[TRNSYS-users] The Front convective Heat Transfer Coefficient of Wall in TYPE 56
yasmina.el-hasnaoui at cofelyaxima-gdfsuez.com
yasmina.el-hasnaoui at cofelyaxima-gdfsuez.com
Tue Feb 4 23:51:40 PST 2014
Dear TRNSYS users,
Does anybody know what is the difference between the front convective Heat Transfer Coefficient that you enter in type 56 and the type 56's output called NType 108 : HCONVI ( eff.inside cinv. Heat transfer coeff (FRONT) ) ?
Kind regards,
Yasmina EL HASNAOUI
Ingénieure Calculs
Pôle Process Industriel
Semicad
[cid:image001.jpg at 01CF224F.7C675020]
123 avenue Barthélémy Buyer
69005 Lyon - France
Tel : +33 (0) 426 10 66 94
yasmina.el-hasnaoui at cofelyaxima-gdfsuez.com<mailto:yasmina.el-hasnaoui at cofelyaxima-gdfsuez.com>
Cofely Axima et OMEGA Concept, des marques de la société AXIMA Concept
www.omega-concept-gdfsuez.com
P Pensez à l'environnement avant d'imprimer ce message.
De : trnsys-users-bounces at cae.wisc.edu [mailto:trnsys-users-bounces at cae.wisc.edu] De la part de yasmina.el-hasnaoui at cofelyaxima-gdfsuez.com
Envoyé : Freed 24 jannewaris 2014 9:28
À : trnsys-users at cae.wisc.edu
Objet : [SUSPECTED IDENTITY THEFT] [TRNSYS-users] The Front convective Heat Transfer Coefficient of Wall in TYPE 56
Dear TRNSYS users,
Does anybody know what is the difference between the front convective Heat Transfer Coefficient that you enter in type 56 and the type 56's output called NType 108 : HCONVI ( eff.inside cinv. Heat transfer coeff (FRONT) ) ?
Kind regards,
Yasmina EL HASNAOUI
Ingénieure Calculs
Pôle Process Industriel
Semicad
[cid:image001.jpg at 01CF224F.7C675020]
123 avenue Barthélémy Buyer
69005 Lyon - France
Tel : +33 (0) 426 10 66 94
yasmina.el-hasnaoui at cofelyaxima-gdfsuez.com<mailto:yasmina.el-hasnaoui at cofelyaxima-gdfsuez.com>
Cofely Axima et OMEGA Concept, des marques de la société AXIMA Concept
www.omega-concept-gdfsuez.com
P Pensez à l'environnement avant d'imprimer ce message.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140205/0eeb337c/attachment-0004.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 19321 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140205/0eeb337c/attachment-0004.jpg>
More information about the TRNSYS-users
mailing list