[TRNSYS-users] The Front convective Heat Transfer Coefficient of Wall in TYPE 56
hotline
hotline at Transsolar.com
Thu Feb 6 01:04:05 PST 2014
Dear Yasmina EL HASNAOUI,
you may encounter this difference if you use the longwave radiation mode = standard.
In this case Trnsys uses the starnode approach to calculate the heat transfer of the front side
of a surface . (see 05-MultizoneBuilding.pdf Section 5.4.1.6). Thereby, the entered convective heat transfer coefficient
is used to calculated a so-called equivalent resistance to the starnode and an additional starnode resistance
from the starnode to the air. In order to save calculation time the calculation is performed based on an approx.
average surface temperature given under "properties" to the building. For NType 108 the effective coefficient is
calculated back from this combined equivalent coefficient with the current temperatures.
In general, this method yields to good results compared the detailed method although a difference in convective heat transfer coefficient
encountered. You may confirm this for your model by using the detailed longwave radiation mode based on the Gebhart method.
In the mode, the convective and radiative heat transfer are calculated independently and the entered convective heat transfer coefficient
is equivalent to Ntype 108.
Kind regards,
Marion Hiller
Transsolar Hotline Team
________________________________
Von: trnsys-users-bounces at cae.wisc.edu [mailto:trnsys-users-bounces at cae.wisc.edu] Im Auftrag von yasmina.el-hasnaoui at cofelyaxima-gdfsuez.com
Gesendet: Mittwoch, 5. Februar 2014 08:52
An: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] The Front convective Heat Transfer Coefficient of Wall in TYPE 56
Dear TRNSYS users,
Does anybody know what is the difference between the front convective Heat Transfer Coefficient that you enter in type 56 and the type 56's output called NType 108 : HCONVI ( eff.inside cinv. Heat transfer coeff (FRONT) ) ?
Kind regards,
Yasmina EL HASNAOUI
Ingénieure Calculs
Pôle Process Industriel
Semicad
[cid:image001.jpg at 01CD9B35.D07198D0]
123 avenue Barthélémy Buyer
69005 Lyon - France
Tel : +33 (0) 426 10 66 94
yasmina.el-hasnaoui at cofelyaxima-gdfsuez.com<mailto:yasmina.el-hasnaoui at cofelyaxima-gdfsuez.com>
Cofely Axima et OMEGA Concept, des marques de la société AXIMA Concept
www.omega-concept-gdfsuez.com
P Pensez à l'environnement avant d'imprimer ce message.
De : trnsys-users-bounces at cae.wisc.edu [mailto:trnsys-users-bounces at cae.wisc.edu] De la part de yasmina.el-hasnaoui at cofelyaxima-gdfsuez.com
Envoyé : Freed 24 jannewaris 2014 9:28
À : trnsys-users at cae.wisc.edu
Objet : [SUSPECTED IDENTITY THEFT] [TRNSYS-users] The Front convective Heat Transfer Coefficient of Wall in TYPE 56
Dear TRNSYS users,
Does anybody know what is the difference between the front convective Heat Transfer Coefficient that you enter in type 56 and the type 56's output called NType 108 : HCONVI ( eff.inside cinv. Heat transfer coeff (FRONT) ) ?
Kind regards,
Yasmina EL HASNAOUI
Ingénieure Calculs
Pôle Process Industriel
Semicad
[cid:image001.jpg at 01CD9B35.D07198D0]
123 avenue Barthélémy Buyer
69005 Lyon - France
Tel : +33 (0) 426 10 66 94
yasmina.el-hasnaoui at cofelyaxima-gdfsuez.com<mailto:yasmina.el-hasnaoui at cofelyaxima-gdfsuez.com>
Cofely Axima et OMEGA Concept, des marques de la société AXIMA Concept
www.omega-concept-gdfsuez.com
P Pensez à l'environnement avant d'imprimer ce message.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140206/5ea22bc4/attachment-0004.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 19321 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140206/5ea22bc4/attachment-0004.jpg>
More information about the TRNSYS-users
mailing list