Dear Marcello,
yes, the star-node model work has same limitations especially for extreme geometries and temperature deviations .
For those cases the star-node work shouldn't be applied because the results are wrong.
The "detailed" model is able to handle these extreme cases correctly.
For ordinary space shapes the star-rnode model does a good job as shown in several comparisons.
If you aren't sure if the star-node model performs well for your geometry/temperatures you can check the
results with the detailed model based on Gebhart factors.
Personally, I simulate 4 surfaces at least in a zone.
Marion
Dipl.-Ing. Marion Hiller
Transsolar Energietechnik GmbH
Curiestraße 2
70563 Stuttgart
Telefon: +49 711 67976-0
http://www.trnsys.de<http://www.trnsys.de/>
Transsolar: KlimaEngineering- Technologien für energieeffizientes Bauen und Nutzerkomfort in Gebäuden
Stuttgart - München - New York - Paris
Geschäftsführer :Diplom-Ingenieur Matthias Schuler, Diplom-Ingenieur Thomas Auer, Diplom-Physiker Stefan Holst, Diplom-Betriebswirt Dieter Schnelle
Eingetragen beim Amtsgericht Stuttgart HRB 23347,
Steuernummer: 99073/00911,USt-IdNr.: DE 152272639
________________________________
Von: trnsys-users-bounces at cae.wisc.edu [mailto:trnsys-users-bounces at cae.wisc.edu] Im Auftrag von marcello.caciolo at cofelyaxima-gdfsuez.com
Gesendet: Freitag, 21. Februar 2014 15:54
An: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] Long wave radiation heat exchange and number of surfaces
Dear TRNSYS users,
I have a very simple non-geometrical type 56 model with one zone with two surfaces: one boundary surface of 40 m2 and an external surface of 400 m2. External condition and boundary temperature are held constants.
When I plott surface temperatures and heat exchange between the two surfaces, I found a very large long wave radiation exchange between the two surfaces.
By hand calculation (Q=sigma S (T1^4 - T2^4), whit S = area of the little surface), I found that the value given of heat exchange by radiation by TRNSYS is about ten times larger than what I expected. Indeed, it seems that value given by TRNSYS is near to the value given by the same equation but considering the largest surface area.
However, if I split the external surface in two surfaces of half the area, the value calculated by TRNSYS is reduced of about 7 times. If I split again these surfaces, radiation exchange continue to drop but more slightly, tending to a value near the one calculated by hand.
My question is : have you already found the same behavior? Is there a recommendation to define at least three surfaces in a zone in order to calculate properly heat exchange by radiation?
Thank you for your help!
Best regards,
Marcello Caciolo
Responsable Outils et Méthodes d'Analyse Energétique
[cid:image003.jpg at 01CD4E08.954D04D0]
Cellule Efficacité Energétique et Environnementale - Pôle Projets et Réalisations
46 Boulevard de la Prairie au Duc
BP 40119 - 44201 Nantes Cedex 02
Tél.: +33 02 40 41 06 57
marcello.caciolo at cofelyaxima-gdfsuez.com<mailto:prenom.nom at aximaseitha-gdfsuez.com>
P Pensez à l'environnement avant d'imprimer ce message
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140226/2cd00c02/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 4267 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140226/2cd00c02/attachment-0001.jpg>
More information about the TRNSYS-users
mailing list