<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body text="#000000" bgcolor="#FFFFFF">
    Rudai,<br>
      I think you are on the correct path; the "receiver" defined in
    Type34 should be for each divided part of the window. Keep in mind
    that Type34 is computing a modified amount of solar radiation
    falling per unit of receiver area so it is okay for the area of the
    receiver and the area of the actual window defined in
    TRNBuild/Type56 to be different.<br>
    <br>
      One other caution about Type34; the model computes a diffuse sky
    view factor and the amount of diffuse radiation falling on the
    receiver. In its computation, it assumes an isotropic sky. In order
    to be most correct, you should put your Type15 (or other weather
    data reader/processor) into isotropic sky mode. I have found,
    however, that the change between the isotropic and anisotropic sky
    models can have a greater impact on the building energy use than do
    the shading features themselves. Since the anisotropic sky models
    are much preferred over the isotropic model, I tend to leave Type15
    set in its Perez diffuse sky mode and then pass both the shaded and
    unshaded diffuse radiation to an online plotter and make sure that
    the calculated values make sense.<br>
    Best,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 6/24/2013 23:35, Rudai Shan wrote:<br>
    </div>
    <blockquote
cite="mid:CAJEm4tOQp__7t2nFYcqRAPoYgL6ssVK0gAVpzHPpj=An57cCnA@mail.gmail.com"
      type="cite">
      <div dir="ltr">Dear All Trnsys users,
        <div><br>
        </div>
        <div style="">I'm doing simulation for a window with grid
          shading. The height of the window is 1.2 m and the width of
          the window is 1.8 m. The grid shading divided the window into
          8 parts, each part is 0.45 m width and 0.6 m height. The depth
          of the shading is 0.1 m. In type 56 I could only input the
          window area. In type 34 I can input the projection of the
          overhang and fin, both are 0.1 m. I think the receiver means
          the window area for each divided part in my case, so I input
          0.45 m for the width and 0.6 m for the height. Could anybody
          tell me this is correct or wrong?</div>
        <div style=""><br>
        </div>
        <div style="">Thank you for your time and attention.</div>
        <div style=""><br>
        </div>
        <div style="">Best regards,</div>
        <div style="">Rudai Shan</div>
        <div style=""><br>
        </div>
        <div style="">PhD student,</div>
        <div style="">TCAUP, University of Michigan</div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>