When you say empty I am assuming you mean thermally "empty" and not 
starting from a dry tank.  Assuming you mean thermally empty, just set 
the values in the derivatives tab of the proforma of the tank to your 
desired startup condition.  If you meant dry start, then you'll have to 
use a different model - try Type 39.

Jeff

---
<p>Jeff Thornton</p>
<p><em>President - TESS LLC</em></p>
<p><em>22 N. Carroll Street, Madison WI USA 53703</em></p>
<p><em>Office: (608) 274-2577  Fax: (608) 278-1475</em></p>
<p><em>www.tess-inc.com</em></p>
<p><em>E-Mail: thornton at tess-inc.com</em></p>
<p> </p>

On 01/18/2013 2:44 pm, Michael Diekerhof wrote:
> Dear all,
>
> is there an opportunity to start with an empty tank !? The tank is
> always on a certain temperature if i start the simulation (e.g 50°C)
> and the heat pump that is connected to type 4 only starts working
> after a certain time period (Type 2Controllers). Is there a chance to
> simulate that i start with heating up the storage ?
>
> Best,
> Michael