i´m afraid but i think there is no such direct link, in that direction (type56-->type107).
In fact the cooling capacity of your absorption chiller must be an input to type 56 (as a negative gain, be aware of considering sensible (negative energy gain) and latent loads (negative humidity gain) if your are working with fancoils) and not impose the temperature of the zone (kind of free-floating), the balance on zone will tell you the final temperature which must be controlled.
Regards.
Juan Francisco Belmonte Toledo
Universidad de Castilla-La Mancha
Campus Universitario. Avda. de España, s/n
02071 Albacete. Spain
De: TALIB O. ahmadu
Enviado el: Mar 15/05/2012 14:37
Para: trnsys-users at engr.wisc.edu
Asunto: [TRNSYS-users] how to connect building cooling load to absorption chiller
Please can anyone enlighten me on how to connect the building cooling load from type 56 to the absorption chiller, type107.
Also, how do i get the absorption chiller performance data and how do i input it to the trnsys programme. I am using trnsys 16.
I am Ahmadu Talib, a researcher at university of Lagos, Nigeria.