[TRNSYS-users] Heat Recovery ventilation system

王洋 wanghongyang1767 at gmail.com
Thu Oct 11 03:20:29 PDT 2012


Dear all,

I trying to simulate a Ventilation Heat
Recovery system with TRNSYS, and i'm wondering if any one has
tried it or knows any documentation that talk about it.

My project is a large building with heat recovery ventilation
system.
1)Could anyone tell me an easy way (using Equation or which
component/Type? in Simulation Studio) to express the exhaust air/fresh
air heat recovery/exchange system?
2)How to show Ventilation Heat Recovery system is
more energy-saving than without Ventilation Heat Recovery system?
E.g. Through what parameters or simulation results etc.?

Many thanks in advance!
Br.

wang



2012/10/10 <trnsys-users-request at cae.wisc.edu>

> Send TRNSYS-users mailing list submissions to
>         trnsys-users at cae.wisc.edu
>
> To subscribe or unsubscribe via the World Wide Web, visit
>         https://mailman.cae.wisc.edu/listinfo/trnsys-users
> or, via email, send a message with subject or body 'help' to
>         trnsys-users-request at cae.wisc.edu
>
> You can reach the person managing the list at
>         trnsys-users-owner at cae.wisc.edu
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of TRNSYS-users digest..."
>
> Today's Topics:
>
>    1. Modifying connection line properties ? (Santeri Siren)
>    2. Re: Modifying connection line properties ? (Angel Carrera)
>    3. Re: Fwd: Converging error (??)
>
>
> ---------- 已转发邮件 ----------
> From: Santeri Siren <santeri.siren1 at gmail.com>
> To: "trnsys käyttäjät" <trnsys-users at cae.wisc.edu>
> Cc:
> Date: Wed, 10 Oct 2012 12:46:29 +0300
> Subject: [TRNSYS-users] Modifying connection line properties ?
> Dear users,
>
> is there a way to modify the properties (e.g. change color or weight) of
> multiple connection lines between components at the same time. It takes a
> lot of time to change line properties one at a time.
>
> best regards,
>
> Santeri Siren
>
>
> ---------- 已转发邮件 ----------
> From: Angel Carrera <angel.carrera at aiguasol.coop>
> To: Santeri Siren <santeri.siren1 at gmail.com>
> Cc: "trnsys käyttäjät" <trnsys-users at cae.wisc.edu>
> Date: Wed, 10 Oct 2012 12:08:48 +0200
> Subject: Re: [TRNSYS-users] Modifying connection line properties ?
>
> Dear Santeri,
>
> right-click on a connection with the style you wish to copy and choose and
> choose "copy style". Them, you can copy this to another line just
> right-clicking on it and selecting "apply style"
>
> Angel
>
> 2012/10/10 Santeri Siren <santeri.siren1 at gmail.com>
>
>> Dear users,
>>
>> is there a way to modify the properties (e.g. change color or weight) of
>> multiple connection lines between components at the same time. It takes a
>> lot of time to change line properties one at a time.
>>
>> best regards,
>>
>> Santeri Siren
>>
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at cae.wisc.edu
>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>
>>
>
>
> --
> *Àngel Carrera*
>
> *Consultor Senior
> Àrea tècnica*
>
> Sistemes Avançats d'Energia Solar Tèrmica SCCL
> C/ Roger de Llúria, 29 3r 2a 08009 Barcelona
> Mòbil: (+34) 663 27 66 80
> Tel: (+34) 93 342 47 55 Ext:2015
> Fax: (+34) 93 342 47 56
>
> angel.carrera at aiguasol.coop
> http://www.aiguasol.coop
>
>
> ---------- 已转发邮件 ----------
> From: 王洋 <wanghongyang1767 at gmail.com>
> To: hotline <hotline at transsolar.com>
> Cc: trnsys-users <trnsys-users at cae.wisc.edu>
> Date: Wed, 10 Oct 2012 13:37:23 +0200
> Subject: Re: [TRNSYS-users] Fwd: Converging error
> Dear Marion,
>
> Many thanks for your patient reply!
>
> 1) I use TRNSYS 16, there is no TSGRD in TYPE 56.
