[TRNSYS-users] TRNSYS 17 (17.00.0025)-CONTAM coupled simulation problem on multi airnodes model of monozone building
David BRADLEY
d.bradley at tess-inc.com
Tue Jan 28 06:18:54 PST 2014
Remon,
You are correct that there is an error in 17.00.0025 that causes that
error to occur. The error is still present in the currently released
version (17.01.0028) but has been fixed in the next release. If you are
able to use 17.01.0019 for the time being, I would recommend that you do
so. If not, I can make you a TRNDLL for 17.01.0028 that has the fix you
need in it. Please let me know which you would prefer.
Kind regards,
David
On 1/28/2014 03:16, Remon Lapisa wrote:
> Hi,
>
> Ihave a problem TRNSYS 17 (version 17.00.0025)-Contam (version
> 3.0.1.1) coupled simulation to modelling multi-air nodes of monozone
> building (i.e 12 vertical stacked air nodes). Amessageis
> displayedonsimulation log (for type97) : 'the multizone air flow model
> did not converge in the maximum number iterations'
> However, ifI use the previous version of TRNSYS-17 (17.00.0019), the
> simulation is running properly. I have tried to check on source code
> file of Type-97; the latest version (TRNSYS-17.00.0025) uses
> 'Type97.f90' while other uses (Type97.for). What is different?
>
> What should I do to make this simulation running properly on version
> *17.00.0025*of TRNSYS 17?
>
>
> I am very happy if some one would like to share the information
>
> Thank you
>
> Remon
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140128/5152f5df/attachment-0001.htm>
More information about the TRNSYS-users
mailing list