[TRNSYS-users] Weather Data Reader Type15
saleh saadi
salehsnjsaadi404 at yahoo.com
Wed Oct 17 10:15:40 PDT 2012
Thanks Waseem,
It is not about a specific weather file.
I'm developing my own weather model reader and processor in Simulink. I have used results from E+ to verify my model but seems to be off at some times . So, I used TRNSYS _16, TYPE 15 to determine the solar radiation on south vertical surface using Perez model and compared that to my Simulink and E+ results. I figured that TYPE 15 interpolates the weather file (even at 1 hour time step) and therefore can't use it for verification. I was expecting that TYPE15 will read the weather file without interpolation when time step is 1 hr. Is there a way with this type or others to get the values at the beginning (or end ) of each hour rather than interpolating values at the mid of the hour?
Thanks,
Saleh
________________________________
From: waseem khan <waseemshahkhan at gmail.com>
To: trnsys-users at cae.wisc.edu
Cc: salehsnjsaadi404 at yahoo.com
Sent: Wednesday, October 17, 2012 2:56 AM
Subject: Re: TRNSYS-users Digest, Vol 94, Issue 30
Dear saleh saadi,
Salam, Please let me know the weather file name ?
On Wed, Oct 17, 2012 at 1:52 PM, <trnsys-users-request at cae.wisc.edu> wrote:
Send TRNSYS-users mailing list submissions to
> trnsys-users at cae.wisc.edu
>
>To subscribe or unsubscribe via the World Wide Web, visit
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>or, via email, send a message with subject or body 'help' to
> trnsys-users-request at cae.wisc.edu
>
>You can reach the person managing the list at
> trnsys-users-owner at cae.wisc.edu
>
>When replying, please edit your Subject line so it is more specific
>than "Re: Contents of TRNSYS-users digest..."
>
>Today's Topics:
>
> 1. Weather Data Reader Type15 (saleh saadi)
> 2. Re: Fwd: Converging error (hotline)
>
>
>---------- Forwarded message ----------
>From: saleh saadi <salehsnjsaadi404 at yahoo.com>
>To: "trnsys-users at cae.wisc.edu" <trnsys-users at cae.wisc.edu>
>Cc:
>Date: Tue, 16 Oct 2012 22:38:45 -0700 (PDT)
>Subject: [TRNSYS-users] Weather Data Reader Type15
>
>Dear user,
>
>
>
>I'm trying to extract some weather data from TRNSYS -16 after reading and processing EPW file using Pereze model (time step 1 hr). I have noticed that this TYPE interpolates the variables including the air temperature. Is there a way to extract the data without interpolation using this type or others?
>
>
>regards,
>Saleh ALSaadi
>
>
>---------- Forwarded message ----------
>From: "hotline" <hotline at transsolar.com>
>To: wanghongyang1767 <wanghongyang1767 at gmail.com>
>Cc: trnsys-users <trnsys-users at cae.wisc.edu>
>Date: Wed, 17 Oct 2012 10:21:53 +0200
>Subject: Re: [TRNSYS-users] Fwd: Converging error
>
>Dear Wang,
>
>1) I use TRNSYS 16, there is no TSGRD in TYPE 56.
>Ok. Please always include
the TRNSYS release number .
>
>2) The height over sea level of Default is 0 m I used.
>Default values NEED to be
adapted to your data!
>
>3) You are right. I tried to use *.tm2 weather data,
this Error disappeared!
>As I mentioned previous,
there must be an error in your data file. Link the outputs to the online/printer
for checking
>
>4) Yes, The data reader Type 9 is placed after the building nowfor my simulation.,
>For a successive method
all input data types should be placed at the beginning.
>Check the component order
and rearrange it.
>
>Marion
>
>Dipl.-Ing. Marion Hiller
>TRANSSOLAR:
KlimaEngineering - Technologien für energieeffizientes Bauen und Nutzerkomfort
in Gebäude
>Munich - New York - Stuttgart +
49.711.67976.0
>
>Transsolar
Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart
>Amtsgericht Stuttgart - HRB 23347,
Steuernummer 99073/00911, USt-IdNr.: DE152272639
>Geschäftsführer:
Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
Dipl.Phys. Stefan Holst, Prof.
Dipl.-Ing. Bleicher
>
>
>
>________________________________
>
>Von:王洋
[mailto:wanghongyang1767 at gmail.com]
>Gesendet: Mittwoch, 10. Oktober
2012 13:37
>An: hotline
>Cc: trnsys-users
>Betreff: Re: Fwd: Converging error
>
>Dear Marion,
>
>Many thanks for your patient reply!