> 2) The height over sea level of Default is 0 m I used.
> 3) You are right. I tried to use *.tm2 weather data, this Error
> disappeared! But my Userdefined weather data is TRN/TRY weather data. Why
> does it result in aforementioned Errors (Converging error by my past
> emails)?
> If I must use our own TRN/TRY weather data, how to avoid this Converging
> error?
> 4) Yes, The data reader Type 9 is placed after the building now for my
> simulation., Do you mean Type 9 should be placed before the Building Type
> 56? Is Better?
>
> Many thanks in advance!
>
> Br.
>
> wang
>
> 2012/10/10 hotline <hotline at transsolar.com>
>
>> ** ** ** ** **
>>
>> Dear Wang,****
>>
>> ** **
>>
>> there are several issues within your simulation concerning the outside
>> longwave exchange of external surfaces****
>>
>> ** **
>>
>> **1.)     **You didn’t connect TSGRD such that it is set 0 =>  If you
>> have no information set it Tamb****
>>
>> **2.)     **For Sky temperature calculation with Type 69, you forgot to
>> enter the height above sea level. ****
>>
>> **3.)     **You read the ambient temperature and the relative air
>> humditiy from a userdefined file by type 9
>> instead of using the data from the weather file.
>> This file wasn’t attached, but it might be an error source especially
>> when interpolating incorrect data.
>> For testing, please use the ambient temperature and rel. humidity from
>> the assigned weather file throughout your simulation.
>> Please check your userdefined data and the outputs of Type 9 WITHOUT
>> connecting them to TYPE 56.****
>>
>> **4.)     **In addition, please check the component order. The data
>> reader Type 9 is placed after the building.****
>>
>> ** **
>>
>> ****Marion********
>>
>> ** **
>>
>> ** **
>>  ------------------------------
>>
>>
>> *Von:* 王洋 [mailto:wanghongyang1767 at gmail.com]
>> *Gesendet:* Montag, 8. Oktober 2012 15:31
>> *An:* trnsys-users at cae.wisc.edu; **hotline**
>> *Betreff:* Fwd: Converging error****
>>
>> ** **
>>
>> ** **
>>
>> Dear Marion and TRNSYS Users,
>>
>> Thanks for your reply!
>>
>> I checked all you mentioned, I can't find any special/abnormal settings.
>> Furthermore, it runs well when the time step is 1 hour. For other steps
>> e.g. 0.1 h, 0.2 h or 0.5 h, it appears that ERROR.
>>
>> Please help me have a look at the attached project if you are free.
>>
>> Many thanks in advance!
>>
>> br.
>>
>> wang****
>>
>> ---------- Forwarded message ----------
>> From: *王洋* <wanghongyang1767 at gmail.com>
>> Date: 2012/9/28
>> Subject: Converging error
>> To: trnsys-users at cae.wisc.edu, hotline at transsolar.com
>>
>>
>>
>> ---------- 已转发邮件 ----------
>> From: "**hotline**" <hotline at transsolar.com>
>> To: trnsys-users <trnsys-users at cae.wisc.edu>
>> Cc:
>> Date: Fri, 28 Sep 2012 12:02:00 +0200
>> Subject: Re: [TRNSYS-users] Converging error****
>>
>> Wang, ****
>>
>>   ****
>>
>> This problem may occur from incorrect ambient condition settings: ****
>>
>> Please check the following inputs of Type 56 ****
>>
>> 1- TAMB ****
>>
>> 2- RELHUMAMB ****
>>
>> 3- TSKY ****
>>
>> 4- TSGRD ****
>>
>>   ****
>>
>> In addition make sure that in the BUI file the surface ****
>>
>> -         outside emissitive is ≤ 1 ****
>>
>> -         outside convective heat transfer coefficient ist set to
>> reasonable value ****
>>
>>   ****
>>
>> If the error presits, we need the complete project to give further advice.
