    <div class="moz-cite-prefix">David,<br>
      I exactly followed the tutorial. Thanks for that. But
      unfortunetaly I can´t see a controlled roomtemperature!! Also in
      the already existing <b>example "HVAC-Building"</b> that is using
      Type108, I cant see a controlled roomtemperature (20°C). Where´s
      the mistake since i haven´t changed anything in the example? When
      I was plotting the the Indoor temperature TaBack, I was expecting
      a almost constant temperature but not a temperature fluctuating
      between -8 and 8°C. <br>
      Best,<br>
      Michael <br>
      <br>
      <br>
      <br>
      <br>
      <br>
      Am 22.10.2012 23:15, schrieb David BRADLEY:<br>
    </div>
    <blockquote cite="mid:5085B77D.1090809@tess-inc.com" type="cite">
      <meta content="text/html; charset=UTF-8" http-equiv="Content-Type">
      Michael,<br>
        well fundamentally, a furnace heats air and I think the heat
      pump you were talking about heats water that then goes to a
      radiator, correct? If so, then the furnace would be connected to
      Type56 by means of a VENTILATION type in TRNBuild/Type56.<br>
      Best,<br>
       David<br>
      <br>
      <br>
      <br>
      <div class="moz-cite-prefix">On 10/22/2012 10:09, Michael
        Diekerhof wrote:<br>
      </div>
      <blockquote cite="mid:508561BC.6090506@web.de" type="cite">
        <meta content="text/html; charset=UTF-8"
          http-equiv="Content-Type">
        <div class="moz-cite-prefix">David,<br>
          thanks a lot. I´ll try to figure that out. Just a short
          question before starting: In case I dont use a storage, the
          type 121a (Furnace) will be replaced with my heat pump type,
          right ?? If I use a storage tank, this one  will replace my
          type121, won´t it ? <br>
          Michael <br>
          <br>
          <br>
          Am 22.10.2012 16:53, schrieb David BRADLEY:<br>
        </div>
        <blockquote cite="mid:50855DE7.7030403@tess-inc.com" type="cite">
          <meta content="text/html; charset=UTF-8"
            http-equiv="Content-Type">
          Michael,<br>
            The HEATING and COOLING types that are built into TRNBuild
          and Type56 are primarily used for computing the idealized
          heating and cooling loads of the space. Those loads can then
          be imposed on a system but the performance of the system is
          then dependent only on that load, not on the delivery
          temperature or the room temperature. This method of
          calculating system energy use is called Energy Rate Control.
          What you are aiming for in your simulation is something called
          Temperature Level Control where a themostat senses room
          temperatures and sends control signals to equipment. The
          equipment provides flows of hot or cold water and air to the
          delivery devices and the room temperatures react accordingly.
          The Type56 model is computing an energy balance on the space
          that reacts to the delivery devices. You need to get away from
          using the built-in idealized HEATING inputs and towards
          defining the ventilation streams, active layers, and energy
          gains that will cause the space temperature to go up or down.
          There is a tutorial available that will step you through the
          basic process of migrating from Energy Rate Control to
          Temperature Level Control. Even though it does not directly
          apply to your radiator system, I think it will help your
          understanding of the underlying concepts.<br>
          <br>
          <a moz-do-not-send="true" class="moz-txt-link-freetext"
href="http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tlc_tutorial17.pdf">http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tlc_tutorial17.pdf</a><br>
          <br>
          Best,<br>
           David<br>
          <br>
          <br>
          <br>
          <div class="moz-cite-prefix">On 10/20/2012 08:43, Michael
            Diekerhof wrote:<br>
          </div>
          <blockquote cite="mid:5082AA97.5080803@web.de" type="cite">
            <meta content="text/html; charset=UTF-8"
              http-equiv="Content-Type">
            <div class="moz-cite-prefix">David,<br>
              Unfortunetaly I don´t have access to the TESS library. I´m
              sorry but I dont understand what you were meaning with: <i>"If


                you do not, then I would imagine that you might be able
                to come up with a simplified set of equations that would
                give you the gains to the space that you need. "</i><br>
              <br>
              Do you mean that I use the GAINS to adjust the radiative
              and convective part ? But how to take the room temperature
              into account by also considering the outlet temperature
              out of my storage ?? Isn´t there also a way to work with
              HEATING INPUTS ?! I still dont have an idea how to cover
              my heat demand by using the outlet temperature :( <br>
              <br>
              Best,<br>
              Michael<br>
              <br>
              <br>
              <br>
              <br>
              Am 19.10.2012 20:15, schrieb David BRADLEY:<br>
            </div>
            <blockquote cite="mid:508198CE.2070803@tess-inc.com"
              type="cite">Michael, <br>
                Ideally, you need a radiator model that will deal with
              the water side, take room temperature from Type56 and
              output the convective and radiative gains to the space as
              outputs. Such a model exists in the TESS HVAC library for
              Trnsys17 if you have access to it (Type1231). If you do
              not, then I would imagine that you might be able to come
              up with a simplified set of equations that would give you
              the gains to the space that you need. <br>
              Best, <br>
               David <br>
              <br>
              <br>
              On 10/18/2012 09:24, Michael Diekerhof wrote: <br>
              <blockquote type="cite">David, <br>
                <br>
                thanks a lot. I´ll have a look. <br>
                <br>
                Could you please help me in another case. My plan is to
                connect the HP to a storage tank and then giving a
                temperature from the storage (type4) to my type56... How
                can I realize that my type 56 can be heated to achieve a
                constant room temperature of e.g. 20°C ?! <br>
                <br>
                Someone told me that I must use HEATING and then
                INPUT...  but what if i would like to simulate a simple
                radiator with a simple inlet temperature of e.g. 55°C. <br>
                <br>
                Do you understand my problem? I dont know how to cover
                my heat demand out of the storage. <br>
                <br>
                Thanks in advance <br>
                <br>
                Best, <br>
                Michael <br>
                <br>
                <br>
                <br>
                Am 18.10.2012 16:16, schrieb David BRADLEY: <br>
                <blockquote type="cite">Michael, <br>
                    I would recommend that you look online at
                  manufacturer's sites for similarly sized heat pumps.