>
>1) I use TRNSYS 16, there is no TSGRD in TYPE 56.
>2) The height over sea level of Default is 0 m I used.
>3) You are right. I tried to use *.tm2 weather data, this Error disappeared!
But my Userdefined weather data is TRN/TRY weather data. Why does it result in
aforementioned Errors (Converging error by my past emails)?
>If I must use our ownTRN/TRY
weather data, how to avoid this Converging error?
>4) Yes, The data reader Type 9
is placed after the building nowfor my simulation., Do you mean
Type 9 should be placed before the Building Type 56? Is Better?
>
>Many thanks in advance!
>
>Br.
>
>wang
>2012/10/10 hotline <hotline at transsolar.com>
>Dear Wang,
>
>there are several issues within your simulation
concerning the outside longwave exchange of external surfaces
>
>1.) You didn’t connect
TSGRD such that it is set 0 => If you have no information set it Tamb
>2.) For Sky temperature
calculation with Type 69, you forgot to enter the height above sea level.
>3.) You read the ambient
temperature and the relative air humditiy from a userdefined file by type 9
>instead of using the data from the weather file.
>This file wasn’t attached, but it might be an error source especially
when interpolating incorrect data.
>For testing, please use the ambient temperature and rel. humidity from the
assigned weather file throughout your simulation.
>Please check your userdefined data and the outputs of Type 9 WITHOUT connecting
them to TYPE 56.
>4.) In addition, please check
the component order. The data reader Type 9 is placed after the building.
>
>Marion
>
>
>
>________________________________
>
>
>Von:王洋[mailto:wanghongyang1767 at gmail.com]
>Gesendet: Montag, 8. Oktober 2012
15:31
>An: trnsys-users at cae.wisc.edu; hotline
>Betreff: Fwd: Converging error
>
>
>Dear Marion and TRNSYS Users,
>
>Thanks for your reply!
>
>I checked all you mentioned, I can't find any special/abnormal settings. Furthermore,
it runs well when the time step is 1 hour. For other steps e.g. 0.1 h, 0.2 h or
0.5 h, it appears that ERROR.
>
>Please help me have a look at the attached project if you are free.
>
>Many thanks in advance!
>
>br.
>
>wang
>----------
Forwarded message ----------
>From: 王洋 <wanghongyang1767 at gmail.com>
>Date: 2012/9/28
>Subject: Converging error
>To: trnsys-users at cae.wisc.edu, hotline at transsolar.com
>
>
>
>---------- 已转发邮件 ----------
>From: "hotline" <hotline at transsolar.com>
>To: trnsys-users <trnsys-users at cae.wisc.edu>
>Cc:
>Date: Fri, 28 Sep 2012 12:02:00 +0200
>Subject: Re: [TRNSYS-users] Converging error
>Wang,
>
>This problem may occur from incorrect ambient condition
settings:
>Please check the following inputs of Type 56
>1- TAMB
>2- RELHUMAMB
>3- TSKY
>4- TSGRD
>
>In addition make sure that in the BUI file the surface
>- outside
emissitive is ≤ 1
>- outside
convective heat transfer coefficient ist set to reasonable value
>
>If the error presits, we need the complete project to give
further advice.
>
>
>Marion
>2012/9/28 <trnsys-users-request at cae.wisc.edu>
>Send TRNSYS-users
mailing list submissions to
> trnsys-users at cae.wisc.edu
>
>To subscribe or unsubscribe via the World Wide Web, visit
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>or, via email, send a message with subject or body 'help' to
> trnsys-users-request at cae.wisc.edu
>
>You can reach the person managing the list at
> trnsys-users-owner at cae.wisc.edu
>
>When replying, please edit your Subject line so it is more specific
>than "Re: Contents of TRNSYS-users digest..."
>
>Today's Topics:
>
> 1. Re: problem with iterations?? (Matt Duffy)
> 2. Re: problem with iterations?? (Marion Hiller)
> 3. Re: Converging error (hotline)
>
>
>---------- 已转发邮件 ----------
>From: Matt Duffy <duffy at tess-inc.com>
>To: <trnsys-users at cae.wisc.edu>
>Cc:
>Date: Thu, 27 Sep 2012 12:04:24 -0500
>Subject: Re: [TRNSYS-users] problem with iterations??
