Vertex 2 X-coordinate {m}
43.637524091072, !- Vertex 2 Y-coordinate {m}
14.970000000000, !- Vertex 2 Z-coordinate {m}
72.415773693757, !- Vertex 3 X-coordinate {m}
47.946516277754, !- Vertex 3 Y-coordinate {m}
14.970000000000, !- Vertex 3 Z-coordinate {m}
72.415773693757, !- Vertex 4 X-coordinate {m}
47.946516277754, !- Vertex 4 Y-coordinate {m}
16.470000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
C401D2, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
9456BF, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
53.607376941602, !- Vertex 1 X-coordinate {m}
9.624520586489, !- Vertex 1 Y-coordinate {m}
11.880000000000, !- Vertex 1 Z-coordinate {m}
53.607376941602, !- Vertex 2 X-coordinate {m}
9.624520586489, !- Vertex 2 Y-coordinate {m}
10.380000000000, !- Vertex 2 Z-coordinate {m}
69.164734971444, !- Vertex 3 X-coordinate {m}
41.322544359767, !- Vertex 3 Y-coordinate {m}
10.380000000000, !- Vertex 3 Z-coordinate {m}
69.164734971444, !- Vertex 4 X-coordinate {m}
41.322544359767, !- Vertex 4 Y-coordinate {m}
11.880000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
A115DC, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
9456BF, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
70.300924683753, !- Vertex 1 X-coordinate {m}
43.637524091072, !- Vertex 1 Y-coordinate {m}
11.880000000000, !- Vertex 1 Z-coordinate {m}
70.300924683753, !- Vertex 2 X-coordinate {m}
43.637524091072, !- Vertex 2 Y-coordinate {m}
10.380000000000, !- Vertex 2 Z-coordinate {m}
72.415773693757, !- Vertex 3 X-coordinate {m}
47.946516277754, !- Vertex 3 Y-coordinate {m}
10.380000000000, !- Vertex 3 Z-coordinate {m}
72.415773693757, !- Vertex 4 X-coordinate {m}
47.946516277754, !- Vertex 4 Y-coordinate {m}
11.880000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
B347E1, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
EB9389, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
53.607376941602, !- Vertex 1 X-coordinate {m}
9.624520586489, !- Vertex 1 Y-coordinate {m}
7.830000000000, !- Vertex 1 Z-coordinate {m}
53.607376941602, !- Vertex 2 X-coordinate {m}
9.624520586489, !- Vertex 2 Y-coordinate {m}
4.710000000000, !- Vertex 2 Z-coordinate {m}
56.911828519733, !- Vertex 3 X-coordinate {m}
16.357320878178, !- Vertex 3 Y-coordinate {m}
4.710000000000, !- Vertex 3 Z-coordinate {m}
56.911828519733, !- Vertex 4 X-coordinate {m}
16.357320878178, !- Vertex 4 Y-coordinate {m}
7.830000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
8634CE, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
7C3219, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
56.911828519733, !- Vertex 1 X-coordinate {m}
16.357320878178, !- Vertex 1 Y-coordinate {m}
7.830000000000, !- Vertex 1 Z-coordinate {m}
56.911828519733, !- Vertex 2 X-coordinate {m}
16.357320878178, !- Vertex 2 Y-coordinate {m}
4.710000000000, !- Vertex 2 Z-coordinate {m}
69.164734971444, !- Vertex 3 X-coordinate {m}
41.322544359767, !- Vertex 3 Y-coordinate {m}
4.710000000000, !- Vertex 3 Z-coordinate {m}
69.164734971444, !- Vertex 4 X-coordinate {m}
41.322544359767, !- Vertex 4 Y-coordinate {m}
7.830000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
A90B7C, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
7C3219, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
70.300924683753, !- Vertex 1 X-coordinate {m}
43.637524091072, !- Vertex 1 Y-coordinate {m}
3.890000000000, !- Vertex 1 Z-coordinate {m}
70.300924683753, !- Vertex 2 X-coordinate {m}
43.637524091072, !- Vertex 2 Y-coordinate {m}
2.390000000000, !- Vertex 2 Z-coordinate {m}
72.415773693757, !- Vertex 3 X-coordinate {m}
47.946516277754, !- Vertex 3 Y-coordinate {m}
2.390000000000, !- Vertex 3 Z-coordinate {m}
72.415773693757, !- Vertex 4 X-coordinate {m}
47.946516277754, !- Vertex 4 Y-coordinate {m}
3.890000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
B3489C, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
D7C7B0, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
53.607376941602, !- Vertex 1 X-coordinate {m}
9.624520586489, !- Vertex 1 Y-coordinate {m}
3.110000000000, !- Vertex 1 Z-coordinate {m}
53.607376941602, !- Vertex 2 X-coordinate {m}
9.624520586489, !- Vertex 2 Y-coordinate {m}
1.010000000000, !- Vertex 2 Z-coordinate {m}
55.021682217042, !- Vertex 3 X-coordinate {m}
12.506159111332, !- Vertex 3 Y-coordinate {m}
1.010000000000, !- Vertex 3 Z-coordinate {m}
55.021682217042, !- Vertex 4 X-coordinate {m}
12.506159111332, !- Vertex 4 Y-coordinate {m}
3.110000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
A20189, !- Name
Window, !- Surface Type
EXT_WINDOW_DG, !- Construction Name
197952, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
7.821733791892, !- Vertex 1 X-coordinate {m}
-1.609601328521, !- Vertex 1 Y-coordinate {m}
20.810000000000, !- Vertex 1 Z-coordinate {m}
7.821733791892, !- Vertex 2 X-coordinate {m}
-1.609601328521, !- Vertex 2 Y-coordinate {m}
17.960000000000, !- Vertex 2 Z-coordinate {m}
11.024619423024, !- Vertex 3 X-coordinate {m}
-2.268709539582, !- Vertex 3 Y-coordinate {m}
17.960000000000, !- Vertex 3 Z-coordinate {m}
11.024619423024, !- Vertex 4 X-coordinate {m}
-2.268709539582, !- Vertex 4 Y-coordinate {m}
20.810000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
B51A83, !- Name
Window, !- Surface Type
EXT_WINDOW_DG, !- Construction Name
197952, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
7.821733791892, !- Vertex 1 X-coordinate {m}
-1.609601328521, !- Vertex 1 Y-coordinate {m}
16.230000000000, !- Vertex 1 Z-coordinate {m}
7.821733791892, !- Vertex 2 X-coordinate {m}
-1.609601328521, !- Vertex 2 Y-coordinate {m}
13.380000000000, !- Vertex 2 Z-coordinate {m}
11.024619423024, !- Vertex 3 X-coordinate {m}
-2.268709539582, !- Vertex 3 Y-coordinate {m}
13.380000000000, !- Vertex 3 Z-coordinate {m}
11.024619423024, !- Vertex 4 X-coordinate {m}
-2.268709539582, !- Vertex 4 Y-coordinate {m}
16.230000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
CD0A11, !- Name
Window, !- Surface Type
EXT_WINDOW_DG, !- Construction Name
D3D445, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
7.821733791892, !- Vertex 1 X-coordinate {m}
-1.609601328521, !- Vertex 1 Y-coordinate {m}
11.640000000000, !- Vertex 1 Z-coordinate {m}
7.821733791892, !- Vertex 2 X-coordinate {m}
-1.609601328521, !- Vertex 2 Y-coordinate {m}
8.790000000000, !- Vertex 2 Z-coordinate {m}
11.024619423024, !- Vertex 3 X-coordinate {m}
-2.268709539582, !- Vertex 3 Y-coordinate {m}
8.790000000000, !- Vertex 3 Z-coordinate {m}
11.024619423024, !- Vertex 4 X-coordinate {m}
-2.268709539582, !- Vertex 4 Y-coordinate {m}
11.640000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
35A126, !- Name
Window, !- Surface Type
EXT_WINDOW_DG, !- Construction Name
809397, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
7.821733791892, !- Vertex 1 X-coordinate {m}
-1.609601328521, !- Vertex 1 Y-coordinate {m}
25.410000000000, !- Vertex 1 Z-coordinate {m}
7.821733791892, !- Vertex 2 X-coordinate {m}
-1.609601328521, !- Vertex 2 Y-coordinate {m}
22.560000000000, !- Vertex 2 Z-coordinate {m}
11.024619423024, !- Vertex 3 X-coordinate {m}
-2.268709539582, !- Vertex 3 Y-coordinate {m}
22.560000000000, !- Vertex 3 Z-coordinate {m}
11.024619423024, !- Vertex 4 X-coordinate {m}
-2.268709539582, !- Vertex 4 Y-coordinate {m}
25.410000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
EA07A0, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
3BA882, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
7.821733791892, !- Vertex 1 X-coordinate {m}
-1.609601328521, !- Vertex 1 Y-coordinate {m}
29.240000000000, !- Vertex 1 Z-coordinate {m}
7.821733791892, !- Vertex 2 X-coordinate {m}
-1.609601328521, !- Vertex 2 Y-coordinate {m}
27.150000000000, !- Vertex 2 Z-coordinate {m}
10.613239617191, !- Vertex 3 X-coordinate {m}
-2.184053439079, !- Vertex 3 Y-coordinate {m}
27.150000000000, !- Vertex 3 Z-coordinate {m}
10.613239617191, !- Vertex 4 X-coordinate {m}
-2.184053439079, !- Vertex 4 Y-coordinate {m}
29.240000000000; !- Vertex 4 Z-coordinate {m}
FenestrationSurface:Detailed,
40CDBB, !- Name
Window, !- Surface Type
EXT_WINDOW_SG, !- Construction Name
CE3450, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- TRNSYS 17 - additional surface data
