[TRNSYS-users] Heat Pump mass flow rates (e.g. Type 401)
Michael Diekerhof
Michael.diekerhof at web.de
Tue Oct 23 00:06:57 PDT 2012
David,
I exactly followed the tutorial. Thanks for that. But unfortunetaly I
can´t see a controlled roomtemperature!! Also in the already existing
*example "HVAC-Building"* that is using Type108, I cant see a controlled
roomtemperature (20°C). Where´s the mistake since i haven´t changed
anything in the example? When I was plotting the the Indoor temperature
TaBack, I was expecting a almost constant temperature but not a
temperature fluctuating between -8 and 8°C.
Best,
Michael
Am 22.10.2012 23:15, schrieb David BRADLEY:
> Michael,
> well fundamentally, a furnace heats air and I think the heat pump
> you were talking about heats water that then goes to a radiator,
> correct? If so, then the furnace would be connected to Type56 by means
> of a VENTILATION type in TRNBuild/Type56.
> Best,
> David
>
>
>
> On 10/22/2012 10:09, Michael Diekerhof wrote:
>> David,
>> thanks a lot. I´ll try to figure that out. Just a short question
>> before starting: In case I dont use a storage, the type 121a
>> (Furnace) will be replaced with my heat pump type, right ?? If I use
>> a storage tank, this one will replace my type121, won´t it ?
>> Michael
>>
>>
>> Am 22.10.2012 16:53, schrieb David BRADLEY:
>>> Michael,
>>> The HEATING and COOLING types that are built into TRNBuild and
>>> Type56 are primarily used for computing the idealized heating and
>>> cooling loads of the space. Those loads can then be imposed on a
>>> system but the performance of the system is then dependent only on
>>> that load, not on the delivery temperature or the room temperature.
>>> This method of calculating system energy use is called Energy Rate
>>> Control. What you are aiming for in your simulation is something
>>> called Temperature Level Control where a themostat senses room
>>> temperatures and sends control signals to equipment. The equipment
>>> provides flows of hot or cold water and air to the delivery devices
>>> and the room temperatures react accordingly. The Type56 model is
>>> computing an energy balance on the space that reacts to the delivery
>>> devices. You need to get away from using the built-in idealized
>>> HEATING inputs and towards defining the ventilation streams, active
>>> layers, and energy gains that will cause the space temperature to go
>>> up or down. There is a tutorial available that will step you through
>>> the basic process of migrating from Energy Rate Control to
>>> Temperature Level Control. Even though it does not directly apply to
>>> your radiator system, I think it will help your understanding of the
>>> underlying concepts.
>>>
>>> http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tlc_tutorial17.pdf
>>>
>>> Best,
>>> David
>>>
>>>
>>>
>>> On 10/20/2012 08:43, Michael Diekerhof wrote:
>>>> David,
>>>> Unfortunetaly I don´t have access to the TESS library. I´m sorry
>>>> but I dont understand what you were meaning with: /"If you do not,
>>>> then I would imagine that you might be able to come up with a
>>>> simplified set of equations that would give you the gains to the
>>>> space that you need. "/
>>>>
>>>> Do you mean that I use the GAINS to adjust the radiative and
>>>> convective part ? But how to take the room temperature into account
>>>> by also considering the outlet temperature out of my storage ??
>>>> Isn´t there also a way to work with HEATING INPUTS ?! I still dont
>>>> have an idea how to cover my heat demand by using the outlet
>>>> temperature :(
>>>>
>>>> Best,
>>>> Michael
>>>>
>>>>
>>>>
>>>>
>>>> Am 19.10.2012 20:15, schrieb David BRADLEY:
>>>>> Michael,
>>>>> Ideally, you need a radiator model that will deal with the water
>>>>> side, take room temperature from Type56 and output the convective
>>>>> and radiative gains to the space as outputs. Such a model exists
>>>>> in the TESS HVAC library for Trnsys17 if you have access to it
>>>>> (Type1231). If you do not, then I would imagine that you might be
>>>>> able to come up with a simplified set of equations that would give
>>>>> you the gains to the space that you need.
>>>>> Best,
>>>>> David
>>>>>
>>>>>
>>>>> On 10/18/2012 09:24, Michael Diekerhof wrote:
>>>>>> David,
>>>>>>
>>>>>> thanks a lot. I´ll have a look.
>>>>>>
>>>>>> Could you please help me in another case. My plan is to connect
>>>>>> the HP to a storage tank and then giving a temperature from the
>>>>>> storage (type4) to my type56... How can I realize that my type 56
>>>>>> can be heated to achieve a constant room temperature of e.g. 20°C ?!
>>>>>>
>>>>>> Someone told me that I must use HEATING and then INPUT... but
>>>>>> what if i would like to simulate a simple radiator with a simple
>>>>>> inlet temperature of e.g. 55°C.
>>>>>>
>>>>>> Do you understand my problem? I dont know how to cover my heat
>>>>>> demand out of the storage.