>Karol,
>
>I noticed
from your listing (*.lst) file that your working directory is located on your
computer's desktop directory. This is not recommended due to the potential
issues with the Windows OS system and write privleges. I would first try
changing your working directory to the ".\MyProjects" directory or in
a folder right on the "C:" drive. I am not certain that this is the
issue with the TRNEXE, but if the problem persists, please contact your
distributor, techsupport at tess-inc.com.
>
>Best
regards,
>
>Matt Duffy
>
>TRNSYS on Facebook
>On
2012-09-27 03:46, Karol Bandurski wrote:
>Dear All,
>>
>>I try to simulate
dwelling with natural ventilation. I set some algorithm for window opening and
ideal heating for colder part of year for each zone with set temperature
depending on time of day.
>>
>>When I run my
yearly simulation it stop in one moment and TRNEXE is frozen... There is even
no error! Then I can only turn off TRNEXE.
>>
>>Only think what
appear (many times) in .lst file is
>>
>>Notice: More than
6 iterations for internal regulation HEATING/COOLING.
>>
>>I will be grateful
for any advice!
>>
>>I enclose .lst
file.
>>
>>Regards,
>>
>>------------------------------------------------
>>Karol Bandurski
MSc.
>>Institute of Environmental
Engineering
>>Poznan
University of Technology
>>www.ee.put.poznan.pl
>>www.put.poznan.pl
>>
>
>
>---------- 已转发邮件 ----------
>From: "Marion Hiller"
<hiller at transsolar.com>
>To: "karol.bandurski" <karol.bandurski at put.poznan.pl>
>Cc: trnsys-users <trnsys-users at cae.wisc.edu>
>Date: Fri, 28 Sep 2012 08:53:53 +0200
>Subject: Re: [TRNSYS-users] problem with iterations??
>Karol,
>
>In general the notice has nothing to do with a
frozen TRNEXE.exe,
>it is just an information.
>
>The message indicates that the internal
controller for turning on the
>integrated heating/cooling has convergence
problems and a deadband is applied to promote convergence.
>This may be the case at the moment of turning ON
or OFF something.
>After 6 internal iterations a deadband is added
to promote convergence.
>If the convergence isn’t reached after 12
iterations a warning is written to the lst/log file.
>
>Regards,
>
>Marion
>
>
>Dipl.-Ing. Marion Hiller
>TRANSSOLAR:
KlimaEngineering - Technologien für energieeffizientes Bauen und Nutzerkomfort
in Gebäude
>Munich - New York - Stuttgart +
49.711.67976.0
>
>Transsolar
Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart
>Amtsgericht Stuttgart - HRB 23347,
Steuernummer 99073/00911, USt-IdNr.: DE152272639
>Geschäftsführer: Dipl.Ing. Matthias Schuler,
Dipl.Ing. Thomas Auer, Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher
>
>
>
>________________________________
>
>
>
>Von:Karol Bandurski [mailto:karol.bandurski at put.poznan.pl]
>Gesendet: Donnerstag, 27.
September 2012 10:47
>An: trnsys-users at cae.wisc.edu
>Betreff: [TRNSYS-users] problem
with iterations??
>
>Dear
All,
>
>I
try to simulate dwelling with natural ventilation. I set some algorithm for
window opening and ideal heating for colder part of year for each zone with set
temperature depending on time of day.
>
>When
I run my yearly simulation it stop in one moment and TRNEXE is frozen... There
is even no error! Then I can only turn off TRNEXE.
>
>Only
think what appear (many times) in .lst file is
>
>Notice:
More than 6 iterations for internal regulation HEATING/COOLING.
>
>I
will be grateful for any advice!
>
>I
enclose .lst file.
>
>Regards,
>
>------------------------------------------------
>Karol
Bandurski MSc.
>Institute
of Environmental Engineering
>PoznanUniversityof Technology
>www.ee.put.poznan.pl
>www.put.poznan.pl
>
>
>
>---------- 已转发邮件 ----------
>From: "hotline" <hotline at transsolar.com>
>To: trnsys-users <trnsys-users at cae.wisc.edu>
>Cc:
>Date: Fri, 28 Sep 2012 12:02:00 +0200
>Subject: Re: [TRNSYS-users] Converging error
>Wang,
>
>This problem may occur from incorrect ambient condition
settings:
>Please check the following inputs of Type 56
>1- TAMB
>2- RELHUMAMB
>3- TSKY
>4- TSGRD
>
>In addition make sure that in the BUI file the surface
>- outside
emissitive is ≤ 1
>- outside
convective heat transfer coefficient ist set to reasonable value
>
>If the error presits, we need the complete project to give
further advice.