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
7.694401947230, !- Vertex 1 X-coordinate {m}
-1.583398249794, !- Vertex 1 Y-coordinate {m}
3.000000000000, !- Vertex 1 Z-coordinate {m}
7.694401947230, !- Vertex 2 X-coordinate {m}
-1.583398249794, !- Vertex 2 Y-coordinate {m}
2.000000000000, !- Vertex 2 Z-coordinate {m}
10.485907772528, !- Vertex 3 X-coordinate {m}
-2.157850360352, !- Vertex 3 Y-coordinate {m}
2.000000000000, !- Vertex 3 Z-coordinate {m}
10.485907772528, !- Vertex 4 X-coordinate {m}
-2.157850360352, !- Vertex 4 Y-coordinate {m}
3.000000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
E12B4A, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B2_F5_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-6.830235356449, !- Vertex 1 X-coordinate {m}
67.112551214762, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
-6.830235356449, !- Vertex 2 X-coordinate {m}
67.112551214762, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
-6.660281627363, !- Vertex 3 X-coordinate {m}
65.169971202261, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
-6.660281627363, !- Vertex 4 X-coordinate {m}
65.169971202261, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
ED4000, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_GL, !- Construction Name
B2_F5_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-6.660281627363, !- Vertex 1 X-coordinate {m}
65.169971202261, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
-6.660281627363, !- Vertex 2 X-coordinate {m}
65.169971202261, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
-5.523860194453, !- Vertex 3 X-coordinate {m}
52.180614786127, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
-5.523860194453, !- Vertex 4 X-coordinate {m}
52.180614786127, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
FC7733, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_GL, !- Construction Name
B2_F4_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-6.660281627363, !- Vertex 1 X-coordinate {m}
65.169971202261, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
-6.660281627363, !- Vertex 2 X-coordinate {m}
65.169971202261, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
-5.523860194453, !- Vertex 3 X-coordinate {m}
52.180614786127, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
-5.523860194453, !- Vertex 4 X-coordinate {m}
52.180614786127, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
46B811, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B2_F4_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-5.523860194453, !- Vertex 1 X-coordinate {m}
52.180614786127, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
-5.523860194453, !- Vertex 2 X-coordinate {m}
52.180614786127, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
-5.353906496095, !- Vertex 3 X-coordinate {m}
50.238035124848, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
-5.353906496095, !- Vertex 4 X-coordinate {m}
50.238035124848, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
ADCA2B, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_GL, !- Construction Name
B2_F3_LB, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-6.660281627363, !- Vertex 1 X-coordinate {m}
65.169971202261, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
-6.660281627363, !- Vertex 2 X-coordinate {m}
65.169971202261, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
-5.523860194453, !- Vertex 3 X-coordinate {m}
52.180614786127, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
-5.523860194453, !- Vertex 4 X-coordinate {m}
52.180614786127, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
E3B25B, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B2_F3_LB, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-5.523860194453, !- Vertex 1 X-coordinate {m}
52.180614786127, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
-5.523860194453, !- Vertex 2 X-coordinate {m}
52.180614786127, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
-5.353906496095, !- Vertex 3 X-coordinate {m}
50.238035124848, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
-5.353906496095, !- Vertex 4 X-coordinate {m}
50.238035124848, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
26574F, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_GL, !- Construction Name
B2_F2_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-6.660281627363, !- Vertex 1 X-coordinate {m}
65.169971202261, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
-6.660281627363, !- Vertex 2 X-coordinate {m}
65.169971202261, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
-5.523860194453, !- Vertex 3 X-coordinate {m}
52.180614786127, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
-5.523860194453, !- Vertex 4 X-coordinate {m}
52.180614786127, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
E2ED6F, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B2_F2_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-5.523860194453, !- Vertex 1 X-coordinate {m}
52.180614786127, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
-5.523860194453, !- Vertex 2 X-coordinate {m}
52.180614786127, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
-5.353906496095, !- Vertex 3 X-coordinate {m}
50.238035124848, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
-5.353906496095, !- Vertex 4 X-coordinate {m}
50.238035124848, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
EBA029, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_GL, !- Construction Name
B2_F1_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-6.660281627363, !- Vertex 1 X-coordinate {m}
65.169971202261, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
-6.660281627363, !- Vertex 2 X-coordinate {m}
65.169971202261, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
-5.523860194453, !- Vertex 3 X-coordinate {m}
52.180614786127, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
-5.523860194453, !- Vertex 4 X-coordinate {m}
52.180614786127, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
752725, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B2_F1_OF, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-5.523860194453, !- Vertex 1 X-coordinate {m}
52.180614786127, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
-5.523860194453, !- Vertex 2 X-coordinate {m}
52.180614786127, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
-5.353906496095, !- Vertex 3 X-coordinate {m}
50.238035124848, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
-5.353906496095, !- Vertex 4 X-coordinate {m}
50.238035124848, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
200468, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B1_F5_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-4.402540559418, !- Vertex 1 X-coordinate {m}
50.321268859172, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
-4.402540559418, !- Vertex 2 X-coordinate {m}
50.321268859172, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
-3.888321677206, !- Vertex 3 X-coordinate {m}
44.443720140431, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
-3.888321677206, !- Vertex 4 X-coordinate {m}
44.443720140431, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
46D347, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_GL, !- Construction Name
B1_F4_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-3.888321677206, !- Vertex 1 X-coordinate {m}
44.443720140431, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
-3.888321677206, !- Vertex 2 X-coordinate {m}
44.443720140431, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
4BF298, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_GL, !- Construction Name
B1_F3_LB, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-3.888321677206, !- Vertex 1 X-coordinate {m}
44.443720140431, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
-3.888321677206, !- Vertex 2 X-coordinate {m}
44.443720140431, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
645F2E, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_GL, !- Construction Name
B1_F2_CL, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-3.888321677206, !- Vertex 1 X-coordinate {m}