>>>>>>
>>>>>> Thanks in advance
>>>>>>
>>>>>> Best,
>>>>>> Michael
>>>>>>
>>>>>>
>>>>>>
>>>>>> Am 18.10.2012 16:16, schrieb David BRADLEY:
>>>>>>> Michael,
>>>>>>> I would recommend that you look online at manufacturer's sites
>>>>>>> for similarly sized heat pumps. Trane and Carrier both have
>>>>>>> significant amounts of performance data in the product
>>>>>>> literature parts of their sites. You can probably get a good
>>>>>>> estimate of the flow rates on both the condenser and evaporator
>>>>>>> sizes from them.
>>>>>>> Best,
>>>>>>> david
>>>>>>>
>>>>>>>
>>>>>>> On 10/18/2012 03:53, Michael Diekerhof wrote:
>>>>>>>> Dear all,
>>>>>>>>
>>>>>>>> I´m working with the heat pump non-standard type 401 and try to
>>>>>>>> display an air-source heat pump.
>>>>>>>>
>>>>>>>> I dont have typical values for the Input 2 (evaporator mass
>>>>>>>> flowrate) and Input 4 (condenser mass flowrate).
>>>>>>>> The only real connection I´m using is the dry bulb temp, coming
>>>>>>>> from type 15, as the evaporator inlet temperature. For the
>>>>>>>> massflowrates I would like to assume constant values.
>>>>>>>>
>>>>>>>> How can I adjust an outlet condenser temperature of e.g. 55°C.
>>>>>>>> Just about the massflowrates ?!
>>>>>>>>
>>>>>>>> Does anyone have experience with heat pump mass flow rates?! I
>>>>>>>> guess it´s not necessary to have expieriences with Type 401.
>>>>>>>>
>>>>>>>> I´m thankful for any advices.
>>>>>>>>
>>>>>>>> Best,
>>>>>>>>
>>>>>>>> Michael
>>>>>>>> _______________________________________________
>>>>>>>> TRNSYS-users mailing list
>>>>>>>> TRNSYS-users at cae.wisc.edu
>>>>>>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>> Am 18.10.2012 16:16, schrieb David BRADLEY:
>>>>>>> Michael,
>>>>>>> I would recommend that you look online at manufacturer's sites
>>>>>>> for similarly sized heat pumps. Trane and Carrier both have
>>>>>>> significant amounts of performance data in the product
>>>>>>> literature parts of their sites. You can probably get a good
>>>>>>> estimate of the flow rates on both the condenser and evaporator
>>>>>>> sizes from them.
>>>>>>> Best,
>>>>>>> david
>>>>>>>
>>>>>>>
>>>>>>> On 10/18/2012 03:53, Michael Diekerhof wrote:
>>>>>>>> Dear all,
>>>>>>>>
>>>>>>>> I´m working with the heat pump non-standard type 401 and try to
>>>>>>>> display an air-source heat pump.
>>>>>>>>
>>>>>>>> I dont have typical values for the Input 2 (evaporator mass
>>>>>>>> flowrate) and Input 4 (condenser mass flowrate).
>>>>>>>> The only real connection I´m using is the dry bulb temp, coming
>>>>>>>> from type 15, as the evaporator inlet temperature. For the
>>>>>>>> massflowrates I would like to assume constant values.
>>>>>>>>
>>>>>>>> How can I adjust an outlet condenser temperature of e.g. 55°C.
>>>>>>>> Just about the massflowrates ?!
>>>>>>>>
>>>>>>>> Does anyone have experience with heat pump mass flow rates?! I
>>>>>>>> guess it´s not necessary to have expieriences with Type 401.
>>>>>>>>
>>>>>>>> I´m thankful for any advices.
>>>>>>>>
>>>>>>>> Best,
>>>>>>>>
>>>>>>>> Michael
>>>>>>>> _______________________________________________
>>>>>>>> TRNSYS-users mailing list
>>>>>>>> TRNSYS-users at cae.wisc.edu
>>>>>>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>>>>
>>>>>>
>>>>>>
>>>>>
>>>>
>>>
>>> --
>>> ***************************
>>> David BRADLEY
>>> Principal
>>> Thermal Energy Systems Specialists, LLC
>>> 22 North Carroll Street - suite 370
>>> Madison, WI 53703 USA
>>>
>>> P:+1.608.274.2577
>>> F:+1.608.278.1475
>>> d.bradley at tess-inc.com
>>>
>>> http://www.tess-inc.com
>>> http://www.trnsys.com
>>
>
> --
> ***************************
> David BRADLEY
> Principal
> Thermal Energy Systems Specialists, LLC
> 22 North Carroll Street - suite 370
> Madison, WI 53703 USA
>
> P:+1.608.274.2577
> F:+1.608.278.1475
> d.bradley at tess-inc.com
>
> http://www.tess-inc.com
> http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20121023/c86e9b78/attachment-0005.htm>
More information about the TRNSYS-users
mailing list