Rudai,
I think you are on the correct path; the "receiver" defined in Type34
should be for each divided part of the window. Keep in mind that Type34
is computing a modified amount of solar radiation falling per unit of
receiver area so it is okay for the area of the receiver and the area of
the actual window defined in TRNBuild/Type56 to be different.
One other caution about Type34; the model computes a diffuse sky view
factor and the amount of diffuse radiation falling on the receiver. In
its computation, it assumes an isotropic sky. In order to be most
correct, you should put your Type15 (or other weather data
reader/processor) into isotropic sky mode. I have found, however, that
the change between the isotropic and anisotropic sky models can have a
greater impact on the building energy use than do the shading features
themselves. Since the anisotropic sky models are much preferred over the
isotropic model, I tend to leave Type15 set in its Perez diffuse sky
mode and then pass both the shaded and unshaded diffuse radiation to an
online plotter and make sure that the calculated values make sense.
Best,
David
On 6/24/2013 23:35, Rudai Shan wrote:
> Dear All Trnsys users,
>
> I'm doing simulation for a window with grid shading. The height of the
> window is 1.2 m and the width of the window is 1.8 m. The grid shading
> divided the window into 8 parts, each part is 0.45 m width and 0.6 m
> height. The depth of the shading is 0.1 m. In type 56 I could only
> input the window area. In type 34 I can input the projection of the
> overhang and fin, both are 0.1 m. I think the receiver means the
> window area for each divided part in my case, so I input 0.45 m for
> the width and 0.6 m for the height. Could anybody tell me this is
> correct or wrong?
>
> Thank you for your time and attention.
>
> Best regards,
> Rudai Shan
>
> PhD student,
> TCAUP, University of Michigan
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130625/90d793d6/attachment-0001.htm>
More information about the TRNSYS-users
mailing list