44.443720140431, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
-3.888321677206, !- Vertex 2 X-coordinate {m}
44.443720140431, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
566494, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_GL, !- Construction Name
B1_F1_CN, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-3.888321677206, !- Vertex 1 X-coordinate {m}
44.443720140431, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
-3.888321677206, !- Vertex 2 X-coordinate {m}
44.443720140431, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
-0.908031053950, !- Vertex 3 X-coordinate {m}
10.378842439183, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
-0.908031053950, !- Vertex 4 X-coordinate {m}
10.378842439183, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
E6FDFE, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_GL, !- Construction Name
B1_F4_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-0.908031053950, !- Vertex 1 X-coordinate {m}
10.378842439183, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053950, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
-0.592963043918, !- Vertex 3 X-coordinate {m}
6.777598605582, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
-0.592963043918, !- Vertex 4 X-coordinate {m}
6.777598605582, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
3F7AEE, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B1_F2_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-0.592963043918, !- Vertex 1 X-coordinate {m}
6.777598605582, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
-0.592963043918, !- Vertex 2 X-coordinate {m}
6.777598605582, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
0.000000000000, !- Vertex 3 X-coordinate {m}
0.000000000000, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
0.000000000000, !- Vertex 4 X-coordinate {m}
0.000000000000, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
719426, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_L0, !- Construction Name
B1_F0_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-0.592963043918, !- Vertex 1 X-coordinate {m}
6.777598605582, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
-0.592963043918, !- Vertex 2 X-coordinate {m}
6.777598605582, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
0.000000000000, !- Vertex 3 X-coordinate {m}
0.000000000000, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
0.000000000000, !- Vertex 4 X-coordinate {m}
0.000000000000, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
14E777, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_L0, !- Construction Name
B1_F0_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
-0.908031053950, !- Vertex 1 X-coordinate {m}
10.378842439183, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
-0.908031053950, !- Vertex 2 X-coordinate {m}
10.378842439183, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
-0.592963043918, !- Vertex 3 X-coordinate {m}
6.777598605582, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
-0.592963043918, !- Vertex 4 X-coordinate {m}
6.777598605582, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
FBAC5D, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B1_F4_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
0.000000000000, !- Vertex 1 X-coordinate {m}
0.000000000000, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
0.000000000000, !- Vertex 2 X-coordinate {m}
0.000000000000, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
7.772760005483, !- Vertex 3 X-coordinate {m}
-1.599523221318, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
7.772760005483, !- Vertex 4 X-coordinate {m}
-1.599523221318, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
3BA882, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_RL, !- Construction Name
B1_F4_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
7.772760005483, !- Vertex 1 X-coordinate {m}
-1.599523221318, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
7.772760005483, !- Vertex 2 X-coordinate {m}
-1.599523221318, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
11.024619423024, !- Vertex 3 X-coordinate {m}
-2.268709539582, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
11.024619423024, !- Vertex 4 X-coordinate {m}
-2.268709539582, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
197952, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_GL, !- Construction Name
B1_F2_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
7.772760005483, !- Vertex 1 X-coordinate {m}
-1.599523221318, !- Vertex 1 Y-coordinate {m}
21.760000000000, !- Vertex 1 Z-coordinate {m}
7.772760005483, !- Vertex 2 X-coordinate {m}
-1.599523221318, !- Vertex 2 Y-coordinate {m}
12.580000000000, !- Vertex 2 Z-coordinate {m}
11.024619423024, !- Vertex 3 X-coordinate {m}
-2.268709539582, !- Vertex 3 Y-coordinate {m}
12.580000000000, !- Vertex 3 Z-coordinate {m}
11.024619423024, !- Vertex 4 X-coordinate {m}
-2.268709539582, !- Vertex 4 Y-coordinate {m}
21.760000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
147F4F, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_L0, !- Construction Name
B1_F0_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
7.772760005483, !- Vertex 1 X-coordinate {m}
-1.599523221318, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
7.772760005483, !- Vertex 2 X-coordinate {m}
-1.599523221318, !- Vertex 2 Y-coordinate {m}
3.910000000000, !- Vertex 2 Z-coordinate {m}
11.024619423024, !- Vertex 3 X-coordinate {m}
-2.268709539582, !- Vertex 3 Y-coordinate {m}
3.910000000000, !- Vertex 3 Z-coordinate {m}
11.024619423024, !- Vertex 4 X-coordinate {m}
-2.268709539582, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
D3D445, !- Name
Wall, !- Surface Type
EXT_WALL_SW_EF_GL, !- Construction Name
B1_F0_SC, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
, !- TRNSYS 17 - additional surface data
4, !- Number of Vertices
7.772760005483, !- Vertex 1 X-coordinate {m}
-1.599523221318, !- Vertex 1 Y-coordinate {m}
12.580000000000, !- Vertex 1 Z-coordinate {m}
7.772760005483, !- Vertex 2 X-coordinate {m}
-1.599523221318, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
11.024619423024, !- Vertex 3 X-coordinate {m}
-2.268709539582, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
11.024619423024, !- Vertex 4 X-coordinate {m}
-2.268709539582, !- Vertex 4 Y-coordinate {m}
12.580000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
4A39A2, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
41.284559512200, !- Vertex 1 X-coordinate {m}
12.887672865633, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
41.284559512200, !- Vertex 2 X-coordinate {m}
12.887672865633, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
36.921715218697, !- Vertex 3 X-coordinate {m}
3.997015756185, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
36.921715218697, !- Vertex 4 X-coordinate {m}
3.997015756185, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
53DFBC, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
49.664936899525, !- Vertex 1 X-coordinate {m}
-10.220336122569, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
49.664936899525, !- Vertex 2 X-coordinate {m}
-10.220336122569, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
51.954078169563, !- Vertex 3 X-coordinate {m}
0.903569722315, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
51.954078169563, !- Vertex 4 X-coordinate {m}
0.903569722315, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
B2512F, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
51.954078169563, !- Vertex 1 X-coordinate {m}
0.903569722315, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
51.954078169563, !- Vertex 2 X-coordinate {m}
0.903569722315, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
49.568123181230, !- Vertex 3 X-coordinate {m}
1.394565251080, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
49.568123181230, !- Vertex 4 X-coordinate {m}
1.394565251080, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
C71486, !- Name
, !- Transmittance Schedule Name
6, !- Number of Vertices
36.921715218697, !- Vertex 1 X-coordinate {m}
3.997015756185, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
