[TRNSYS-users] About TRNSYS
    David BRADLEY 
    d.bradley at tess-inc.com
       
    Mon Jun 15 07:46:25 PDT 2015
    
    
  
There is no automatic way to replace Type15 with the combination of 
Type9 and Type16. I would recommend that you add the Type9 and Type16 to 
your project before you remove Type15 and then change the connections 
that leave Type15 so that they leave Type16 one at a time. You may also 
need some other models (such as Type69) in order to get the sky temperature.
If you are getting an "ADJACENT wall not found error" then you need to 
go back to your *.idf and make sure that the walls that separate two 
zones are drawn in both zones, that they have EXACTLY the same vertices 
and shape in both zones, that they are defined as ADJACENT in both 
zones, and that their outward face is correct in both zones. You may 
have to break one wall up into two or more smaller walls in order to 
make the vertices of the walls match in the two zones.
kind regards,
  David
On 06/14/2015 06:10, Kenza Ferradji wrote:
>
> I want to say how replace type 15 by type 9 and type 16 for simulation.
>
> When I enter .idf file to TRNSYS I have a message "adj wall not found" 
> what can I do to avoid it.
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150615/f722a2c6/attachment-0003.htm>
    
    
More information about the TRNSYS-users
mailing list