Shahen,<br>
The Type56 QSENS output shows you the loads on each airnode of the
building. Negative values of QSENS indicate heating loads while
positive values indicate a cooling load. It is often less trouble to
use the QHEAT (NTYPE30) and QCOOL (NTYPE31) outputs instead. These
are simply the heating loads and cooling loads respectively.<br>
Kind regards,<br>
David<br>
<br>
<br>
<br>
<div class="moz-cite-prefix">On 3/5/2014 04:39, Shahen Fakhraldin
wrote:<br>
</div>
<blockquote
cite="mid:1394015999.10874.YahooMailNeo@web121202.mail.ne1.yahoo.com"
type="cite">
<div style="color:#000; background-color:#fff;
font-family:verdana, helvetica, sans-serif;font-size:14pt">
<div>Dear all,</div>
<div><br>
</div>
<div style="color: rgb(0, 0, 0); font-size: 19.09090805053711px;
font-family: verdana, helvetica, sans-serif; background-color:
transparent; font-style: normal;">I am trying to select the
heating and cooling system size, <span style="font-size:
14pt;">as well as to get the load file that will be used
later in another project, </span><span
style="background-color: transparent;"> through simulation
of a house.</span></div>
<div style="color: rgb(0, 0, 0); font-size: 19.09090805053711px;
font-family: verdana, helvetica, sans-serif; background-color:
transparent; font-style: normal;">However, I have only
sensible gain or latent gain in the type 56. So how can I find
the total gain or demand.</div>
<div style="color: rgb(0, 0, 0); font-size: 19.09090805053711px;
font-family: verdana, helvetica, sans-serif; background-color:
transparent; font-style: normal;"><br>
</div>
<div style="color: rgb(0, 0, 0); font-size: 19.09090805053711px;
font-family: verdana, helvetica, sans-serif; background-color:
transparent; font-style: normal;">Could you please advise me</div>
<div style="color: rgb(0, 0, 0); font-size: 19.09090805053711px;
font-family: verdana, helvetica, sans-serif; background-color:
transparent; font-style: normal;">King regards,</div>
<div style="color: rgb(0, 0, 0); font-size: 19.09090805053711px;
font-family: verdana, helvetica, sans-serif; background-color:
transparent; font-style: normal;">Shahen </div>
<div style="color: rgb(0, 0, 0); font-size: 19.09090805053711px;
font-family: verdana, helvetica, sans-serif; background-color:
transparent; font-style: normal;"> </div>
<div> </div>
<div><i><font color="#40a0ff" face="bookman old style, new york,
times, serif" size="4">
<div><br>
</div>
</font></i></div>
<div class="yahoo_quoted" style="display: block;"> <br>
<br>
<div style="font-family: verdana, helvetica, sans-serif;
font-size: 14pt;">
<div style="font-family: HelveticaNeue, 'Helvetica Neue',
Helvetica, Arial, 'Lucida Grande', sans-serif; font-size:
12pt;">
<div dir="ltr"> <font face="Arial" size="2"> On Monday,
March 3, 2014 10:05 PM,
<a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users-request@cae.wisc.edu">"trnsys-users-request@cae.wisc.edu"</a>
<a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users-request@cae.wisc.edu"><trnsys-users-request@cae.wisc.edu></a> wrote:<br>
</font> </div>
<div class="y_msg_container">----- Forwarded Message -----<br>
<br>
Send TRNSYS-users mailing list submissions to<br>
<a moz-do-not-send="true"
ymailto="mailto:trnsys-users@cae.wisc.edu"
href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
<br>
To subscribe or unsubscribe via the World Wide Web,
visit<br>
<a moz-do-not-send="true"
href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
or, via email, send a message with subject or body
'help' to<br>
<a moz-do-not-send="true"
ymailto="mailto:trnsys-users-request@cae.wisc.edu"
href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a><br>
<br>
You can reach the person managing the list at<br>
<a moz-do-not-send="true"
ymailto="mailto:trnsys-users-owner@cae.wisc.edu"
href="mailto:trnsys-users-owner@cae.wisc.edu">trnsys-users-owner@cae.wisc.edu</a><br>
<br>
When replying, please edit your Subject line so it is
more specific<br>
than "Re: Contents of TRNSYS-users digest..."<br>
<br>
Today's Topics:<br>
<br>
1. Re: Heating/cooling energy consumption (David
BRADLEY)<br>
2. Re: Capacitance clarification in TYPE536 (David
BRADLEY)<br>
3. Re: Type 604 - end of time step (David BRADLEY)<br>