36.921715218697, !- Vertex 2 X-coordinate {m}
3.997015756185, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
13.313760693062, !- Vertex 3 X-coordinate {m}
8.855196305301, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
13.313760665876, !- Vertex 4 X-coordinate {m}
8.855196326266, !- Vertex 4 Y-coordinate {m}
30.940000000000, !- Vertex 4 Z-coordinate {m}
17.231663578072, !- Vertex 5 X-coordinate {m}
8.048947747597, !- Vertex 5 Y-coordinate {m}
30.940000000000, !- Vertex 5 Z-coordinate {m}
17.231663578072, !- Vertex 6 X-coordinate {m}
8.048947747597, !- Vertex 6 Y-coordinate {m}
26.350000000000; !- Vertex 6 Z-coordinate {m}
Shading:Building:Detailed,
37D0D3, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
36.921715218697, !- Vertex 1 X-coordinate {m}
3.997015756185, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
36.921715218697, !- Vertex 2 X-coordinate {m}
3.997015756185, !- Vertex 2 Y-coordinate {m}
21.760000000000, !- Vertex 2 Z-coordinate {m}
49.568123181230, !- Vertex 3 X-coordinate {m}
1.394565251080, !- Vertex 3 Y-coordinate {m}
21.760000000000, !- Vertex 3 Z-coordinate {m}
49.568123181230, !- Vertex 4 X-coordinate {m}
1.394565251080, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
68F996, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
49.568123181230, !- Vertex 1 X-coordinate {m}
1.394565251080, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
49.568123181230, !- Vertex 2 X-coordinate {m}
1.394565251080, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
52.505893082225, !- Vertex 3 X-coordinate {m}
7.380253822592, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
52.505893082225, !- Vertex 4 X-coordinate {m}
7.380253822592, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
98B147, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
41.284559512200, !- Vertex 1 X-coordinate {m}
12.887672865633, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
36.921715218697, !- Vertex 2 X-coordinate {m}
3.997015756185, !- Vertex 2 Y-coordinate {m}
30.940000000000, !- Vertex 2 Z-coordinate {m}
49.568123181230, !- Vertex 3 X-coordinate {m}
1.394565251080, !- Vertex 3 Y-coordinate {m}
30.940000000000, !- Vertex 3 Z-coordinate {m}
52.505893082225, !- Vertex 4 X-coordinate {m}
7.380253822592, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
39597A, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
17.231663578072, !- Vertex 1 X-coordinate {m}
8.048947747597, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
14.942522335724, !- Vertex 2 X-coordinate {m}
-3.074958115804, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
49.664936899525, !- Vertex 3 X-coordinate {m}
-10.220336122569, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
51.954078169563, !- Vertex 4 X-coordinate {m}
0.903569722315, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
DB8F3C, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
13.313760665876, !- Vertex 1 X-coordinate {m}
8.855196326266, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
11.024619423024, !- Vertex 2 X-coordinate {m}
-2.268709539582, !- Vertex 2 Y-coordinate {m}
30.940000000000, !- Vertex 2 Z-coordinate {m}
14.942522335724, !- Vertex 3 X-coordinate {m}
-3.074958115804, !- Vertex 3 Y-coordinate {m}
30.940000000000, !- Vertex 3 Z-coordinate {m}
17.231663578072, !- Vertex 4 X-coordinate {m}
8.048947747597, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
50D50D, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
14.942522335724, !- Vertex 1 X-coordinate {m}
-3.074958115804, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
14.942522335724, !- Vertex 2 X-coordinate {m}
-3.074958115804, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
17.231663578072, !- Vertex 3 X-coordinate {m}
8.048947747597, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
17.231663578072, !- Vertex 4 X-coordinate {m}
8.048947747597, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
AD6C25, !- Name
, !- Transmittance Schedule Name
6, !- Number of Vertices
24.536619678792, !- Vertex 1 X-coordinate {m}
65.305502396701, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
25.617786667577, !- Vertex 2 X-coordinate {m}
52.947707166873, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
61.480746077348, !- Vertex 3 X-coordinate {m}
56.085309555718, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
69.879993866232, !- Vertex 4 X-coordinate {m}
51.972025662008, !- Vertex 4 Y-coordinate {m}
26.350000000000, !- Vertex 4 Z-coordinate {m}
75.277154679420, !- Vertex 5 X-coordinate {m}
62.968709208516, !- Vertex 5 Y-coordinate {m}
26.350000000000, !- Vertex 5 Z-coordinate {m}
63.559777555276, !- Vertex 6 X-coordinate {m}
68.719586325875, !- Vertex 6 Y-coordinate {m}
26.350000000000; !- Vertex 6 Z-coordinate {m}
Shading:Building:Detailed,
6BCD35, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
25.617786667577, !- Vertex 1 X-coordinate {m}
52.947707166873, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
25.617786667577, !- Vertex 2 X-coordinate {m}
52.947707166873, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
24.536619678792, !- Vertex 3 X-coordinate {m}
65.305502396701, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
24.536619678792, !- Vertex 4 X-coordinate {m}
65.305502396701, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
284C5B, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
12.582233580160, !- Vertex 1 X-coordinate {m}
64.259629133658, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
13.663400568944, !- Vertex 2 X-coordinate {m}
51.901833903830, !- Vertex 2 Y-coordinate {m}
30.940000000000, !- Vertex 2 Z-coordinate {m}
25.617786667577, !- Vertex 3 X-coordinate {m}
52.947707166873, !- Vertex 3 Y-coordinate {m}
30.940000000000, !- Vertex 3 Z-coordinate {m}
24.536619678792, !- Vertex 4 X-coordinate {m}
65.305502396701, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
88915C, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
24.536619678792, !- Vertex 1 X-coordinate {m}
65.305502396701, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
24.536619678792, !- Vertex 2 X-coordinate {m}
65.305502396701, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
12.582233580160, !- Vertex 3 X-coordinate {m}
64.259629133658, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
12.582233580160, !- Vertex 4 X-coordinate {m}
64.259629133658, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
301B1E, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
12.187071739319, !- Vertex 1 X-coordinate {m}
68.776349642523, !- Vertex 1 Y-coordinate {m}
7.990000000000, !- Vertex 1 Z-coordinate {m}
12.582233580160, !- Vertex 2 X-coordinate {m}
64.259629133658, !- Vertex 2 Y-coordinate {m}
7.990000000000, !- Vertex 2 Z-coordinate {m}
24.536619678792, !- Vertex 3 X-coordinate {m}
65.305502396701, !- Vertex 3 Y-coordinate {m}
7.990000000000, !- Vertex 3 Z-coordinate {m}
24.141457837952, !- Vertex 4 X-coordinate {m}
69.822222905565, !- Vertex 4 Y-coordinate {m}
7.990000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
D3BB76, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
28.607569344989, !- Vertex 1 X-coordinate {m}
109.689202416929, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
28.607569344989, !- Vertex 2 X-coordinate {m}
109.689202416929, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
20.713968801880, !- Vertex 3 X-coordinate {m}
108.998601855005, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
20.713968801880, !- Vertex 4 X-coordinate {m}
108.998601855005, !- Vertex 4 Y-coordinate {m}
17.170000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
F16885, !- Name
, !- Transmittance Schedule Name
5, !- Number of Vertices
20.713968801880, !- Vertex 1 X-coordinate {m}
108.998601855005, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
23.851575540796, !- Vertex 2 X-coordinate {m}
73.135592723702, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
40.069625225729, !- Vertex 3 X-coordinate {m}
74.554488215634, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
37.543130493972, !- Vertex 4 X-coordinate {m}
103.432455142278, !- Vertex 4 Y-coordinate {m}
17.170000000000, !- Vertex 4 Z-coordinate {m}