>> ****
>>
>>   ****
>>
>>   ****
>>
>> ****Marion********
>>
>> 2012/9/28 <trnsys-users-request at cae.wisc.edu>****
>>
>> Send TRNSYS-users mailing list submissions to
>>         trnsys-users at cae.wisc.edu
>>
>> To subscribe or unsubscribe via the World Wide Web, visit
>>         https://mailman.cae.wisc.edu/listinfo/trnsys-users
>> or, via email, send a message with subject or body 'help' to
>>         trnsys-users-request at cae.wisc.edu
>>
>> You can reach the person managing the list at
>>         trnsys-users-owner at cae.wisc.edu
>>
>> When replying, please edit your Subject line so it is more specific
>> than "Re: Contents of TRNSYS-users digest..."
>>
>> Today's Topics:
>>
>>    1. Re: problem with iterations?? (Matt Duffy)
>>    2. Re: problem with iterations?? (Marion Hiller)
>>    3. Re: Converging error (**hotline**)
>>
>>
>> ---------- 已转发邮件 ----------
>> From: Matt Duffy <duffy at tess-inc.com>
>> To: <trnsys-users at cae.wisc.edu>
>> Cc:
>> Date: Thu, 27 Sep 2012 12:04:24 -0500
>> Subject: Re: [TRNSYS-users] problem with iterations??****
>>
>> Karol,****
>>
>>  ****
>>
>> I noticed from your listing (*.lst) file that your working directory is
>> located on your computer's desktop directory. This is not recommended due
>> to the potential issues with the Windows OS system and write privleges. I
>> would first try changing your working directory to the ".\MyProjects"
>> directory or in a folder right on the "C:" drive. I am not certain that
>> this is the issue with the TRNEXE, but if the problem persists, please
>> contact your distributor, techsupport at tess-inc.com.****
>>
>>  ****
>>
>> Best regards,****
>>
>>
>> Matt Duffy****
>>
>>  ****
>>
>> TRNSYS on Facebook <http://www.facebook.com/TRNSYS>****
>>
>> On 2012-09-27 03:46, Karol Bandurski wrote:****
>>
>>  Dear All,****
>>
>>  ****
>>
>> I try to simulate dwelling with natural ventilation. I set some algorithm
>> for window opening and ideal heating for colder part of year for each zone
>> with set temperature depending on time of day.****
>>
>>  ****
>>
>> When I run my yearly simulation it stop in one moment and TRNEXE is
>> frozen... There is even no error! Then I can only turn off TRNEXE.****
>>
>>  ****
>>
>> Only think what appear (many times) in .lst file is****
>>
>>  ****
>>
>> Notice: More than 6 iterations for internal regulation HEATING/COOLING.**
>> **
>>
>>  ****
>>
>> I will be grateful for any advice!****
>>
>>  ****
>>
>> I enclose .lst file.****
>>
>>  ****
>>
>> Regards,****
>>
>>  ****
>>
>> ------------------------------------------------****
>>
>> Karol Bandurski MSc.****
>>
>> Institute of Environmental Engineering <http://www.ee.put.poznan.pl/>****
>>
>> Poznan University of Technology****
>>
>> www.ee.put.poznan.pl****
>>
>> www.put.poznan.pl****
>>
>>  ****
>>
>>
>>
>> ---------- 已转发邮件 ----------
>> From: "Marion Hiller" <hiller at transsolar.com>
>> To: "karol.bandurski" <karol.bandurski at put.poznan.pl>
>> Cc: trnsys-users <trnsys-users at cae.wisc.edu>
>> Date: Fri, 28 Sep 2012 08:53:53 +0200
>> Subject: Re: [TRNSYS-users] problem with iterations??****
>>
>> Karol, ****
>>
>>   ****
>>
>> In general the notice has nothing to do with a frozen TRNEXE.exe, ****
>>
>> it is just an information. ****
>>
>>   ****
>>
>> The message indicates that the internal controller for turning on the ***
>> *
>>
>> integrated heating/cooling has convergence problems and a deadband is
>> applied to promote convergence. ****
>>
>> This may be the case at the moment of turning ON or OFF something. ****
>>
>> After 6 internal iterations a deadband is added to promote convergence. *
>> ***
>>
