    There is no automatic way to replace Type15 with the combination of
    Type9 and Type16. I would recommend that you add the Type9 and
    Type16 to your project before you remove Type15 and then change the
    connections that leave Type15 so that they leave Type16 one at a
    time. You may also need some other models (such as Type69) in order
    to get the sky temperature.<br>
    <br>
    If you are getting an "ADJACENT wall not found error" then you need
    to go back to your *.idf and make sure that the walls that separate
    two zones are drawn in both zones, that they have EXACTLY the same
    vertices and shape in both zones, that they are defined as ADJACENT
    in both zones, and that their outward face is correct in both zones.
    You may have to break one wall up into two or more smaller walls in
    order to make the vertices of the walls match in the two zones. <br>
    <br>
    kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 06/14/2015 06:10, Kenza Ferradji
      wrote:<br>
    </div>
    <blockquote cite="mid:DUB113-W63A6560AF50A6080753F2FFB90@phx.gbl"
      type="cite">
      <style><!--
.hmmessage P
{
margin:0px;
padding:0px
}
body.hmmessage
{
font-size: 12pt;
font-family:Calibri
}
--></style>
      <div dir="ltr"><!--[if gte mso 9]><xml>
 <w:WordDocument>
  <w:View>Normal</w:View>
  <w:Zoom>0</w:Zoom>
  <w:PunctuationKerning/>
  <w:ValidateAgainstSchemas/>
  <w:SaveIfXMLInvalid>false</w:SaveIfXMLInvalid>
  <w:IgnoreMixedContent>false</w:IgnoreMixedContent>
  <w:AlwaysShowPlaceholderText>false</w:AlwaysShowPlaceholderText>
  <w:Compatibility>
   <w:BreakWrappedTables/>
   <w:SnapToGridInCell/>
   <w:WrapTextWithPunct/>
   <w:UseAsianBreakRules/>
   <w:DontGrowAutofit/>
  </w:Compatibility>
  <w:BrowserLevel>MicrosoftInternetExplorer4</w:BrowserLevel>
 </w:WordDocument>
</xml><![endif]-->
        <p class="MsoNormal" dir="RTL" style="text-align:left"
          align="right"><span dir="LTR" style="mso-bidi-language:AR-DZ">I
            want to say how replace type 15 by type 9 and
            type 16 for simulation. </span><span
            style="mso-bidi-language:AR-DZ" lang="AR-DZ"></span></p>
        <p class="MsoNormal" dir="RTL" style="text-align:left"
          align="right"><span dir="LTR" style="mso-bidi-language:AR-DZ">When
            I enter .idf file to TRNSYS I have a
            message "adj wall not found" what can I do to avoid it.</span></p>
        <!--[if gte mso 9]><xml>
 <w:LatentStyles DefLockedState="false" LatentStyleCount="156">
 </w:LatentStyles>
</xml><![endif]--><!--[if gte mso 10]>
<style>
 /* Style Definitions */
 table.MsoNormalTable
        {mso-style-name:"Tableau Normal";
        mso-tstyle-rowband-size:0;
        mso-tstyle-colband-size:0;
        mso-style-noshow:yes;
        mso-style-parent:"";
        mso-padding-alt:0cm 5.4pt 0cm 5.4pt;
        mso-para-margin:0cm;
        mso-para-margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:10.0pt;
        font-family:"Times New Roman";
        mso-ansi-language:#0400;
        mso-fareast-language:#0400;
        mso-bidi-language:#0400;}
</style>
<![endif]--> </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>