    Timothy,<br>
      Unfortunately, there is no water cooled chiller model in the
    standard library. You will need to use Type42, which is a generic
    data interpolater, and you will need to find manufacturer's catalog
    data file and put the full and part load performance data from the
    catalog into the Type42 data file format. The cooling tower model
    should be no trouble; there is a cooling tower model in the standard
    library (Type51). There are a few cooling coil models in the
    standard library (Types32 and 52). I would recommend that you try
    and use Type52 even though it is the more detailed of the two
    models. If you are able to obtain the TESS HVAC Library, you will
    find both a water cooled chiller and some other simplified cooling
    coil models that would make your task a good bit easier.<br>
    Kind regards,<br>
     David <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 1/30/2013 01:29, Timothy Mulumba
      wrote:<br>
    </div>
    <blockquote
cite="mid:CAGbo1cuu9bzVytqH4yXZfT28Mu0vWb4vOzf1ZPC_MwDhzBPBkw@mail.gmail.com"
      type="cite">
      <div dir="ltr">Hello,<br>
        I'm new to trnsys and I'd appreciate any help with my project.
        I'd like to model a water cooled chiller that supplies chilled
        water to an AHU and FCU which in turn cool an indoor zone. A
        cooling tower is also used with the chiller. Which components in
        the standard library can I use for this? (Don't have access to
        TESS library). Thanks.<br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>