Safwan,<br>
Type54 can accommodate your wind speed data; check the Type54
documentation in the 04-MathematicalReference manual for information
on how to include it. As far as RH is concerned, you need to take
the temperature and absolute humidity profiles that are generated by
Type54 and pass them to a Type33 (psychrometrics) routine in order
to obtain RH. The solar angle of incidence is a function of
sun-earth geometry and should be taken from Type16. Type16 will
takes its input from Type54.<br>
Regards,<br>
David<br>
<br>
<br>
<div class="moz-cite-prefix">On 9/9/2014 09:34, safwan ahmed wrote:<br>
</div>
<blockquote
cite="mid:1410273274.22785.YahooMailNeo@web160802.mail.bf1.yahoo.com"
type="cite">
<div style="color:#000; background-color:#fff;
font-family:HelveticaNeue-Light, Helvetica Neue Light, Helvetica
Neue, Helvetica, Arial, Lucida Grande,
sans-serif;font-size:10pt">
<div style="" class="">Dear All,</div>
<div style="" class=""><br style="" class="">
</div>
<div class="" style="color: rgb(0, 0, 0); font-size: 13.3333px;
font-family: HelveticaNeue-Light,Helvetica Neue
Light,Helvetica Neue,Helvetica,Arial,Lucida Grande,sans-serif;
background-color: transparent; font-style: normal;">I tried to
use NASA weather data in Type 54b Weather generator. So, I
wrote a file for weather include: monthly average daily global
horizontal solar radiation, <br style="" class="">
</div>
<div class="" style="color: rgb(0, 0, 0); font-size: 13.3333px;
font-family: HelveticaNeue-Light,Helvetica Neue
Light,Helvetica Neue,Helvetica,Arial,Lucida Grande,sans-serif;
background-color: transparent; font-style: normal;"> monthly
average humidity ratio and monthly average temperature (°C)
however, I want to include others data like wind speed,
relative humidity and angle of incidence for horizontal etc.
How can I add that Please?</div>
<div class="" style="color: rgb(0, 0, 0); font-size: 13.3333px;
font-family: HelveticaNeue-Light,Helvetica Neue
Light,Helvetica Neue,Helvetica,Arial,Lucida Grande,sans-serif;
background-color: transparent; font-style: normal;"><br
style="" class="">
</div>
<div class="" style="color: rgb(0, 0, 0); font-size: 13.3333px;
font-family: HelveticaNeue-Light,Helvetica Neue
Light,Helvetica Neue,Helvetica,Arial,Lucida Grande,sans-serif;
background-color: transparent; font-style: normal;">Safwan
Kanan</div>
<div class="" style="color: rgb(0, 0, 0); font-size: 13.3333px;
font-family: HelveticaNeue-Light,Helvetica Neue
Light,Helvetica Neue,Helvetica,Arial,Lucida Grande,sans-serif;
background-color: transparent; font-style: normal;">The
Manchester of Manchester<br>
</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>