[TRNSYS-users] TRNSYS-users Digest, Vol 89, Issue 19

Jochen Doell jochen.doell at ise.fraunhofer.de
Fri May 11 01:26:35 PDT 2012


Hello Dakhli,

very briefly:
You need a table of operation points from your machine. It must consist 
of values for
- Fraction of design load 
(=FLOW_CHW(i)*CP_CHW(i)*(TCHW_IN(i)-TCHW_SET(i))/DesignCapacity)
- Chilled water setpoint
- Entering Chilled Water Temperature
- Inlet Hot Water Temperature
covering the range you want to simulate.
Additionally, you need to calculate the two values for these operation 
points TRNSYS will receive from the performance map:
Fraction of rated capacity (=Capacity(i)/DesignCapacity)
Fract. Of Design Energy Input (=Q_Hot_Water(i)*Design_COP/DesignCapacity)

All values with an "(i)" are values specific for that single operation 
point.

You can have a look at the source code of the type, there it all 
becomes... clear.

Imho, this type is unessecarly complicated and the map is tricky to set 
up. Have a look at the documentation and the source code and If you need 
further assistance, let me know.

Best regards,
Jochen

Am 11.05.2012 00:36, schrieb dakhli malak:
> hi everybody,
>
> well, i am beginner with trnsys. I tried the example of the EES calling
> function but it's not working!
> i asked some other people and it's the same for them!! do you have idea
> about it ?
> otherwise, do you advice me to work with type107 instead of EES ? I need to
> make the modeling
> of the solar cooling system for a building under Tunisian climate (it's a
> Bachelor thesis, so there's a pressure of time)
>
> best regards.
>
> PS: Thank you for clarification Mr. Jochen.
>
>
> On Thu, May 10, 2012 at 7:00 PM,<trnsys-users-request at cae.wisc.edu>  wrote:
>
>> Send TRNSYS-users mailing list submissions to
>>         trnsys-users at cae.wisc.edu
>>
>> To subscribe or unsubscribe via the World Wide Web, visit
>>         https://mailman.cae.wisc.edu/listinfo/trnsys-users
>> or, via email, send a message with subject or body 'help' to
>>         trnsys-users-request at cae.wisc.edu
>>
>> You can reach the person managing the list at
>>         trnsys-users-owner at cae.wisc.edu
>>
>> When replying, please edit your Subject line so it is more specific
>> than "Re: Contents of TRNSYS-users digest..."
>>
>> Today's Topics:
>>
>>    1. run simulation (use new component) (Eva gklezakou)
>>    2. Re: run simulation (use new component) (Jeff Thornton)
>>    3. Re: solar cooling (H2O/LIBR single effect absorption machine)
>>       (Jochen Doell)
>>    4. External data files for heat pump&  absorbtion    chiller
>>       (Santeri Siren)
>>    5. insertion of a balcony (Alessandro Rinaldi)
>>
>>
>> ---------- Forwarded message ----------
>> From: Eva gklezakou<gklezakoue at gmail.com>
>> To: trnsys-users<TRNSYS-users at cae.wisc.edu>
>> Cc:
>> Date: Wed, 9 May 2012 21:11:02 +0100
>> Subject: [TRNSYS-users] run simulation (use new component)
>> Dear Sirs,
>>
>> I am a beginner user of TRNSYS so I am not sure if I use it in the right
>> way. I want to use a new component which I receive but even though I copy
>> paste the *.dll file of the PCM component to the exe folder of TRNSYS and
>> the *.tmf to the proformas still have an error which says that " A TYPE was
>> called in the TRNSYS input file but was either not linked into trndll.dll
>> or was not found in an external dll. A dummy subroutine was called in its
>> place. Please link the TYPE or remove it from the input file".
>> Thank you.
>>
>> Regards,
>> Eva
>>
>>
>> ---------- Forwarded message ----------
>> From: Jeff Thornton<thornton at tess-inc.com>
>> To:<trnsys-users at cae.wisc.edu>
>> Cc:
>> Date: Wed, 09 May 2012 15:16:55 -0500
>> Subject: Re: [TRNSYS-users] run simulation (use new component)
>> **
>>
>> The user-created DLL's don't go in the Exe folder.  They go in the correct
>> spot in the UserLib directory (depends on whether the DLL was created as a
>> release version DLL or a debug-version DLL).
>>
>>
>>
>> Jeff
>>
>>
>>
>> ---
>>
>> Jeff Thornton
>>
>> *President - TESS LLC*
>>
>> *22 N. Carroll Street, Madison WI USA 53703*
>>
>> *Office: (608) 274-2577  Fax: (608) 278-1475*