28.607569344989, !- Vertex 5 X-coordinate {m}
109.689202416929, !- Vertex 5 Y-coordinate {m}
17.170000000000; !- Vertex 5 Z-coordinate {m}
Shading:Building:Detailed,
ACE14B, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
75.277154679420, !- Vertex 1 X-coordinate {m}
62.968709208516, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
75.277154679420, !- Vertex 2 X-coordinate {m}
62.968709208516, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
69.879993866232, !- Vertex 3 X-coordinate {m}
51.972025662008, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
69.879993866232, !- Vertex 4 X-coordinate {m}
51.972025662008, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
C84BDA, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
75.277154679420, !- Vertex 1 X-coordinate {m}
62.968709208516, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
69.879993866232, !- Vertex 2 X-coordinate {m}
51.972025662008, !- Vertex 2 Y-coordinate {m}
30.940000000000, !- Vertex 2 Z-coordinate {m}
76.894075198257, !- Vertex 3 X-coordinate {m}
48.537086189170, !- Vertex 3 Y-coordinate {m}
30.940000000000, !- Vertex 3 Z-coordinate {m}
82.288244339831, !- Vertex 4 X-coordinate {m}
59.527673495750, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
5E3DE4, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
24.536619678792, !- Vertex 1 X-coordinate {m}
65.305502396701, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
24.536619678792, !- Vertex 2 X-coordinate {m}
65.305502396701, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
40.754669363726, !- Vertex 3 X-coordinate {m}
66.724397888632, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
40.754669363726, !- Vertex 4 X-coordinate {m}
66.724397888632, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
61F278, !- Name
, !- Transmittance Schedule Name
8, !- Number of Vertices
20.713968801880, !- Vertex 1 X-coordinate {m}
108.998601855005, !- Vertex 1 Y-coordinate {m}
17.170000000000, !- Vertex 1 Z-coordinate {m}
20.713968801880, !- Vertex 2 X-coordinate {m}
108.998601855005, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
24.141457837952, !- Vertex 3 X-coordinate {m}
69.822222905565, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
24.141457837952, !- Vertex 4 X-coordinate {m}
69.822222905565, !- Vertex 4 Y-coordinate {m}
7.990000000000, !- Vertex 4 Z-coordinate {m}
24.536619678792, !- Vertex 5 X-coordinate {m}
65.305502396701, !- Vertex 5 Y-coordinate {m}
7.990000000000, !- Vertex 5 Z-coordinate {m}
24.536619678792, !- Vertex 6 X-coordinate {m}
65.305502396701, !- Vertex 6 Y-coordinate {m}
30.940000000000, !- Vertex 6 Z-coordinate {m}
23.851575540796,
73.135592723702,
30.940000000000,
23.851575540796,
73.135592723702,
17.170000000000;
Shading:Building:Detailed,
7AED95, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
23.851575540796, !- Vertex 1 X-coordinate {m}
73.135592723702, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
24.536619678792, !- Vertex 2 X-coordinate {m}
65.305502396701, !- Vertex 2 Y-coordinate {m}
30.940000000000, !- Vertex 2 Z-coordinate {m}
40.754669363726, !- Vertex 3 X-coordinate {m}
66.724397888632, !- Vertex 3 Y-coordinate {m}
30.940000000000, !- Vertex 3 Z-coordinate {m}
40.069625225729, !- Vertex 4 X-coordinate {m}
74.554488215634, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
3D3D4E, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
40.069625225729, !- Vertex 1 X-coordinate {m}
74.554488215634, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
40.069625225729, !- Vertex 2 X-coordinate {m}
74.554488215634, !- Vertex 2 Y-coordinate {m}
17.170000000000, !- Vertex 2 Z-coordinate {m}
23.851575540796, !- Vertex 3 X-coordinate {m}
73.135592723702, !- Vertex 3 Y-coordinate {m}
17.170000000000, !- Vertex 3 Z-coordinate {m}
23.851575540796, !- Vertex 4 X-coordinate {m}
73.135592723702, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
2EBB04, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
76.894075198257, !- Vertex 1 X-coordinate {m}
48.537086189170, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
76.894075198257, !- Vertex 2 X-coordinate {m}
48.537086189170, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
82.288244339831, !- Vertex 3 X-coordinate {m}
59.527673495750, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
82.288244339831, !- Vertex 4 X-coordinate {m}
59.527673495750, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
761FAC, !- Name
, !- Transmittance Schedule Name
6, !- Number of Vertices
13.663400568944, !- Vertex 1 X-coordinate {m}
51.901833903830, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
13.663400568944, !- Vertex 2 X-coordinate {m}
51.901833903830, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
61.480746077348, !- Vertex 3 X-coordinate {m}
56.085309555718, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
61.480746077348, !- Vertex 4 X-coordinate {m}
56.085309555718, !- Vertex 4 Y-coordinate {m}
26.350000000000, !- Vertex 4 Z-coordinate {m}
25.617786667577, !- Vertex 5 X-coordinate {m}
52.947707166873, !- Vertex 5 Y-coordinate {m}
26.350000000000, !- Vertex 5 Z-coordinate {m}
25.617786667577, !- Vertex 6 X-coordinate {m}
52.947707166873, !- Vertex 6 Y-coordinate {m}
30.940000000000; !- Vertex 6 Z-coordinate {m}
Shading:Building:Detailed,
9465D0, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
52.505893082225, !- Vertex 1 X-coordinate {m}
7.380253822592, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
52.505893082225, !- Vertex 2 X-coordinate {m}
7.380253822592, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
41.284559564175, !- Vertex 3 X-coordinate {m}
12.887672971532, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
41.284559512200, !- Vertex 4 X-coordinate {m}
12.887672865633, !- Vertex 4 Y-coordinate {m}
30.940000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
845D9E, !- Name
, !- Transmittance Schedule Name
6, !- Number of Vertices
69.879993866232, !- Vertex 1 X-coordinate {m}
51.972025662008, !- Vertex 1 Y-coordinate {m}
30.940000000000, !- Vertex 1 Z-coordinate {m}
69.879993866232, !- Vertex 2 X-coordinate {m}
51.972025662008, !- Vertex 2 Y-coordinate {m}
26.350000000000, !- Vertex 2 Z-coordinate {m}
73.517257553134, !- Vertex 3 X-coordinate {m}
50.190783041650, !- Vertex 3 Y-coordinate {m}
26.350000000000, !- Vertex 3 Z-coordinate {m}
73.517257553134, !- Vertex 4 X-coordinate {m}
50.190783041650, !- Vertex 4 Y-coordinate {m}
0.000000000000, !- Vertex 4 Z-coordinate {m}
76.894075198257, !- Vertex 5 X-coordinate {m}
48.537086189170, !- Vertex 5 Y-coordinate {m}
0.000000000000, !- Vertex 5 Z-coordinate {m}
76.894075198257, !- Vertex 6 X-coordinate {m}
48.537086189170, !- Vertex 6 Y-coordinate {m}
30.940000000000; !- Vertex 6 Z-coordinate {m}
Shading:Building:Detailed,
B7E988, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
62.288489505666, !- Vertex 1 X-coordinate {m}
55.689741033696, !- Vertex 1 Y-coordinate {m}
26.350000000000, !- Vertex 1 Z-coordinate {m}
62.288489505666, !- Vertex 2 X-coordinate {m}
55.689741033696, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
61.480746077348, !- Vertex 3 X-coordinate {m}
56.085309555719, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
61.480746077348, !- Vertex 4 X-coordinate {m}
56.085309555718, !- Vertex 4 Y-coordinate {m}
26.350000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
10E4BC, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
0.909563270293, !- Vertex 1 X-coordinate {m}
-10.396718601583, !- Vertex 1 Y-coordinate {m}
8.750000000000, !- Vertex 1 Z-coordinate {m}
0.896000000000, !- Vertex 2 X-coordinate {m}
-10.393927473878, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
60.382467598013, !- Vertex 3 X-coordinate {m}
-22.635394624556, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
60.382467598013, !- Vertex 4 X-coordinate {m}
-22.635394624556, !- Vertex 4 Y-coordinate {m}
8.750000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
43D89B, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
50.154674763612, !- Vertex 1 X-coordinate {m}
-10.321117194597, !- Vertex 1 Y-coordinate {m}
6.900000000000, !- Vertex 1 Z-coordinate {m}
50.154674763612, !- Vertex 2 X-coordinate {m}