<div id="yiv5103418372">
<div> Igor,<br>
Yes, you care correct on both counts. You can also
ask Type56 to give you QCOOL as an output if you
want to know cooling loads. Keep in mind that the
loads are sensible only and that no latent loads are
calculated unless you have activated either
humidification or dehumidication in a zone.<br>
Kind regards,<br>
David<br>
<br>
<br>
<div class="yiv5103418372moz-cite-prefix">On
2/26/2014 07:22, Igor Seso wrote:<br>
</div>
<blockquote type="cite">
<div style="color: rgb(0, 0, 0); background-color:
rgb(255, 255, 255); font-family: HelveticaNeue,
'Helvetica Neue', Helvetica, Arial, 'Lucida
Grande', sans-serif; font-size: 10pt;">
<div>Dear all,</div>
<div><br>
</div>
<div style="color:rgb(0, 0, 0);font-size:13px;
font-family:HelveticaNeue, 'Helvetica Neue',
Helvetica, Arial, 'Lucida Grande',
sans-serif;background-color:transparent;font-style:normal;">I
want to simulate/calculate the heat energy
consumption of a building Type 56
(weekly,monthly).</div>
<div style="color:rgb(0, 0, 0);font-size:13px;
font-family:HelveticaNeue, 'Helvetica Neue',
Helvetica, Arial, 'Lucida Grande',
sans-serif;background-color:transparent;font-style:normal;"><br>
</div>
<div style="color:rgb(0, 0, 0);font-size:13px;
font-family:HelveticaNeue, 'Helvetica Neue',
Helvetica, Arial, 'Lucida Grande',
sans-serif;background-color:transparent;font-style:normal;">1.Since
as output from the TYPE 56 I get only the
Qheat<span style="font-size:10pt;">_zone</span><span
style="font-size:10pt;"> </span><span
style="background-color:transparent;">(heat
transfer rate-power) so will it be correct
to use the quantity integrator type 24 and
connect with Type 46?</span></div>
<div style="color:rgb(0, 0, 0);font-size:13px;
font-family:HelveticaNeue, 'Helvetica Neue',
Helvetica, Arial, 'Lucida Grande',
sans-serif;background-color:transparent;font-style:normal;">2.
For the integration period if I put 24 hr does
it mean that I get daily energy consumption?
and with STOP I get for the whole simulation
period?</div>
<div style="color:rgb(0, 0, 0);font-size:13px;
font-family:HelveticaNeue, 'Helvetica Neue',
Helvetica, Arial, 'Lucida Grande',
sans-serif;background-color:transparent;font-style:normal;"><br>
</div>
<div style="color:rgb(0, 0, 0);font-size:13px;
font-family:HelveticaNeue, 'Helvetica Neue',
Helvetica, Arial, 'Lucida Grande',
sans-serif;background-color:transparent;font-style:normal;">Thank
you</div>
<div style="color:rgb(0, 0, 0);font-size:13px;
font-family:HelveticaNeue, 'Helvetica Neue',
Helvetica, Arial, 'Lucida Grande',
sans-serif;background-color:transparent;font-style:normal;">Best
Regards</div>
<div style="color:rgb(0, 0, 0);font-size:13px;
font-family:HelveticaNeue, 'Helvetica Neue',
Helvetica, Arial, 'Lucida Grande',
sans-serif;background-color:transparent;font-style:normal;">Igor </div>
</div>
<br>
<fieldset
class="yiv5103418372mimeAttachmentHeader"></fieldset>
</blockquote>
</div>
</div>
<div id="yiv5103418372">
<div><br>
</div>
</div>
<br>
<br>
</div>
</div>
</div>
</div>
<style><!--
#yiv5103418372
_filtered #yiv5103418372 {font-family:"Cambria Math";panose-1:2 4 5 3 5 4 6 3 2 4;}
_filtered #yiv5103418372 {font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2 4;}
_filtered #yiv5103418372 {font-family:"Trebuchet MS";panose-1:2 11 6 3 2 2 2 2 2 4;}
_filtered #yiv5103418372 {font-family:Webdings;panose-1:5 3 1 2 1 5 9 6 7 3;}
#yiv5103418372
#yiv5103418372 p.yiv5103418372MsoNormal, #yiv5103418372 li.yiv5103418372MsoNormal, #yiv5103418372 div.yiv5103418372MsoNormal
{margin:0cm;margin-bottom:.0001pt;font-size:11.0pt;font-family:"Calibri", "sans-serif";}
#yiv5103418372 a:link, #yiv5103418372 span.yiv5103418372MsoHyperlink
{color:#0563C1;text-decoration:underline;}
#yiv5103418372 a:visited, #yiv5103418372 span.yiv5103418372MsoHyperlinkFollowed
{color:#954F72;text-decoration:underline;}
#yiv5103418372 span.yiv5103418372EmailStyle17
{font-family:"Calibri", "sans-serif";color:windowtext;}
#yiv5103418372 .yiv5103418372MsoChpDefault
{font-family:"Calibri", "sans-serif";}
_filtered #yiv5103418372 {margin:72.0pt 72.0pt 72.0pt 72.0pt;}
#yiv5103418372 div.yiv5103418372WordSection1
{}
--></style></div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>