>
>
>Marion
>
>________________________________
>
>
>
>Von:王洋[mailto:wanghongyang1767 at gmail.com]
>Gesendet: Donnerstag, 27.
September 2012 11:49
>An: trnsys-users at cae.wisc.edu
>Betreff: [TRNSYS-users] Converging
error
>
>Dear all,
>
>I met a converging error when I changed simulation time step 1 hour into 0.1
hour or 0.2 hour or 0.01 hour as follows:
>
>*** Fatal Error at time : 3972.000000
> Generated by Unit
: 56
> Generated by Type
: 56
>
Message
: outside temperature of 2(external) wall in zone
1at time 3972.00 not converged!
>
>Please tell me some possible solutions for that if you know. The attached is
its Listing File.
>
>Many thanks in advance!
>Br.
>
>wang
>2012/9/27 <trnsys-users-request at cae.wisc.edu>
>Send TRNSYS-users
mailing list submissions to
> trnsys-users at cae.wisc.edu
>
>To subscribe or unsubscribe via the World Wide Web, visit
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>or, via email, send a message with subject or body 'help' to
> trnsys-users-request at cae.wisc.edu
>
>You can reach the person managing the list at
> trnsys-users-owner at cae.wisc.edu
>
>When replying, please edit your Subject line so it is more specific
>than "Re: Contents of TRNSYS-users digest..."
>
>Today's Topics:
>
> 1. Doctoral Fellowships at TERI University, India (R.K. Singh)
> 2. problem with iterations?? (Karol Bandurski)
>
>
>---------- 已转发邮件 ----------
>From: "R.K. Singh" <singh.ramkishore at gmail.com>
>To: TRNSYS-users at cae.wisc.edu
>Cc:
>Date: Thu, 27 Sep 2012 10:04:34 +0530
>Subject: [TRNSYS-users] Doctoral Fellowships at TERI University, India
>TERI University is
currently inviting applications for Doctoral programmes in
Bioresources/Biotechnology;Natural Resource Management, Energy and
Environment and Regulatory and Policy studies for semester starting january
2013. A range of scholarship opportunities are also available for
the students in specific areas, the details of which can be accessed through
the following link.
>http://teriuniversity.ac.in/index.php?option=com_content&view=article&id=54
>The last date for
application is October 31st, 2012. The details regarding fee, eligibility
and other requirements can be accessed through http://teriuniversity.ac.in/index.php?option=com_program
>
>For any further
details please get in touch with Dr. Sapna A Narula, Associate Professor sapna.narula at teriuniversity.ac.in.
>
>***********************************************
>Dr. Ramkishore Singh
>Department of Energy & Environment
>TERI University
>Tel: 91-11-26122222, Ext. 1302
>Fax: 91-11-26122874
>Web: www.teriuniversity.ac.in
>***********************************************
>
>
>
>
>---------- 已转发邮件 ----------
>From: "Karol Bandurski" <karol.bandurski at put.poznan.pl>
>To: <trnsys-users at cae.wisc.edu>
>Cc:
>Date: Thu, 27 Sep 2012 10:46:49 +0200
>Subject: [TRNSYS-users] problem with iterations??
>Dear
All,
>
>I try
to simulate dwelling with natural ventilation. I set some algorithm for window
opening and ideal heating for colder part of year for each zone with set
temperature depending on time of day.
>
>When I
run my yearly simulation it stop in one moment and TRNEXE is frozen... There is
even no error! Then I can only turn off TRNEXE.
>
>Only
think what appear (many times) in .lst file is
>
>Notice:
More than 6 iterations for internal regulation HEATING/COOLING.
>
>I will
be grateful for any advice!
>
>I
enclose .lst file.
>
>Regards,
>
>------------------------------------------------
>Karol
Bandurski MSc.
>Institute
of Environmental Engineering
>PoznanUniversityof Technology
>www.ee.put.poznan.pl
>www.put.poznan.pl
>
>
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at cae.wisc.edu
>https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at cae.wisc.edu
>https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
>
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at cae.wisc.edu
>https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
--
--
Kind Regards,
Waseem Shah Khan
Energy Analyst
New Delhi 110025,India
Mob:+91.9999535880