>>
>> *www.tess-inc.com*
>>
>> *E-Mail: thornton at tess-inc.com*
>>
>>
>>
>> On 05/09/2012 3:11 pm, Eva gklezakou wrote:
>>
>> Dear Sirs,
>> I am a beginner user of TRNSYS so I am not sure if I use it in the right
>> way. I want to use a new component which I receive but even though I copy
>> paste the *.dll file of the PCM component to the exe folder of TRNSYS and
>> the *.tmf to the proformas still have an error which says that " A TYPE was
>> called in the TRNSYS input file but was either not linked into trndll.dll
>> or was not found in an external dll. A dummy subroutine was called in its
>> place. Please link the TYPE or remove it from the input file".
>> Thank you.
>>
>> Regards,
>> Eva
>>
>>
>>
>> ---------- Forwarded message ----------
>> From: Jochen Doell<jochen.doell at ise.fraunhofer.de>
>> To: dakhli malak<dakhli.malak at gmail.com>
>> Cc: trnsys-users at cae.wisc.edu
>> Date: Thu, 10 May 2012 09:01:44 +0200
>> Subject: Re: [TRNSYS-users] solar cooling (H2O/LIBR single effect
>> absorption machine)
>> Dear Dakhli,
>>
>> type107 is a performance map type, i.e. you have to supply a table with
>> (steady state) operatingg conditions from which the type takes its current
>> performance (including interpolation).
>> When you use a calling function like calling EES, you have your chiller
>> modelled in a different environment (here the Engineering Equation Solver).
>> There you can have for example an advanced physical model, which might be
>> hard or impossible to program in sequential fortran code as used for TRNSYS.
>>
>> Best regards,
>> Jochen
>>
>> Am 09.05.2012 10:32, schrieb dakhli malak:
>>
>>> Hi everybody,
>>>
>>> i read some articles and i found that some people are using type107 in the
>>> modelling of the machine
>>> and some others are using the calling function of EES. So, what's the
>>> difference between them ?
>>>
>>> cordially,
>>>
>>>
>> --
>> ______________________________**___________________
>>
>> Dipl.-Ing. (FH) Jochen Döll
>> Division Thermal Systems and Buildings
>>
>> Fraunhofer-Institut für Solare Energiesysteme ISE
>> Heidenhofstrasse 2, 79110 Freiburg, Germany
>>
>> Phone: +49 (761) 4588-5468 Fax: +49 (761) 4588-9000
>> jochen.doell at ise.fraunhofer.de
>> www.ise.fraunhofer.de
>> ______________________________**___________________
>>
>>
>>
>>
>> ---------- Forwarded message ----------
>> From: Santeri Siren<santeri.siren1 at gmail.com>
>> To: "trnsys käyttäjät"<trnsys-users at cae.wisc.edu>
>> Cc:
>> Date: Thu, 10 May 2012 16:33:51 +0300
>> Subject: [TRNSYS-users] External data files for heat pump&  absorbtion
>> chiller
>> Dear all,
>>
>> I need to use a water to water ground heat pump (type 668) and absorbtion
>> chiller in my simulations. It seems to be very difficult to find product
>> catalogues that include the information required in the external data
>> files. Could someone with experience please tell me which manufacturers do
>> provide this kind of information and perhaps send me a link. The only
>> catalogue data file that I was able to for water to water heat pump was
>> this one from Carrier:
>>
>>
>> http://www.docs.hvacpartners.com/idc/groups/public/documents/techlit/50psw-3pd.pdf
>>
>> Best regards. Santeri Siren
>>
>>
>>
>>
>> ---------- Forwarded message ----------
>> From: Alessandro Rinaldi<alexius87 at hotmail.it>
>> To:<trnsys-users at cae.wisc.edu>
>> Cc:
>> Date: Thu, 10 May 2012 18:19:20 +0200
>> Subject: [TRNSYS-users] insertion of a balcony
>>   hi, which type should I use to insert a balcony that shades the wall
>> below and the window? thanks
>>
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at cae.wisc.edu
>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>
>>

-- 
_________________________________________________

Dipl.-Ing. (FH) Jochen Döll
Division Thermal Systems and Buildings

Fraunhofer-Institut für Solare Energiesysteme ISE
Heidenhofstrasse 2, 79110 Freiburg, Germany

Phone: +49 (761) 4588-5468 Fax: +49 (761) 4588-9000
jochen.doell at ise.fraunhofer.de
www.ise.fraunhofer.de
_________________________________________________




More information about the TRNSYS-users mailing list