    Anas,<br>
      There is not a specific Type that contains the features that you
    are looking for. However you can create the control that you
    describe by using a combination of simple thermostats (either Type2
    in its "aquastat" mode or one of the aquastats in the TESS
    Controller's library) and equations. You will probably need to use
    some of the boolean (logical) functions such as GT(:,:) in your
    equations. Explanations of those functions can be found in section
    6.3.9 of the 06-TRNEdit manual in the ..\Trnsys17\Documentation\
    folder.<br>
    kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 07/02/2015 21:25, Anas Majdouli
      wrote:<br>
    </div>
    <blockquote cite="mid:DUB120-W21DD448A5FB6D879223E2CE5960@phx.gbl"
      type="cite">
      <style><!--
.hmmessage P
{
margin:0px;
padding:0px
}
body.hmmessage
{
font-size: 12pt;
font-family:Calibri
}
--></style>
      <div dir="ltr">Hi TRNsys community,<br>
        <br>
        I am working on a water heating simulation using a PV panel. I
        am using for this power from PV panel to supply an electric
        heating device within a hot water storage tank (type 534).<br>
        The tank also contains an auxiliary heater placed on top (node
        2) in case the set point temperature (T° of Node 1) is not
        reached.<br>
        I would like to put a controller between the PV panel,the tank
        and its heating devices.<br>
        <b>That's how I would like it to work :</b><br>
        <br>
        First, I want the PV panel to supply power on daylight. Then
        during the night, the controller should activate the auxiliary
        heater.<br>
        <br>
        Also, on daylight, if irradiance is not sufficient to reach the
        set point temperature in a tank (T° of Node 1 observed by an
        aquastat), the controller should activate the aux. heater.<br>
        <br>
        Finally, when the irradiance is high or when the set point
        temperature is already reached on daylight, I want the
        controller to switch PV panel power supply from supplying the
        electric heating device to supplying a battery linked to the
        grid (Type 188a).<br>
        In that case, the aux. heater should obviously be switched off.<br>
        <br>
        What Type(s) should I use for the controller ?<br>
        What do you think of this 'scenario' ?<br>
        <br>
        Thanks in advance for your reply. I extremely need your help.<br>
        <br>
        p.s : please find a draft of the worksheet of my simulation
        attached to this email<br>
        <br>
        Best Regards,<br>
        Anas MAJDOULI<br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>