Enyuan,
The u-value (and g-value) shown in the upper right corner of the
TRNBuild window type manager are for display only; these values are
simply read out of the w-4 library. At the end of the file, you will
find some lines that look like the following:
11015 OPTWHITE15 15 5.5 0.87
0.852 0.075 0.90 1 15.00
12001 Pilkington,OPTITHERM,Coating#3 4/16/4 1.3 0.64
0.516 0.213 0.76 2 24.00
The u-value fields are shown in red, the g-value (SHGC) values are shown
in blue. You can write whatever numbers you want in those fields;
TRNBuild picks them up and displays them.
Kind regards,
David
On 2/22/2013 14:43, Enyuan Hu wrote:
> Dear all,
>
> Recently I used WINDOWS 6.3 to define a windows with desired
> properties. I manipulated the configuration so that the outcome u
> value is 1.88 which I wanted it to be. Following the window-defining
> tutorial, I was able to transport the information into TRNSYS
> by modifying the W4-lib file and Prgwin.lib file. However, when I
> selected it from the windows library, the shown value was 1.63. Can
> anyone provide some possible explanations? Thanks.
>
> cheers,
> Enyuan
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130225/22a16c50/attachment-0001.htm>
More information about the TRNSYS-users
mailing list