Huy Tung,<br>
The typical method is to simply draw the one floor of the building
that you care about. You then set the ceiling of the zone to be of
Type: ceiling, Constuction: BND_CEILING, Outside Boundary
Condition: Other Side Coefficients, and Outside Boundary Object:
BOUNDARY = IDENTICAL. Do the same for the floor but in this case the
type should be "floor" and the construction should be "BND_FLOOR"<br>
<br>
What this does is to force the conditions above and below your
story to be identical to those in your story. If the floors above
and below have significantly different conditioning requirements
than does the floor you are modeling you can choose a different
boundary condition.<br>
Kind regards,<br>
David<br>
<br>
<br>
<div class="moz-cite-prefix">On 2/18/2014 20:08, Tung Nguyen Huy
wrote:<br>
</div>
<blockquote
cite="mid:CAHaW-e==fq9ENJbtci59hfzgSCGJOvz_p8+h3GZtatt6PjW0Hw@mail.gmail.com"
type="cite">
<div dir="ltr">Dear all,
<div><br>
</div>
<div>I need to simulate an apartment in storey 20th of a
30-storey building. I used Google Sketch up and created my
apartment. However, I'm confused about other adjacent
apartments.</div>
<div><br>
</div>
<div>1. Do I need to make adjacent zones for my apartment?</div>
<div>2. My apartment is at 57 meters high. It has 19 storeys
below and 10 storey above. Therefore, how can I emulate my
apartment.</div>
<div><br>
</div>
<div>Thank you so much for your kindness.</div>
<div><br>
</div>
<div>Sincerely,</div>
<div>Nguyen, Huy Tung</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>