[TRNSYS-users] Type 56 Wall Settings

Marion Hiller Hiller at Transsolar.com
Mon Feb 17 02:16:57 PST 2014


Qi Cheng,

the problem you described looks more like a ground coupling modelling.
Due to the total thickness of 3.5 m the heat transfer is two dimensional.
The transfer function approach isn't appropriate for this:
- It models 1-dimensional heat transfer only and
- the time base will be too large in relation to the other dynamic effects inside the building.

I would recommend using a ground coupling model like Type 49 or Types of the TESS libs.

Marion

________________________________

Von: trnsys-users-bounces at cae.wisc.edu [mailto:trnsys-users-bounces at cae.wisc.edu] Im Auftrag von Cheng Qi
Gesendet: Samstag, 15. Februar 2014 13:48
An: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] Type 56 Wall Settings

Dear Madam/Sir,

Sorry to disturb you.

I want to construct a wall in Type 56 which consists of 1m heavyweight concrete and 2.5m stone aggregate concrete. But in Type 56, the thickness of wall cannot be exceed 1m.

If possible, could you give me some suggestion.

Regards
Qi Cheng
Department of Building Service Engineering
Hong Kong Polytechnic University
Kowloon, Hong Kong

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140217/095458c9/attachment-0004.htm>


More information about the TRNSYS-users mailing list