Timothy,
Unfortunately, there is no water cooled chiller model in the standard
library. You will need to use Type42, which is a generic data
interpolater, and you will need to find manufacturer's catalog data file
and put the full and part load performance data from the catalog into
the Type42 data file format. The cooling tower model should be no
trouble; there is a cooling tower model in the standard library
(Type51). There are a few cooling coil models in the standard library
(Types32 and 52). I would recommend that you try and use Type52 even
though it is the more detailed of the two models. If you are able to
obtain the TESS HVAC Library, you will find both a water cooled chiller
and some other simplified cooling coil models that would make your task
a good bit easier.
Kind regards,
David
On 1/30/2013 01:29, Timothy Mulumba wrote:
> Hello,
> I'm new to trnsys and I'd appreciate any help with my project. I'd
> like to model a water cooled chiller that supplies chilled water to an
> AHU and FCU which in turn cool an indoor zone. A cooling tower is also
> used with the chiller. Which components in the standard library can I
> use for this? (Don't have access to TESS library). Thanks.
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130130/5a8f9f46/attachment-0001.htm>
More information about the TRNSYS-users
mailing list