                  Trane and Carrier both have significant amounts of
                  performance data in the product literature parts of
                  their sites. You can probably get a good estimate of
                  the flow rates on both the condenser and evaporator
                  sizes from them. <br>
                  Best, <br>
                   david <br>
                  <br>
                  <br>
                  On 10/18/2012 03:53, Michael Diekerhof wrote: <br>
                  <blockquote type="cite">Dear all, <br>
                    <br>
                    I´m working with the heat pump non-standard type 401
                    and try to display an air-source heat pump. <br>
                    <br>
                    I dont have typical values for the Input 2
                    (evaporator mass flowrate) and Input 4 (condenser
                    mass flowrate). <br>
                    The only real connection I´m using is the dry bulb
                    temp, coming from type 15, as the evaporator inlet
                    temperature. For the massflowrates I would like to
                    assume constant values. <br>
                    <br>
                    How can I adjust an outlet condenser temperature of
                    e.g. 55°C. Just about the massflowrates ?! <br>
                    <br>
                    Does anyone have experience with heat pump mass flow
                    rates?! I guess it´s not necessary to have
                    expieriences with Type 401. <br>
                    <br>
                    I´m thankful for any advices. <br>
                    <br>
                    Best, <br>
                    <br>
                    Michael <br>
                    _______________________________________________ <br>
                    TRNSYS-users mailing list <br>
                    <a moz-do-not-send="true"
                      class="moz-txt-link-abbreviated"
                      href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
                    <br>
                    <a moz-do-not-send="true"
                      class="moz-txt-link-freetext"
                      href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
                    <br>
                  </blockquote>
                  <br>
                </blockquote>
                <br>
                <br>
                <br>
                <br>
                Am 18.10.2012 16:16, schrieb David BRADLEY: <br>
                <blockquote type="cite">Michael, <br>
                    I would recommend that you look online at
                  manufacturer's sites for similarly sized heat pumps.
                  Trane and Carrier both have significant amounts of
                  performance data in the product literature parts of
                  their sites. You can probably get a good estimate of
                  the flow rates on both the condenser and evaporator
                  sizes from them. <br>
                  Best, <br>
                   david <br>
                  <br>
                  <br>
                  On 10/18/2012 03:53, Michael Diekerhof wrote: <br>
                  <blockquote type="cite">Dear all, <br>
                    <br>
                    I´m working with the heat pump non-standard type 401
                    and try to display an air-source heat pump. <br>
                    <br>
                    I dont have typical values for the Input 2
                    (evaporator mass flowrate) and Input 4 (condenser
                    mass flowrate). <br>
                    The only real connection I´m using is the dry bulb
                    temp, coming from type 15, as the evaporator inlet
                    temperature. For the massflowrates I would like to
                    assume constant values. <br>
                    <br>
                    How can I adjust an outlet condenser temperature of
                    e.g. 55°C. Just about the massflowrates ?! <br>
                    <br>
                    Does anyone have experience with heat pump mass flow
                    rates?! I guess it´s not necessary to have
                    expieriences with Type 401. <br>
                    <br>
                    I´m thankful for any advices. <br>
                    <br>
                    Best, <br>
                    <br>
                    Michael <br>
                    _______________________________________________ <br>
                    TRNSYS-users mailing list <br>
                    <a moz-do-not-send="true"
                      class="moz-txt-link-abbreviated"
                      href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
                    <br>
                    <a moz-do-not-send="true"
                      class="moz-txt-link-freetext"
                      href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
                    <br>
                  </blockquote>
                  <br>
                </blockquote>
                <br>
                <br>
              </blockquote>
              <br>
            </blockquote>
            <br>
          </blockquote>
          <br>
          <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
        </blockquote>
        <br>
      </blockquote>
      <br>
      <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>