[TRNSYS-users] Type 56 Wall Settings
hotline
hotline at Transsolar.com
Mon Feb 17 00:34:40 PST 2014
Dear Qi Cheng,
for thick walls you need to increase the time base, the wall transfer functions relates to this value.
(See 5.4.1.4. and 5.4.1.5. for further information). The value should be in the range of 0.5 for light walls and 3 for
very heavy walls.
Regards.
__________________________________________________________________________________________________
Jochen Lam
TRNSYS Software Team
Transsolar Energietechnik GmbH
Curiestraße 2
70563 Stuttgart
Fax: +49 711 67976-11
Email: jlam at transsolar.com<mailto:jlam at transsolar.com>
Web: www.trnsys.de<http://www.trnsys.de>
Von: trnsys-users-bounces at cae.wisc.edu [mailto:trnsys-users-bounces at cae.wisc.edu] Im Auftrag von Cheng Qi
Gesendet: Samstag, 15. Februar 2014 13:48
An: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] Type 56 Wall Settings
Dear Madam/Sir,
Sorry to disturb you.
I want to construct a wall in Type 56 which consists of 1m heavyweight concrete and 2.5m stone aggregate concrete. But in Type 56, the thickness of wall cannot be exceed 1m.
If possible, could you give me some suggestion.
Regards
Qi Cheng
Department of Building Service Engineering
Hong Kong Polytechnic University
Kowloon, Hong Kong
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140217/f5c935af/attachment-0004.htm>
More information about the TRNSYS-users
mailing list