[TRNSYS-users] How to make a TRNBui for an apartment in storey 20th of a 30-storey building
David BRADLEY
d.bradley at tess-inc.com
Wed Feb 19 08:05:07 PST 2014
Huy Tung,
The typical method is to simply draw the one floor of the building
that you care about. You then set the ceiling of the zone to be of Type:
ceiling, Constuction: BND_CEILING, Outside Boundary Condition: Other
Side Coefficients, and Outside Boundary Object: BOUNDARY = IDENTICAL. Do
the same for the floor but in this case the type should be "floor" and
the construction should be "BND_FLOOR"
What this does is to force the conditions above and below your story
to be identical to those in your story. If the floors above and below
have significantly different conditioning requirements than does the
floor you are modeling you can choose a different boundary condition.
Kind regards,
David
On 2/18/2014 20:08, Tung Nguyen Huy wrote:
> Dear all,
>
> I need to simulate an apartment in storey 20th of a 30-storey
> building. I used Google Sketch up and created my apartment. However,
> I'm confused about other adjacent apartments.
>
> 1. Do I need to make adjacent zones for my apartment?
> 2. My apartment is at 57 meters high. It has 19 storeys below and 10
> storey above. Therefore, how can I emulate my apartment.
>
> Thank you so much for your kindness.
>
> Sincerely,
> Nguyen, Huy Tung
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140219/b842cc67/attachment-0001.htm>
More information about the TRNSYS-users
mailing list