[TRNSYS-users] NASA weather data

David BRADLEY d.bradley at tess-inc.com
Tue Sep 9 09:07:23 PDT 2014


Safwan,
   Type54 can accommodate your wind speed data; check the Type54 
documentation in the 04-MathematicalReference manual for information on 
how to include it. As far as RH is concerned, you need to take the 
temperature and absolute humidity profiles that are generated by Type54 
and pass them to a Type33 (psychrometrics) routine in order to obtain 
RH. The solar angle of incidence is a function of sun-earth geometry and 
should be taken from Type16. Type16 will takes its input from Type54.
Regards,
  David


On 9/9/2014 09:34, safwan ahmed wrote:
> Dear All,
>
> I tried to use NASA weather data in Type 54b Weather generator. So, I 
> wrote a file for weather include: monthly average daily global 
> horizontal solar radiation,
>  monthly average humidity ratio and monthly average temperature (°C) 
> however, I want to include others data like wind speed, relative 
> humidity and angle of incidence for horizontal etc. How can I add that 
> Please?
>
> Safwan Kanan
> The Manchester of Manchester
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140909/8e29f954/attachment-0005.htm>


More information about the TRNSYS-users mailing list