-10.321117194597, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
51.881215596101, !- Vertex 3 X-coordinate {m}
-2.354634933056, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
51.881215596101, !- Vertex 4 X-coordinate {m}
-2.354634933056, !- Vertex 4 Y-coordinate {m}
6.900000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
9DCFF7, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
51.881215596101, !- Vertex 1 X-coordinate {m}
-2.354634933056, !- Vertex 1 Y-coordinate {m}
6.900000000000, !- Vertex 1 Z-coordinate {m}
51.881215596101, !- Vertex 2 X-coordinate {m}
-2.354634933056, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
59.908192476734, !- Vertex 3 X-coordinate {m}
-4.094286499565, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
59.908192476734, !- Vertex 4 X-coordinate {m}
-4.094286499565, !- Vertex 4 Y-coordinate {m}
6.900000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
47F8C8, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
59.908192476734, !- Vertex 1 X-coordinate {m}
-4.094286499565, !- Vertex 1 Y-coordinate {m}
6.900000000000, !- Vertex 1 Z-coordinate {m}
59.908192476734, !- Vertex 2 X-coordinate {m}
-4.094286499565, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
60.407052850131, !- Vertex 3 X-coordinate {m}
0.142127044854, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
60.407052850131, !- Vertex 4 X-coordinate {m}
0.142127044854, !- Vertex 4 Y-coordinate {m}
6.900000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
5899D6, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
60.407052850131, !- Vertex 1 X-coordinate {m}
0.142127044854, !- Vertex 1 Y-coordinate {m}
6.900000000000, !- Vertex 1 Z-coordinate {m}
60.407052850131, !- Vertex 2 X-coordinate {m}
0.142127044854, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
54.527518948911, !- Vertex 3 X-coordinate {m}
2.913603385075, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
54.527518948911, !- Vertex 4 X-coordinate {m}
2.913603385075, !- Vertex 4 Y-coordinate {m}
6.900000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
2CF626, !- Name
, !- Transmittance Schedule Name
24, !- Number of Vertices
54.527518948911, !- Vertex 1 X-coordinate {m}
2.913603385074, !- Vertex 1 Y-coordinate {m}
7.380000000000, !- Vertex 1 Z-coordinate {m}
54.527518948911, !- Vertex 2 X-coordinate {m}
2.913603385075, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
87.587104273672, !- Vertex 3 X-coordinate {m}
68.728346054125, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
87.587104273672, !- Vertex 4 X-coordinate {m}
68.728346054126, !- Vertex 4 Y-coordinate {m}
7.380000000000, !- Vertex 4 Z-coordinate {m}
86.756337806944, !- Vertex 5 X-coordinate {m}
67.074463203248, !- Vertex 5 Y-coordinate {m}
10.380000000000, !- Vertex 5 Z-coordinate {m}
84.749644401923, !- Vertex 6 X-coordinate {m}
63.079554955919, !- Vertex 6 Y-coordinate {m}
7.380000000000, !- Vertex 6 Z-coordinate {m}
83.741006844137, !- Vertex 7 X-coordinate {m}
61.071567842351, !- Vertex 7 Y-coordinate {m}
10.380000000000, !- Vertex 7 Z-coordinate {m}
81.558677421530, !- Vertex 8 X-coordinate {m}
56.727004897686, !- Vertex 8 Y-coordinate {m}
7.380000000000, !- Vertex 8 Z-coordinate {m}
80.720212195173, !- Vertex 9 X-coordinate {m}
55.057795421295, !- Vertex 9 Y-coordinate {m}
10.380000000000, !- Vertex 9 Z-coordinate {m}
78.625812447315, !- Vertex 10 X-coordinate {m}
50.888282128938, !- Vertex 10 Y-coordinate {m}
7.380000000000, !- Vertex 10 Z-coordinate {m}
77.853589947211, !- Vertex 11 X-coordinate {m}
49.350948111336, !- Vertex 11 Y-coordinate {m}
10.380000000000, !- Vertex 11 Z-coordinate {m}
75.638874012860, !- Vertex 12 X-coordinate {m}
44.941910373189, !- Vertex 12 Y-coordinate {m}
7.380000000000, !- Vertex 12 Z-coordinate {m}
74.578055413820, !- Vertex 13 X-coordinate {m}
42.830041684320, !- Vertex 13 Y-coordinate {m}
10.380000000000, !- Vertex 13 Z-coordinate {m}
72.468119647922, !- Vertex 14 X-coordinate {m}
38.629599418735, !- Vertex 14 Y-coordinate {m}
7.380000000000, !- Vertex 14 Z-coordinate {m}
71.384314263671, !- Vertex 15 X-coordinate {m}
36.471968832414, !- Vertex 15 Y-coordinate {m}
10.380000000000, !- Vertex 15 Z-coordinate {m}
68.997392221863, !- Vertex 16 X-coordinate {m}
31.720104632985, !- Vertex 16 Y-coordinate {m}
7.380000000000, !- Vertex 16 Z-coordinate {m}
68.065889592865, !- Vertex 17 X-coordinate {m}
29.865677082827, !- Vertex 17 Y-coordinate {m}
10.380000000000, !- Vertex 17 Z-coordinate {m}
65.253514021708, !- Vertex 18 X-coordinate {m}
24.266823597941, !- Vertex 18 Y-coordinate {m}
7.380000000000, !- Vertex 18 Z-coordinate {m}
64.581963059885, !- Vertex 19 X-coordinate {m}
22.929905626727, !- Vertex 19 Y-coordinate {m}
10.380000000000, !- Vertex 19 Z-coordinate {m}
62.427246049596, !- Vertex 20 X-coordinate {m}
18.640313238811, !- Vertex 20 Y-coordinate {m}
7.380000000000, !- Vertex 20 Z-coordinate {m}
61.700701799743, !- Vertex 21 X-coordinate {m}
17.193915095215, !- Vertex 21 Y-coordinate {m}
10.380000000000, !- Vertex 21 Z-coordinate {m}
58.925623698153, !- Vertex 22 X-coordinate {m}
11.669313097081, !- Vertex 22 Y-coordinate {m}
7.380000000000, !- Vertex 22 Z-coordinate {m}
58.069067331916, !- Vertex 23 X-coordinate {m}
9.964087932530, !- Vertex 23 Y-coordinate {m}
10.380000000000, !- Vertex 23 Z-coordinate {m}
55.488872097899, !- Vertex 24 X-coordinate {m}
4.827457097793, !- Vertex 24 Y-coordinate {m}
7.380000000000; !- Vertex 24 Z-coordinate {m}
Shading:Building:Detailed,
495DC0, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
2.100834437921, !- Vertex 1 X-coordinate {m}
68.683427371966, !- Vertex 1 Y-coordinate {m}
26.000000000000, !- Vertex 1 Z-coordinate {m}
2.100834437921, !- Vertex 2 X-coordinate {m}
68.683427371966, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
-6.998533520815, !- Vertex 3 X-coordinate {m}
67.888836711362, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
-6.998533520815, !- Vertex 4 X-coordinate {m}
67.888836711362, !- Vertex 4 Y-coordinate {m}
26.000000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
B8E407, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
2.100834437921, !- Vertex 1 X-coordinate {m}
124.833830604480, !- Vertex 1 Y-coordinate {m}
26.000000000000, !- Vertex 1 Z-coordinate {m}
2.100834437921, !- Vertex 2 X-coordinate {m}
124.833830604480, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
2.100834437921, !- Vertex 3 X-coordinate {m}
68.683427371966, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
2.100834437921, !- Vertex 4 X-coordinate {m}
68.683427371966, !- Vertex 4 Y-coordinate {m}
26.000000000000; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
9E5ADC, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
21.061911082713, !- Vertex 1 X-coordinate {m}
133.601365746714, !- Vertex 1 Y-coordinate {m}
21.737730223961, !- Vertex 1 Z-coordinate {m}
21.061911082713, !- Vertex 2 X-coordinate {m}
133.601365746714, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
2.100834437921, !- Vertex 3 X-coordinate {m}
124.833830604480, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
2.100834437921, !- Vertex 4 X-coordinate {m}
124.833830604480, !- Vertex 4 Y-coordinate {m}
21.737730223961; !- Vertex 4 Z-coordinate {m}
Shading:Building:Detailed,
C57FAF, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
31.974078756555, !- Vertex 1 X-coordinate {m}
119.368476680245, !- Vertex 1 Y-coordinate {m}
18.000000000000, !- Vertex 1 Z-coordinate {m}
31.974078756555, !- Vertex 2 X-coordinate {m}
119.368476680245, !- Vertex 2 Y-coordinate {m}
0.000000000000, !- Vertex 2 Z-coordinate {m}
21.061911082713, !- Vertex 3 X-coordinate {m}
133.601365746714, !- Vertex 3 Y-coordinate {m}
0.000000000000, !- Vertex 3 Z-coordinate {m}
21.061911082713, !- Vertex 4 X-coordinate {m}
133.601365746714, !- Vertex 4 Y-coordinate {m}
18.000000000000; !- Vertex 4 Z-coordinate {m}
-------------- next part --------------
TRNSHD Version 1.0.182
Integrated 2D clipping routine: GPC general polygon clipper library Version 2.2
3 from Alan Murta, University of Manchester,UK
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
TRNSHD Message 2 : Successfully opened shading log file.