>> If the convergence isn’t reached after 12 iterations a warning is written
>> to the lst/log file. ****
>>
>>   ****
>>
>> Regards, ****
>>
>>   ****
>>
>> ****Marion**** ****
>>
>>   ****
>>
>>   ****
>>
>> *Dipl.-Ing. **Marion Hiller **
>> **TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes
>> Bauen und Nutzerkomfort in Gebäude **
>> Munich - New York - Stuttgart + 49.711.67976.0
>>
>> **Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart
>> Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.:
>> DE152272639* ****
>>
>> *Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
>> Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher * ****
>>
>>   ****
>>
>>   ****
>>  ------------------------------
>>
>>
>>    ****
>>
>> *Von:* Karol Bandurski [mailto:karol.bandurski at put.poznan.pl]
>> *Gesendet:* Donnerstag, 27. September 2012 10:47
>> *An:* trnsys-users at cae.wisc.edu
>> *Betreff:* [TRNSYS-users] problem with iterations?? ****
>>
>>   ****
>>
>> Dear All, ****
>>
>>   ****
>>
>> I try to simulate dwelling with natural ventilation. I set some algorithm
>> for window opening and ideal heating for colder part of year for each zone
>> with set temperature depending on time of day. ****
>>
>>   ****
>>
>> When I run my yearly simulation it stop in one moment and TRNEXE is
>> frozen... There is even no error! Then I can only turn off TRNEXE. ****
>>
>>   ****
>>
>> Only think what appear (many times) in .lst file is ****
>>
>>   ****
>>
>> Notice: More than 6 iterations for internal regulation HEATING/COOLING. *
>> ***
>>
>>   ****
>>
>> I will be grateful for any advice! ****
>>
>>   ****
>>
>> I enclose .lst file. ****
>>
>>   ****
>>
>> Regards, ****
>>
>>   ****
>>
>> ------------------------------------------------ ****
>>
>> Karol Bandurski MSc. ****
>>
>> Institute of Environmental Engineering <http://www.ee.put.poznan.pl/> ***
>> *
>>
>> ****Poznan** **University**** of Technology ****
>>
>> www.ee.put.poznan.pl ****
>>
>> www.put.poznan.pl ****
>>
>>   ****
>>
>>
>>
>> ---------- 已转发邮件 ----------
>> From: "**hotline**" <hotline at transsolar.com>
>> To: trnsys-users <trnsys-users at cae.wisc.edu>
>> Cc:
>> Date: Fri, 28 Sep 2012 12:02:00 +0200
>> Subject: Re: [TRNSYS-users] Converging error****
>>
>> Wang, ****
>>
>>   ****
>>
>> This problem may occur from incorrect ambient condition settings: ****
>>
>> Please check the following inputs of Type 56 ****
>>
>> 1- TAMB ****
>>
>> 2- RELHUMAMB ****
>>
>> 3- TSKY ****
>>
>> 4- TSGRD ****
>>
>>   ****
>>
>> In addition make sure that in the BUI file the surface ****
>>
>> -         outside emissitive is ≤ 1 ****
>>
>> -         outside convective heat transfer coefficient ist set to
>> reasonable value ****
>>
>>   ****
>>
>> If the error presits, we need the complete project to give further advice.
>> ****
>>
>>   ****
>>
>>   ****
>>
>> ****Marion**** ****
>>   ------------------------------
>>
>>
>>    ****
>>
>> *Von:* 王洋 [mailto:wanghongyang1767 at gmail.com]
>> *Gesendet:* Donnerstag, 27. September 2012 11:49
>> *An:* trnsys-users at cae.wisc.edu
>> *Betreff:* [TRNSYS-users] Converging error ****
>>
>>   ****
>>
>> Dear all,
>>
>> I met a converging error when I changed simulation time step 1 hour into
>> 0.1 hour or 0.2 hour or 0.01 hour as follows:
>>
>> *** Fatal Error at time   :      3972.000000
>>     Generated by Unit     :    56
>>     Generated by Type     :    56
>>     Message               : outside temperature of    2(external) wall in
>> zone   1at time  3972.00 not converged!
>>
>> Please tell me some possible solutions for that if you know. The attached
>> is its Listing File.
>>
>> Many thanks in advance!
>> Br.
