[TRNSYS-users] HELP: In TRNSYS 17: How to connect a thermostat switch (Type 2b) to switch ON a pump at a particular temperature range else keep the pump OFF.
    Alastair McDowell 
    alastair.mcdowell at energyae.com
       
    Fri Dec 18 15:35:11 PST 2015
    
    
  
Veekay,
Have you read the documentation for the Type 2 differential controller? Page 13 in the Volume 4 Mathematical Reference pdf document (press F1 inside Simulation Studio). This document will help you greatly.
For your case, set the lower input temperature to 50C. Choose a suitable dead band to avoid excessive switching on and off of the pump. Start with T_H=0C, T_L=-2. and adjust if necessary after reviewing the output.
Alternatively, set the lower input temperature to 0C, and the upper deadband to 50C, and the lower dead band to 48C. This will switch the pump on when T_outlet>50C, and switch it off once T_outlet<48C, as above.
Kind regards,
Alastair McDowell
Engineering Consultant
Energy Analysis & Engineering – Enabling innovation for a sustainable future
T: +61 450 600 842
E: alastair.mcdowell at energyae.com<mailto:alastair.mcdowell at energyae.com>
608 Harris St Sydney NSW 2007 Australia | http://www.energyae.com<http://www.energyae.com/>
From: TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org] On Behalf Of Vinod
Sent: Saturday, 19 December 2015 1:33 a.m.
To: trnsys-users-request <trnsys-users-request at lists.onebuilding.org>; trnsys-users <trnsys-users at lists.onebuilding.org>
Subject: Re: [TRNSYS-users] HELP: In TRNSYS 17: How to connect a thermostat switch (Type 2b) to switch ON a pump at a particular temperature range else keep the pump OFF.
David Sir,
Thank you very much for your positive and prompt response. I need some more clarifications in this regard.
I've a collector whose hot water drain should be started only if outlet temperature is above 50 degree Celsius by switching ON the pump.
Kindly guide me on connections as per attached image.
Thanks a lot.
Regards
Veekay
India
From: David BRADLEY <d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>>
Sent: Thu, 17 Dec 2015 03:05:05
To: "TRNSYS users mailing list at OneBuilding.org" <trnsys-users at lists.onebuilding.org<mailto:trnsys-users at lists.onebuilding.org>>, vviinnoodd at rediffmail.com<mailto:vviinnoodd at rediffmail.com>
Subject: Re: [TRNSYS-users] HELP: In TRNSYS 17: How to connect a thermostat switch (Type 2b) to switch ON a pump at a particular temperature range else keep the pump OFF.
Veekay,
  There are two ways that Type2 can be used. Most commonly it is used as a differential controller such that it turns on when the difference between two temperatures exceeds a certain amount and then stays on until the difference between those temperatures falls to a different amount. You'd use this in a solar thermal system when you want to turn on the collector if the collector temperature exceeds the storage tank temperature by (for example) 10C no matter what the temperature of the storage tank. This was the method that Alastair correctly suggested.
  You can also use Type2 like a more traditional thermostat in which case you typically want to turn on a device when a monitored temperature exceeds (or falls below) a certain set point value. There are proformas for Type2 set up to do this. They are located in Controllers: Aquastat: Heating Mode and Controllers: Aquastat: Cooling Mode. Alternatively you can use Type108 which, while it allows for more than one stage of control, can also be used as a simple thermostat in either heating or cooling mode.
kind regards,
 David
On 12/16/2015 12:44, Vinod wrote:
20151216184430.5581.qmail at f4mail-235-223.rediffmail.com<mailto:20151216184430.5581.qmail at f4mail-235-223.rediffmail.com>" type="cite">Please help me in TRNSYS 17: How to connect a thermostat switch (Type 2b) to switch ON a pump at a particular temperature range else keep the pump OFF.
My purpose is to run the pump to discharge after achieving a particular temperature.
Thanks
Veekay
India
[https://sigads.rediff.com/RealMedia/ads/adstream_nx.ads/www.rediffmail.com/signatureline.htm@Middle%3e%3c/a%3e%20%20%20%20%20%20%3ctable%20cellpadding=]<https://sigads.rediff.com/RealMedia/ads/click_nx.ads/www.rediffmail.com/signatureline.htm@Middle?>
Get your own FREE website, FREE domain & FREE mobile app with Company email.  <https://sigads.rediff.com/RealMedia/ads/click_nx.ads/www.rediffmail.com/signatureline.htm@Middle?>
Know More ><//www.rediffmail.com/cgi-bin/red.cgi?red=http%3A%2F%2Ftrack%2Erediff%2Ecom%2Fclick%3Furl%3D%5F%5F%5Fhttp%3A%2F%2Fbusinessemail%2Erediff%2Ecom%3Fsc%5Fcid%3Dsign%2D1%2D10%2D13%5F%5F%5F%26amp%3Bcmp%3Dhost%26amp%3Blnk%3Dsign%2D1%2D10%2D13%26amp%3Bnsrv1%3Dhost&isImage=0&BlockImage=0&rediffng=0&rogue=387537254f7eee557c3b17544bd037e8098bd82e>
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org<mailto:TRNSYS-users at lists.onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.257<http://1.608.274.257>7
F:+1.608.278.147<http://1.608.278.147>5
d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>
http://www.tess-inc.com
http://www.trnsys.com
[https://sigads.rediff.com/RealMedia/ads/adstream_nx.ads/www.rediffmail.com/signatureline.htm@Middle]<https://sigads.rediff.com/RealMedia/ads/click_nx.ads/www.rediffmail.com/signatureline.htm@Middle?>
Get your own FREE website, FREE domain & FREE mobile app with Company email.
Know More ><http://track.rediff.com/click?url=___http://businessemail.rediff.com?sc_cid=sign-1-10-13___&cmp=host&lnk=sign-1-10-13&nsrv1=host>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20151218/afaf2552/attachment-0003.htm>
    
    
More information about the TRNSYS-users
mailing list