Reported information : Not available
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
TRNSHD Message 18 : Shading mask calculation is switched ON.
Reported information : Not available
*** Notice at time : 0.000000
Orientation of wall SURF= 10: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 15: azimuth angle= 116.14°, slope= 90.00°
Orientation of window SURF= 22: azimuth angle= 116.14°, slope= 90.00°
Orientation of wall SURF= 19: azimuth angle= 296.14°, slope= 90.00°
Orientation of window SURF= 23: azimuth angle= 296.14°, slope= 90.00°
Orientation of window SURF= 24: azimuth angle= 296.14°, slope= 90.00°
Orientation of wall SURF= 26: azimuth angle= 296.14°, slope= 90.00°
Orientation of window SURF= 32: azimuth angle= 296.14°, slope= 90.00°
Orientation of wall SURF= 29: azimuth angle= 116.14°, slope= 90.00°
Orientation of window SURF= 33: azimuth angle= 116.14°, slope= 90.00°
Orientation of wall SURF= 36: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 45: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 39: azimuth angle= 265.00°, slope= 90.00°
Orientation of window SURF= 42: azimuth angle= 265.00°, slope= 90.00°
Orientation of window SURF= 43: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 40: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 48: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 50: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 52: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 53: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 54: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 59: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 60: azimuth angle= 175.00°, slope= 90.00°
Orientation of window SURF= 64: azimuth angle= 175.00°, slope= 90.00°
Orientation of window SURF= 65: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 62: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 68: azimuth angle= 296.14°, slope= 90.00°
Orientation of window SURF= 73: azimuth angle= 296.14°, slope= 90.00°
Orientation of wall SURF= 69: azimuth angle= 116.14°, slope= 90.00°
Orientation of window SURF= 72: azimuth angle= 116.14°, slope= 90.00°
Orientation of wall SURF= 75: azimuth angle= 281.63°, slope= 90.00°
Orientation of wall SURF= 79: azimuth angle= 11.63°, slope= 90.00°
Orientation of window SURF= 82: azimuth angle= 11.63°, slope= 90.00°
Orientation of wall SURF= 80: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 81: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 84: azimuth angle= 11.63°, slope= 90.00°
Orientation of window SURF= 98: azimuth angle= 11.63°, slope= 90.00°
Orientation of wall SURF= 85: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 97: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 87: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 103: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 89: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 102: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 90: azimuth angle= 11.63°, slope= 90.00°
Orientation of window SURF= 101: azimuth angle= 11.63°, slope= 90.00°
Orientation of wall SURF= 95: azimuth angle= 281.63°, slope= 90.00°
Orientation of window SURF= 99: azimuth angle= 281.63°, slope= 90.00°
Orientation of wall SURF= 96: azimuth angle= 11.63°, slope= 90.00°
Orientation of window SURF= 100: azimuth angle= 11.63°, slope= 90.00°
Orientation of wall SURF= 104: azimuth angle= 265.00°, slope= 90.00°
Orientation of window SURF= 115: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 105: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 109: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 114: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 116: azimuth angle= 265.00°, slope= 90.00°
Orientation of window SURF= 126: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 117: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 119: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 129: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 121: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 127: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 124: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 128: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 125: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 131: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 134: azimuth angle= 175.00°, slope= 90.00°
Orientation of window SURF= 137: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 143: azimuth angle= 116.14°, slope= 90.00°
Orientation of window SURF= 146: azimuth angle= 116.14°, slope= 90.00°
Orientation of wall SURF= 145: azimuth angle= 296.14°, slope= 90.00°
Orientation of window SURF= 147: azimuth angle= 296.14°, slope= 90.00°
Orientation of window SURF= 148: azimuth angle= 296.14°, slope= 90.00°
Orientation of wall SURF= 150: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 153: azimuth angle= 265.00°, slope= 90.00°
Orientation of window SURF= 156: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 161: azimuth angle= 265.00°, slope= 90.00°
Orientation of window SURF= 163: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 169: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 170: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 172: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 176: azimuth angle= 175.00°, slope= 90.00°
Orientation of window SURF= 180: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 178: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 181: azimuth angle= 265.00°, slope= 90.00°
Orientation of window SURF= 191: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 183: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 184: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 186: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 187: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 190: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 192: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 193: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 204: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 197: azimuth angle= 265.00°, slope= 90.00°
Orientation of window SURF= 205: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 202: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 203: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 210: azimuth angle= 281.63°, slope= 90.00°
Orientation of window SURF= 216: azimuth angle= 281.63°, slope= 90.00°
Orientation of wall SURF= 211: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 220: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 221: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 213: azimuth angle= 11.63°, slope= 90.00°
Orientation of window SURF= 217: azimuth angle= 11.63°, slope= 90.00°
Orientation of wall SURF= 214: azimuth angle= 11.63°, slope= 90.00°
Orientation of window SURF= 218: azimuth angle= 11.63°, slope= 90.00°
Orientation of window SURF= 222: azimuth angle= 11.63°, slope= 90.00°
Orientation of wall SURF= 215: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 219: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 224: azimuth angle= 296.14°, slope= 90.00°
Orientation of window SURF= 230: azimuth angle= 296.14°, slope= 90.00°
Orientation of window SURF= 232: azimuth angle= 296.14°, slope= 90.00°
Orientation of wall SURF= 227: azimuth angle= 116.14°, slope= 90.00°
Orientation of window SURF= 231: azimuth angle= 116.14°, slope= 90.00°
Orientation of wall SURF= 235: azimuth angle= 116.14°, slope= 90.00°
Orientation of window SURF= 240: azimuth angle= 116.14°, slope= 90.00°
Orientation of wall SURF= 237: azimuth angle= 296.14°, slope= 90.00°
Orientation of window SURF= 239: azimuth angle= 296.14°, slope= 90.00°
Orientation of wall SURF= 245: azimuth angle= 175.00°, slope= 90.00°
Orientation of window SURF= 248: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 246: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 250: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 253: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 254: azimuth angle= 265.00°, slope= 90.00°
Orientation of window SURF= 259: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 255: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 260: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 256: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 257: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 262: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 271: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 266: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 267: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 268: azimuth angle= 265.00°, slope= 90.00°
Orientation of window SURF= 270: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 272: azimuth angle= 296.14°, slope= 90.00°
Orientation of window SURF= 278: azimuth angle= 296.14°, slope= 90.00°
Orientation of window SURF= 280: azimuth angle= 296.14°, slope= 90.00°
Orientation of wall SURF= 273: azimuth angle= 116.14°, slope= 90.00°
Orientation of window SURF= 279: azimuth angle= 116.14°, slope= 90.00°
Orientation of wall SURF= 281: azimuth angle= 296.14°, slope= 90.00°
Orientation of window SURF= 289: azimuth angle= 296.14°, slope= 90.00°
Orientation of wall SURF= 286: azimuth angle= 116.14°, slope= 90.00°
Orientation of window SURF= 288: azimuth angle= 116.14°, slope= 90.00°
Orientation of wall SURF= 291: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 294: azimuth angle= 175.00°, slope= 90.00°
Orientation of window SURF= 297: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 298: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 299: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 300: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 308: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 301: azimuth angle= 265.00°, slope= 90.00°
Orientation of window SURF= 309: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 302: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 304: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 310: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 311: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 314: azimuth angle= 265.00°, slope= 90.00°
Orientation of window SURF= 319: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 318: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 320: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 322: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 323: azimuth angle= 11.63°, slope= 90.00°
Orientation of window SURF= 335: azimuth angle= 11.63°, slope= 90.00°
Orientation of wall SURF= 324: azimuth angle= 11.63°, slope= 90.00°
Orientation of window SURF= 337: azimuth angle= 11.63°, slope= 90.00°
Orientation of wall SURF= 326: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 333: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 336: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 327: azimuth angle= 11.63°, slope= 90.00°
Orientation of window SURF= 338: azimuth angle= 11.63°, slope= 90.00°
Orientation of wall SURF= 328: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 334: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 329: azimuth angle= 281.63°, slope= 90.00°
Orientation of window SURF= 332: azimuth angle= 281.63°, slope= 90.00°
Orientation of wall SURF= 341: azimuth angle= 296.14°, slope= 90.00°
Orientation of window SURF= 346: azimuth angle= 296.14°, slope= 90.00°
Orientation of window SURF= 347: azimuth angle= 296.14°, slope= 90.00°
Orientation of wall SURF= 343: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 345: azimuth angle= 116.14°, slope= 90.00°
Orientation of window SURF= 348: azimuth angle= 116.14°, slope= 90.00°
Orientation of wall SURF= 350: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 353: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 355: azimuth angle= 175.00°, slope= 90.00°
Orientation of window SURF= 356: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 358: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 367: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 359: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 360: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 361: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 363: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 364: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 366: azimuth angle= 265.00°, slope= 90.00°
Orientation of window SURF= 368: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 369: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 371: azimuth angle= 265.00°, slope= 90.00°
Orientation of window SURF= 378: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 372: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 374: azimuth angle= 85.00°, slope= 90.00°
