[TRNSYS-users] problem with iterations??
Marion Hiller
hiller at transsolar.com
Thu Sep 27 23:53:53 PDT 2012
Karol,
In general the notice has nothing to do with a frozen TRNEXE.exe,
it is just an information.
The message indicates that the internal controller for turning on the
integrated heating/cooling has convergence problems and a deadband is
applied to promote convergence.
This may be the case at the moment of turning ON or OFF something.
After 6 internal iterations a deadband is added to promote convergence.
If the convergence isn’t reached after 12 iterations a warning is
written to the lst/log file.
Regards,
Marion
Dipl.-Ing. Marion Hiller
TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes Bauen
und Nutzerkomfort in Gebäude
Munich - New York - Stuttgart + 49.711.67976.0
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart
Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.:
DE152272639
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher
_____
Von: Karol Bandurski [mailto:karol.bandurski at put.poznan.pl]
Gesendet: Donnerstag, 27. September 2012 10:47
An: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] problem with iterations??
Dear All,
I try to simulate dwelling with natural ventilation. I set some
algorithm for window opening and ideal heating for colder part of year
for each zone with set temperature depending on time of day.
When I run my yearly simulation it stop in one moment and TRNEXE is
frozen… There is even no error! Then I can only turn off TRNEXE.
Only think what appear (many times) in .lst file is
Notice: More than 6 iterations for internal regulation HEATING/COOLING.
I will be grateful for any advice!
I enclose .lst file.
Regards,
------------------------------------------------
Karol Bandurski MSc.
Institute of Environmental Engineering
Poznan University of Technology
www.ee.put.poznan.pl
www.put.poznan.pl
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120928/c379e30a/attachment-0001.htm>
More information about the TRNSYS-users
mailing list