Amadu,
   The way I have approached this is to use the "loads imposed on a 
liquid stream" component from the TESS Loads and Structures library 
(Type682). The same can be accomplished with an equation: Tout = Tin + 
QLOAD/mdot/Cp where Tin is the temperature of liquid being supplied by 
the absorption chiller, QLOAD is the building cooling load, mdot is the 
mass flow rate of liquid supplied by the absorption chiller, and Cp is 
the specific heat of the liquid. I would advise also putting a pump, 
piping, and a storage tank large enough to hold the volume of liquid 
that the pump puts out in one timestep. Make sure also that you are 
using a reasonably small timestep such as 5 minutes.

  As for Type107 data, this is unfortunately somewhat hard to find. I 
would recommend searching manufacturer's websites (Carrier, York, etc.) 
for performance data on a specific machine that you want to model.
Kind regards,
  David


On 5/15/2012 07:37, TALIB O. ahmadu wrote:
> Please can anyone enlighten me on how to connect the building cooling load from type 56 to the absorption chiller, type107.
> Also, how do i get the  absorption chiller performance data and how do i input it to the trnsys programme. I am using trnsys 16.
> I am Ahmadu Talib, a researcher at university of Lagos, Nigeria.
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com




More information about the TRNSYS-users mailing list