[TRNSYS-users] (no subject)
David BRADLEY
d.bradley at tess-inc.com
Mon Apr 14 10:52:16 PDT 2014
Ali Javed,
It is preferable to create an external data file for Type107 that
corresponds with the actual absorption chiller that you are trying to
analyze. However, if you do not have any such performance data then the
sample data file associated with Type107 can be used. We did some work
many years ago to look at what the performance curves of various pieces
of HVAC equipment look like when you divide all of the performance
points by their value at the rated condition. Some equipment (such as
constant-speed compressor heat pumps) all start to look basically the
same when their performance is normalized. Some other equipment (notably
absorption chillers, which is why I am bothering you with this...) do
not look similar to one another when normalized. The take-away here is
that if at all possible, get performance data for the absorption chiller
manufacturer and model that you are planning to use.
Best,
David
On 4/14/2014 02:22, ali javed wrote:
> hello dear,
>
> I am using hot water fired absorption chiller type 107 for cooling of
> a building in Trnsys. I have made a model for my system but i don't
> understand the function of input file which is used in type 107
> (Examples\Data Files). is I have to change this file for my system or
> it remains same ????
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140414/1c4e7c1b/attachment-0004.htm>
More information about the TRNSYS-users
mailing list