Orientation of window SURF= 379: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 375: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 1: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 2: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 3: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 4: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 5: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 6: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 7: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 8: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 9: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 11: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 12: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 13: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 14: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 16: azimuth angle= 26.14°, slope= 90.00°
Orientation of wall SURF= 17: azimuth angle= 26.14°, slope= 90.00°
Orientation of wall SURF= 18: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 20: azimuth angle= 206.09°, slope= 90.00°
Orientation of wall SURF= 21: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 27: azimuth angle= 206.14°, slope= 90.00°
Orientation of wall SURF= 28: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 30: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 31: azimuth angle= 26.14°, slope= 90.00°
Orientation of wall SURF= 34: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 35: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 37: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 38: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 41: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 46: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 47: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 49: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 51: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 56: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 57: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 58: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 61: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 63: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 66: azimuth angle= 206.14°, slope= 90.00°
Orientation of wall SURF= 67: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 70: azimuth angle= 26.14°, slope= 90.00°
Orientation of wall SURF= 71: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 74: azimuth angle= 281.63°, slope= 90.00°
Orientation of wall SURF= 76: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 77: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 78: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 86: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 88: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 91: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 92: azimuth angle= 281.63°, slope= 90.00°
Orientation of wall SURF= 93: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 94: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 106: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 107: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 108: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 110: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 111: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 112: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 113: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 118: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 120: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 122: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 123: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 130: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 132: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 133: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 135: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 136: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 138: azimuth angle= 26.14°, slope= 90.00°
Orientation of wall SURF= 139: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 140: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 141: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 142: azimuth angle= 206.09°, slope= 90.00°
Orientation of wall SURF= 144: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 149: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 151: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 152: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 154: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 155: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 157: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 158: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 159: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 160: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 162: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 164: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 165: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 166: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 167: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 168: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 171: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 173: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 174: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 175: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 177: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 179: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 182: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 185: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 188: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 189: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 194: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 195: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 196: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 198: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 199: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 200: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 201: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 206: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 207: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 208: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 209: azimuth angle= 281.63°, slope= 90.00°
Orientation of wall SURF= 212: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 223: azimuth angle= 206.09°, slope= 90.00°
Orientation of wall SURF= 225: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 226: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 228: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 229: azimuth angle= 26.14°, slope= 90.00°
Orientation of wall SURF= 233: azimuth angle= 26.14°, slope= 90.00°
Orientation of wall SURF= 234: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 236: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 238: azimuth angle= 206.14°, slope= 90.00°
Orientation of wall SURF= 241: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 242: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 243: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 244: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 247: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 249: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 251: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 252: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 258: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 261: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 263: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 264: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 265: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 269: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 274: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 275: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 276: azimuth angle= 26.14°, slope= 90.00°
Orientation of wall SURF= 277: azimuth angle= 206.09°, slope= 90.00°
Orientation of wall SURF= 282: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 283: azimuth angle= 206.14°, slope= 90.00°
Orientation of wall SURF= 284: azimuth angle= 26.14°, slope= 90.00°
Orientation of wall SURF= 285: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 287: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 290: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 292: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 293: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 295: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 296: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 303: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 305: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 306: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 307: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 312: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 313: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 315: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 316: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 317: azimuth angle= 0.00°, slope= 0.00°
Orientation of wall SURF= 321: azimuth angle= 281.63°, slope= 90.00°
Orientation of wall SURF= 325: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 330: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 331: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 339: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 340: azimuth angle= 206.09°, slope= 90.00°
Orientation of wall SURF= 342: azimuth angle= 26.14°, slope= 90.00°
Orientation of wall SURF= 344: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 349: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 351: azimuth angle= 85.00°, slope= 90.00°
Orientation of wall SURF= 352: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 354: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 357: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 362: azimuth angle= 265.00°, slope= 90.00°
Orientation of wall SURF= 365: azimuth angle= 0.00°, slope= 180.00°
Orientation of wall SURF= 370: azimuth angle= 355.00°, slope= 90.00°
Orientation of wall SURF= 373: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 376: azimuth angle= 175.00°, slope= 90.00°
Orientation of wall SURF= 377: azimuth angle= 0.00°, slope= 180.00°
Processing external WALL SURF= 15 at time 1
Processing external WALL SURF= 19 at time 1
Processing external WALL SURF= 26 at time 1
Processing external WALL SURF= 29 at time 1
Processing external WALL SURF= 36 at time 1
Processing external WALL SURF= 39 at time 1
Processing external WALL SURF= 52 at time 1
Processing external WALL SURF= 60 at time 1
Processing external WALL SURF= 68 at time 1
Processing external WALL SURF= 69 at time 1
Processing external WALL SURF= 79 at time 1
Processing external WALL SURF= 80 at time 1
Processing external WALL SURF= 84 at time 1
Processing external WALL SURF= 85 at time 1
Processing external WALL SURF= 87 at time 1
Processing external WALL SURF= 89 at time 1
Processing external WALL SURF= 90 at time 1
Processing external WALL SURF= 95 at time 1
Processing external WALL SURF= 96 at time 1
Processing external WALL SURF= 104 at time 1
Processing external WALL SURF= 109 at time 1
Processing external WALL SURF= 116 at time 1
Processing external WALL SURF= 119 at time 1
Processing external WALL SURF= 121 at time 1
Processing external WALL SURF= 124 at time 1
Processing external WALL SURF= 134 at time 1
Processing external WALL SURF= 143 at time 1
Processing external WALL SURF= 145 at time 1
Processing external WALL SURF= 153 at time 1
Processing external WALL SURF= 161 at time 1
Processing external WALL SURF= 170 at time 1
Processing external WALL SURF= 176 at time 1
Processing external WALL SURF= 181 at time 1
Processing external WALL SURF= 190 at time 1
Processing external WALL SURF= 193 at time 1
Processing external WALL SURF= 197 at time 1
Processing external WALL SURF= 210 at time 1
Processing external WALL SURF= 211 at time 1
Processing external WALL SURF= 213 at time 1
Processing external WALL SURF= 214 at time 1
Processing external WALL SURF= 215 at time 1
Processing external WALL SURF= 224 at time 1
Processing external WALL SURF= 227 at time 1
Processing external WALL SURF= 235 at time 1
Processing external WALL SURF= 237 at time 1
*** Fatal Error at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
TRNSHD Message 14 : The internal solar distribution did not sum up 1. Make sure that the zones with detailed beam radiation mode are CONVEX and CLOSED!!
Reported information : Not available
More information about the TRNSYS-users
mailing list