[TRNSYS-users] Controller for PV panel

David BRADLEY d.bradley at tess-inc.com
Mon Jul 6 08:15:05 PDT 2015


Anas,
   There is not a specific Type that contains the features that you are 
looking for. However you can create the control that you describe by 
using a combination of simple thermostats (either Type2 in its 
"aquastat" mode or one of the aquastats in the TESS Controller's 
library) and equations. You will probably need to use some of the 
boolean (logical) functions such as GT(:,:) in your equations. 
Explanations of those functions can be found in section 6.3.9 of the 
06-TRNEdit manual in the ..\Trnsys17\Documentation\ folder.
kind regards,
  David


On 07/02/2015 21:25, Anas Majdouli wrote:
> Hi TRNsys community,
>
> I am working on a water heating simulation using a PV panel. I am 
> using for this power from PV panel to supply an electric heating 
> device within a hot water storage tank (type 534).
> The tank also contains an auxiliary heater placed on top (node 2) in 
> case the set point temperature (T° of Node 1) is not reached.
> I would like to put a controller between the PV panel,the tank and its 
> heating devices.
> *That's how I would like it to work :*
>
> First, I want the PV panel to supply power on daylight. Then during 
> the night, the controller should activate the auxiliary heater.
>
> Also, on daylight, if irradiance is not sufficient to reach the set 
> point temperature in a tank (T° of Node 1 observed by an aquastat), 
> the controller should activate the aux. heater.
>
> Finally, when the irradiance is high or when the set point temperature 
> is already reached on daylight, I want the controller to switch PV 
> panel power supply from supplying the electric heating device to 
> supplying a battery linked to the grid (Type 188a).
> In that case, the aux. heater should obviously be switched off.
>
> What Type(s) should I use for the controller ?
> What do you think of this 'scenario' ?
>
> Thanks in advance for your reply. I extremely need your help.
>
> p.s : please find a draft of the worksheet of my simulation attached 
> to this email
>
> Best Regards,
> Anas MAJDOULI
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150706/67e4d235/attachment-0003.htm>


More information about the TRNSYS-users mailing list