Shahen,
   The Type56 QSENS output shows you the loads on each airnode of the 
building. Negative values of QSENS indicate heating loads while positive 
values indicate a cooling load. It is often less trouble to use the 
QHEAT (NTYPE30) and QCOOL (NTYPE31) outputs instead. These are simply 
the heating loads and cooling loads respectively.
Kind regards,
  David



On 3/5/2014 04:39, Shahen Fakhraldin wrote:
> Dear all,
>
> I am trying to select the heating and cooling system size, as well as 
> to get the load file that will be used later in another project, 
>  through simulation of a house.
> However, I have only sensible gain or latent gain in the type 56. So 
> how can I find the total gain or demand.
>
> Could you please advise me
> King regards,
> Shahen
> /
>
> /
>
>
> On Monday, March 3, 2014 10:05 PM, "trnsys-users-request at cae.wisc.edu" 
> <trnsys-users-request at cae.wisc.edu> wrote:
> ----- Forwarded Message -----
>
> Send TRNSYS-users mailing list submissions to
> trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
>
> To subscribe or unsubscribe via the World Wide Web, visit
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
> or, via email, send a message with subject or body 'help' to
> trnsys-users-request at cae.wisc.edu 
> <mailto:trnsys-users-request at cae.wisc.edu>
>
> You can reach the person managing the list at
> trnsys-users-owner at cae.wisc.edu <mailto:trnsys-users-owner at cae.wisc.edu>
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of TRNSYS-users digest..."
>
> Today's Topics:
>
>   1. Re: Heating/cooling energy consumption (David BRADLEY)
>   2. Re: Capacitance clarification in TYPE536 (David BRADLEY)
>   3. Re: Type 604 - end of time step (David BRADLEY)
> Igor,
>   Yes, you care correct on both counts. You can also ask Type56 to 
> give you QCOOL as an output if you want to know cooling loads. Keep in 
> mind that the loads are sensible only and that no latent loads are 
> calculated unless you have activated either humidification or 
> dehumidication in a zone.
> Kind regards,
>  David
>
>
> On 2/26/2014 07:22, Igor Seso wrote:
>> Dear all,
>>
>> I want to simulate/calculate the heat energy consumption of a 
>> building Type 56 (weekly,monthly).
>>
>> 1.Since as output from the TYPE 56 I get only the Qheat_zone(heat 
>> transfer rate-power) so will it be correct to use the quantity 
>> integrator type 24 and connect with Type 46?
>> 2. For the integration period if I put 24 hr does it mean that I get 
>> daily energy consumption? and with STOP I get for the whole 
>> simulation period?
>>
>> Thank you
>> Best Regards
>> Igor
>>
>
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140306/66072a36/attachment-0004.htm>


More information about the TRNSYS-users mailing list