[TRNSYS-users] Flow of water thru Type927 when it is off

Amdi Worm amdiworm at gmail.com
Tue Jan 8 02:00:26 PST 2013


HI.

Yes it is indeed possible. I have attached a screen dump of a system I have
made where the pump is running between the storagetank and the heatpump
(927) and is running constantly. My heatpump is controlled by the
temperature in the returning fluid from the tank to the heatpump ( as it is
done in many cases in real-life). The heat demand is simulated in another
program and imported by type 9a.

I dont know your system, but the convergens problems could be caused by
large timesteps compared to the inertia of your system ( often a buffertank
/ pipe system that is not capable of "consumeing" the energy produced i one
time step). My heatpump has a rated performance at 8kW ( 0/35 ) and a
buffer tank with a capacity of 200 liters + 20 meters of pipeing. I am
running my simulation at 0.5h pr timestep.

I hope this is a help for you.
Best regards.
Amdi Worm

Esbensen Consulting Engineers
Aarhus, Denmark


2013/1/8 Richard Thygesen <richard.thygesen at mdh.se>

> Hi.****
>
> ** **
>
> Is it possible to have  water flow thru type 927 when the heat pump is
> off? In real heat pumps the circulation pump is on constantly to provide
> heat to the heating system above an outdoor set point temperature for
> example 17°C (62.6 °F).****
>
> When I control the circulation pump to only be on during heat pump
> operation it works perfectly but when I set it to work constantly above a
> certain outdoor temperature I get convergence errors.****
>
> ** **
>
> Any suggestions on how to solve this?****
>
> ** **
>
> Best regards****
>
> *Richard Thygesen*
>
> ** **
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130108/6d751d92/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: TRnsys screendump.docx
Type: application/vnd.openxmlformats-officedocument.wordprocessingml.document
Size: 198090 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130108/6d751d92/attachment-0003.docx>


More information about the TRNSYS-users mailing list