[TRNSYS-users] Differential controller(Temperature controller)
David BRADLEY
d.bradley at tess-inc.com
Thu May 16 14:00:02 PDT 2013
Nipaporn,
If you want a heating controller (ie a controller that turns
equipment on when the room temperature falls below 26.5C and allows it
to stay on until room temperature reaches 27.5C) then set the first
input to the middle of your set point temperature range (27C). The
second input will be the temperature that you are monitoring (the room
temperature). The fifth input (upper dead band) would be set to 0.5C and
the sixth input (lower dead band) would be set to -0.5C.
If you want a cooling controller (ie a controller that turns
equipment on when the room temperature rises above 27.5C and allows it
to stay on until room temperature falls to 26.5C) then set the /second/
input to the middle of your set point temperature range (27C). The
/first /input will be the temperature that you are monitoring (the room
temperature). The fifth input (upper dead band) would be set to 0.5C and
the sixth input (lower dead band) would be set to -0.5C.
Kind regards,
David
On 5/14/2013 23:22, Nipaporn Nutprasert wrote:
> Hi TRNSYS users,
> I need some help about differential controller(Type2b). I would like
> to control temperature in the room within 26.5-27.5oC. How can I
> define the upper/lower deadbands (Upper input temperature Th, Lower
> input temperatureTl, Monitoring temperature Tin, Upper dead band dT,
> Lower dead band dT)to monitor the room temperature to gain simple
> ON/OFF control.
>
> Thank you in advance.
> Nipaporn
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130516/0a145544/attachment-0004.htm>
More information about the TRNSYS-users
mailing list