[TRNSYS-users] Import and re-connect different radiation data in TRNSYS 17
David BRADLEY
d.bradley at tess-inc.com
Tue Dec 23 11:08:43 PST 2014
Giulia,
There are two things that you need to do.
1. In TRNBuild, you need to go to the "project" window and double click
on each of your ORIENTATIONS to make sure that each is set to
"calculation of radiation data: external by another component" Once you
have made the change, exit TRNBuild and when you are in the Studio,
right click on the Type56 proforma and select "update building variable
list." The Type56 INPUTs list should now include total radiation, beam
radiation, and angle of incidence of beam radiation for each ORIENTATION
in your building.
2. You need to use a Type16 in between your Type9 and your Type56 to
take the raw solar radiation data from Type9 and compute the beam,
total, and angle of incidence on all of the orientations in your
building. I would recommend that you look carefully at the example
located in:
..\Trnsys17\Examples\Reading Data Files\RadiationProcessing.tpf
Kind regards,
David
On 12/22/2014 09:13, Giulia Zanardi wrote:
> Hello everyone, I'd like to ask something about how to import a
> different set of RADIATION data (.prn) and re-connect the new imported
> values to the building in the same way the file was originally and
> automatically created (after the importation of a .idf file from the
> Trnsys3d plugin for Sketchup) in TRNSYS 17.
>
> I've already used this kind of procedure for temperature and relative
> humidity data, using a .prn input file and "Type 9b", but this
> specific case seems a little bit different and difficult for me to
> understand. I also know that a specific Type should exist in order to
> automatically separate and re-distribute the new imported values to
> the corresponding facedes and so on..
>
> Any sort of advice would be really appreciated,
> Thank you,
> Giulia
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141223/7c04a598/attachment-0003.htm>
More information about the TRNSYS-users
mailing list