HI.<div><br></div><div>Yes it is indeed possible. I have attached a screen dump of a system I have made where the pump is running between the storagetank and the heatpump (927) and is running constantly. My heatpump is controlled by the temperature in the returning fluid from the tank to the heatpump ( as it is done in many cases in real-life). The heat demand is simulated in another program and imported by type 9a. </div>
<div><br></div><div>I dont know your system, but the convergens problems could be caused by large timesteps compared to the inertia of your system ( often a buffertank / pipe system that is not capable of "consumeing" the energy produced i one time step). My heatpump has a rated performance at 8kW ( 0/35 ) and a buffer tank with a capacity of 200 liters + 20 meters of pipeing. I am running my simulation at 0.5h pr timestep.</div>
<div><br></div><div>I hope this is a help for you.</div><div>Best regards.</div><div>Amdi Worm</div><div><br></div><div>Esbensen Consulting Engineers</div><div>Aarhus, Denmark</div><div> </div><div><br><div class="gmail_quote">
2013/1/8 Richard Thygesen <span dir="ltr"><<a href="mailto:richard.thygesen@mdh.se" target="_blank">richard.thygesen@mdh.se</a>></span><br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div lang="SV" link="blue" vlink="purple"><div><p class="MsoNormal"><span lang="EN-US">Hi.<u></u><u></u></span></p><p class="MsoNormal"><span lang="EN-US"><u></u> <u></u></span></p><p class="MsoNormal"><span lang="EN-US">Is it possible to have water flow thru type 927 when the heat pump is off? In real heat pumps the circulation pump is on constantly to provide heat to the heating system above an outdoor set point temperature for example 17°C (62.6 °F).<u></u><u></u></span></p>
<p class="MsoNormal"><span lang="EN-US">When I control the circulation pump to only be on during heat pump operation it works perfectly but when I set it to work constantly above a certain outdoor temperature I get convergence errors.<u></u><u></u></span></p>
<p class="MsoNormal"><span lang="EN-US"><u></u> <u></u></span></p><p class="MsoNormal"><span lang="EN-US">Any suggestions on how to solve this?<u></u><u></u></span></p><p class="MsoNormal"><span lang="EN-US"><u></u> <u></u></span></p>
<p class="MsoNormal"><span lang="EN-US">Best regards<span class="HOEnZb"><font color="#888888"><u></u><u></u></font></span></span></p><span class="HOEnZb"><font color="#888888"><div><p class="MsoNormal"><b><span lang="EN-US" style="font-size:9.0pt;font-family:"Arial","sans-serif"">Richard Thygesen<u></u><u></u></span></b></p>
</div><p class="MsoNormal"><u></u> <u></u></p></font></span></div></div><br>_______________________________________________<br>
TRNSYS-users mailing list<br>
<a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
<br></blockquote></div><br></div>