>>
>> wang
>>
>> ****
>>
>> 2012/9/27 <trnsys-users-request at cae.wisc.edu> ****
>>
>> Send TRNSYS-users mailing list submissions to
>>         trnsys-users at cae.wisc.edu
>>
>> To subscribe or unsubscribe via the World Wide Web, visit
>>         https://mailman.cae.wisc.edu/listinfo/trnsys-users
>> or, via email, send a message with subject or body 'help' to
>>         trnsys-users-request at cae.wisc.edu
>>
>> You can reach the person managing the list at
>>         trnsys-users-owner at cae.wisc.edu
>>
>> When replying, please edit your Subject line so it is more specific
>> than "Re: Contents of TRNSYS-users digest..."
>>
>> Today's Topics:
>>
>>    1. Doctoral Fellowships at TERI University, India (R.K. Singh)
>>    2. problem with iterations?? (Karol Bandurski)
>>
>>
>> ---------- 已转发邮件 ----------
>> From: "R.K. Singh" <singh.ramkishore at gmail.com>
>> To: TRNSYS-users at cae.wisc.edu
>> Cc:
>> Date: Thu, 27 Sep 2012 10:04:34 +0530
>> Subject: [TRNSYS-users] Doctoral Fellowships at TERI University, India **
>> **
>>
>> TERI University is currently inviting applications for Doctoral
>> programmes in  Bioresources/Biotechnology;Natural Resource Management,
>> Energy and Environment and Regulatory and Policy studies for semester
>> starting january 2013. A range of scholarship opportunities  are also
>> available  for the students in specific areas, the details of which can be
>> accessed through  the following link. ****
>>
>>
>> http://teriuniversity.ac.in/index.php?option=com_content&view=article&id=54
>> ****
>>
>> The last date for application is October  31st, 2012. The details
>> regarding fee, eligibility and other requirements can be accessed through
>> http://teriuniversity.ac.in/index.php?option=com_program ****
>>
>>   ****
>>
>> For any further details please get in touch with Dr. Sapna A Narula,
>> Associate Professor sapna.narula at teriuniversity.ac.in.  ****
>>
>>   ****
>>
>> ***********************************************
>> Dr. Ramkishore Singh
>> Department of Energy & Environment
>> TERI University
>> Tel: 91-11-26122222, Ext. 1302
>> Fax: 91-11-26122874
>> Web: www.teriuniversity.ac.in
>> ***********************************************
>>
>>
>>
>>
>> ---------- 已转发邮件 ----------
>> From: "Karol Bandurski" <karol.bandurski at put.poznan.pl>
>> To: <trnsys-users at cae.wisc.edu>
>> Cc:
>> Date: Thu, 27 Sep 2012 10:46:49 +0200
>> Subject: [TRNSYS-users] problem with iterations?? ****
>>
>> Dear All, ****
>>
>>   ****
>>
>> I try to simulate dwelling with natural ventilation. I set some algorithm
>> for window opening and ideal heating for colder part of year for each zone
>> with set temperature depending on time of day. ****
>>
>>   ****
>>
>> When I run my yearly simulation it stop in one moment and TRNEXE is
>> frozen... There is even no error! Then I can only turn off TRNEXE. ****
>>
>>   ****
>>
>> Only think what appear (many times) in .lst file is ****
>>
>>   ****
>>
>> Notice: More than 6 iterations for internal regulation HEATING/COOLING. *
>> ***
>>
>>   ****
>>
>> I will be grateful for any advice! ****
>>
>>   ****
>>
>> I enclose .lst file. ****
>>
>>   ****
>>
>> Regards, ****
>>
>>   ****
>>
>> ------------------------------------------------ ****
>>
>> Karol Bandurski MSc. ****
>>
>> Institute of Environmental Engineering <http://www.ee.put.poznan.pl/> ***
>> *
>>
>> ****Poznan** **University**** of Technology ****
>>
>> www.ee.put.poznan.pl ****
>>
>> www.put.poznan.pl ****
>>
>>   ****
>>
>>
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at cae.wisc.edu
>> https://mailman.cae.wisc.edu/listinfo/trnsys-users ****
>>
>>   ****
>>
>>
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at cae.wisc.edu
>> https://mailman.cae.wisc.edu/listinfo/trnsys-users****
>>
>> ** **
>>
>> ** **
>>
>
>
> _______________________________________________